Wrenches We do allot of these ourselves and, it seems each is different but the last one was 18 units plus the common all got load side taps with fused 30 amp discos, we have also had line side but your panel is hard bused and a load side is the only way. There is a new breaker out but last I heard it is not UL approved I have left them messages with no response. Our utility requires disco's so it works out OK this way. the paperwork is crazy for this with all the little systems. Jerry
On Tue, Jun 14, 2016 at 12:57 PM, August Goers <[email protected]> wrote: > Hi Wrenches, > > > > We’re installing on a lot of multifamily buildings these days. Does anyone > have a clue how to apply NEC 705.12 interconnection rules to the type of > setup in the attached photo? In this case, we have a 200 A or 400 A main > service disconnect feeding a 9-meter bank. The meter bank appears to be > setup so that each meter is fed from the main disconnect by factory > bussing. Each individual meter has a 70 A breaker feeding a remote sub > panel. We want to install a 50 A solar breaker. We can interconnect at one > of the existing meters or possibly install a new solar-service in one of > the blank meter spots. > > > > Cheers, > > > > August > > > > Luminalt > > _______________________________________________ > List sponsored by Redwood Alliance > > List Address: [email protected] > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > List-Archive: > http://www.mail-archive.com/[email protected]/maillist.html > > List rules & etiquette: > www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > www.members.re-wrenches.org > > >
_______________________________________________ List sponsored by Redwood Alliance List Address: [email protected] Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/[email protected]/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org