Hear, Hear, Gary, listen to the Graybeards.

One thing I would like to mention here. Over the last 3 years, I have seen a 
dramatic increase of early failures of Lifeline (like Sun Xtender, made by 
Concorde) batteries. I have been selling and installing Lifeline since 2004 and 
have hundreds of 8-12 year old battery systems being used. I have not been able 
to identify any cause related to use. 

So, has anyone seen Sun Xtender or Concorde early failures in recent years?    
BTW, we have been selling FullRiver batteries for a few years now with no 
failures and very happy customers.

Thank you,

Larry Crutcher
Starlight Solar Power Systems
(928) 342-9103




On Sep 1, 2016, at 6:19 PM, jay <[email protected]> wrote:

HI Ray,

I second your opinion.  

jay

peltz power
> On Sep 1, 2016, at 4:43 PM, Ray Walters <[email protected] 
> <mailto:[email protected]>> wrote:
> 
> Hi Gary;
> 
> I think it would be a waste of time to load test a sealed battery that is 9 
> years old.  Even at only 20% discharge, that battery only has 2800 cycles.  
> At 80% discharge, its 550 cycles.  The daily system cycle is probably roughly 
> a 10% cycle, coupled with the frequent deep cycles.  We have been seeing 5 to 
> 7 years in GTB systems with regular sealed batteries.  Even in float mode, 
> they don't last forever.
> Also the customer has already done a basic load test, and the battery is 
> failing.  Its only a matter of time before you start seeing cell failures, 
> and then the system won't even work when the grid is up.
> I'd just replace the set on your next trip.
> R.Ray Walters
> CTO, Solarray, Inc
> Nabcep Certified PV Installer, 
> Licensed Master Electrician
> Solar Design Engineer
> 303 505-8760
> On 9/1/2016 2:00 PM, jerrysgarage01 wrote:
>> Wrenches
>> You can do a carbon pile test but the best way is testing under several 
>> conditions. Here is an option real easy and maybe faster, put a volt meter 
>> on each battery under constant charge conditions, higher volts on one 
>> battery meens high resistance in battery, low volts meens low resistance, 
>> either extreme can be an issue.  Then let sit for at least an hour with no 
>> load and check the volts, next put a fixed load on the system, again a volt 
>> meter check each battery,  here you may find a lower reading then the rest, 
>> there is the problem, now replace the entire bank not just the single 
>> battery. This is an easy test and the customer can see it easily too.
>> Jerry
>> 
>> 
>> Sent via the Samsung Galaxy S™ III, an AT&T 4G LTE smartphone
>> 
>> 
>> -------- Original message --------
>> From: Gary Bassett
>> Date:09/01/2016 2:51 AM (GMT-10:00)
>> To: "RE-wrenches ([email protected] 
>> <mailto:[email protected]>)"
>> Subject: [RE-wrenches] Test procedure for Concorde batteries
>> 
>> We have a grid tied battery backup system that uses 8 Sun Xtender PVX-2120L 
>> batteries, about 9 years old. The grid has been going out frequently – about 
>> 4 times in the past 3 weeks. When the grid goes out, the battery voltage 
>> gets too low and shuts the system down pretty quickly. One of the times, 
>> this happened within 4 hours. We want to test the capacity of the batteries 
>> and we have a testing procedure from Concorde that seems like it would take 
>> a lot of time. Is there a quick way to test the battery capacity?
>> 
>>  
>> 
>> Gary
>> 
>>  
>> 
>>  
>> 
>> 

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings: