Wrenches,

Recently, we took delivery of a 40 kW LPG generator made by Gillette.

Inspecting the factory wiring of the unit, I had some concerns which are 
outlined in detail below, with an engineer's response inline. The concerns are 
using #4 wire to pull 175A; no plastic bushings on metallic conduit, and ground 
lugs on top of painted surfaces / and insufficiently torqued.

The engineer response has left me somewhat baffled / frustrated in that I do 
not feel that actual issues have been addressed. I don't really care what UL or 
any other authority tells me - pulling 175A continually for many hrs through a 
#4 wire I think is asking for trouble. And my customer won't really care about 
what the UL ratings say if they are dealing with a melted alternator.

Am I missing something here?

Kevin


RE: SP-410-1-1LO     S/N:

I am responding to the concerns written below both in the capacity as designer 
and as U.L. liaison.

We have received this generator, mostly intact. Some freight damage to the 
battery support cross member due to forks not extending the full depth of the 
crate, and are working with the freight company to resolve that.
Sorry for the experienced freight damage.

However, there are some SERIOUS and DANGEROUS issues pertaining to the wiring 
of the alternator! It is obvious that wiring was not done by an electrician.
There are no serious or dangerous issues on this (built to U.L. recognized 
spec) Gillette Generator as referred to in this writing. And - you are correct- 
this wiring, as 'factory wiring and not 'field' wiring, does not require or use 
the specific qualifications of a licensed electrician. The well 
trained/supervised workers here at Gillette have many years of experience 
building the product and are guided as need by a competent engineering staff.

Specifically:

- Alternator to circuit breaker wiring was done with #4 wire (rated 60A max). 
Per your own load chart inside the breaker enclosure (photo attached), that 
wire should be 4/0 to carry the 175A that this generator is capable of 
producing.
This observation is incorrect. The load wiring sizing schedule affixed to the 
side of the circuit breaker box is for 'field connectivity' at 75 deg. F. We do 
our 'factory wiring ' on a different schedule using load cabling from the 
generator to the top of the circuit breaker rated at 150 deg. F. All of this 
cabling has been done, tested and proven by U.L

- There were no plastic bushings (see photo) where the wires exit the metal 
conduit.
The conduit bushing involved is the correct U.L. approved component for the 
installation of spiral wound metal conduit required to be installed on 'open' 
style generator assemblies. A plastic bushing is NOT required as this is again 
'factory wiring', not 'field wiring.

- What would have happened here is the wire heats up due to gross under sizing, 
melts the insulation, and shorts it out. Resulting in a fire or destruction of 
the brand new alternator, and the associated legal proceedings involving all 
parties and a general nightmare for all of us.
 disagree, on several fronts. Referencing the specification standard U.L. 2200, 
many times- local inspectors blur the line between its dominance for standby 
generator systems and NEC-70 (NEC- code). The former covers 'factory' design 
wiring on stationary standby generators subject to witness testing by a U.L. 
certified representative. The latter applies to 'field wiring'- that is 
anything outside the box including connection conduits, load wiring ( at 75 
deg. F) transfer switches, distribution panes and the like. As resident 
designer for the past twenty-six years, I have myself- written eight 
standards/code rebuttals successfully, both for U.L. and local inspectors. 
Comparing a 4ga, 2ga, 1ga and the like against a different class of wiring such 
as a 4/0 would certainly be cause for alarm. But, clearly here the alarm is 
unwarranted.

                - the ground lug on the alternator was not fastened properly (a 
short stud with a nut on it - no way to get proper torque on it - should be a 
bolt), and both this lug and the lug inside the breaker enclosure was fitted on 
top of a painted surface. Every electrician knows you need to scrape off the 
paint so as to allow for proper conductivity.
This lug is not supplied by us. It is supplied as part of the generator 
construction built by Marathon. Marathon generators are certified for U.L. 
1004B- generator assemblies and U.L. 1446 for insulation. This is the equipment 
issued as part of that U.L. certified design. as to their design vs. a 'bolt' 
going into the threads of the hole-  if it was really an issue, it would not 
have passed their U.L. certification testing. Their generator assemblies bear 
their U.L. file certification under R/C (JZGZ2) and listing (JZGZ). In regards 
to the paint removal, the engine and generator are cable grounded to the frame 
of the generator assembly and serrated hardware is used during assembly to 
scratch into the painted surfaces of the boxes and frame. As you notice in the 
picture- the threads in the generator housing sleeve- are not painted.

                These are issues that we are able to remedy. But my client, 
being very hands on has noticed this and inquired, quite reasonably, as to why 
they are paying Energy Alternatives to repair something that they paid for and 
should have been delivered properly done in the first place?
To my findings, there is no warrantable work required.

                I think the fairest solution to this is for us to remedy these 
defects and to have Collicutt reimburse use for time and materials. I will 
complete the work and send you the total bill for compensation unless you would 
like to approach this in a different method. We are hoping to go live with this 
unit in the next few days once the gas fitting is completed.
As stated above- Not required.

I hope these responses help clarify the items in question.


Regards,



_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to