Test resistance only on disconnected wiring, measure resistant to ground either side of the switching point. . The controller will likely be a open collector that will measure current to ground. Do nor use megger, you are not testing insulation. On Jul 5, 2016 10:37 AM, "Drake" <[email protected]> wrote:
Is there a way to test the conductivity sensors for the low water shutoff and restart on a submersible well pump, from the surface? Could the wires be resistivity tested? What should the resistance readings be between the wires? Would a megohm meter be the right tool to use? Could the pump be harmed by the high voltage spike in the water around it produced by the meter? Thanks, Drake Drake Chamberlin *Athens Electric LLC OH License 44810 CO License 3773 NABCEP Certified Solar PV 740-448-7328 <740-448-7328> *http://athens-electric.com/ _______________________________________________ List sponsored by Redwood Alliance List Address: [email protected] Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/[email protected]/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
_______________________________________________ List sponsored by Redwood Alliance List Address: [email protected] Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/[email protected]/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org