Hi William, I have had a similar experience here in New Zealand on a FP2 fitted 
with VFXR3024E inverters.  Factory wired with a Mate3.  Ran ok for around 2 
months then random errors with “FX Firmware incompatible” then “FX Firmware OK” 
until eventually the slave inverter shut down with a message on the mate of 
FXRBL which means Boot Load, going back to very basic bootup mode.  It could 
only be corrected by doing a firmware upgrade which would not work via the Mate 
and Hub, had to plug Mate directly into inverter.  Reloaded system config from 
SD card file and all ok.

 

Now, after around 2 weeks, Mate display went blank except for border graphics.  
Supplier, suspecting a possibly faulty mate has sent a replacement and, when 
trying to load system configuration the file which I resaved on leaving last 
time has been scrambled.

 

Still waiting for a resolution but I suspect it is something to do with the 
VFXR’s or possibly the Mate.  Software bug or something.  Solution might be to 
replace VFXR’s with VFX’s but we will have to see what Outback come back with.  
Meantime I have a very irate customer with ½ of the system operating (Master 
inverter only).  System is nearly 3 hours travel one way so popping over to 
reset it when it is likely to randomly shut down again is not an option!  Still 
waiting to hear from Outback if they will cover this with warranty.

 

Bruce Geddes

Freedom Energy Ltd

 

From: RE-wrenches [mailto:[email protected]] On Behalf 
Of William Miller
Sent: Friday, 11 November 2016 5:26 p.m.
To: RE-wrenches
Subject: Re: [RE-wrenches] Outback Programming Ghost

 

Ray:

 

I have no reason to believe anyone has been meddling. No one knows the 
password. It does look like some serious glitch. 

 

William


On Nov 10, 2016, at 6:25 PM, Ray Walters <[email protected]> wrote:

It almost sounds like someone got in there and tried to reprogram stuff 
themselves.  Have you installed the proper anti-Gremlin devices?



R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer, 
Licensed Master Electrician
Solar Design Engineer
303 505-8760

On 11/10/2016 12:34 PM, William Miller wrote:

Colleagues: 

 

I maintain an off-grid, 8 stack FX Outback system with 3 charge controllers.  
The system has been on line for about 6 years.  It got upgraded about 7 months 
ago with 2 Mate3s.

 

About a week ago the system shutdown, leaving the customer without power.  A 
maintenance worker started a generator and power was restored.  I did not hear 
about the situation for several days.

 

A maintenance supervisor was dispatched yesterday to work with me over the 
telephone to see if we could restart the system.  The system would only run if 
the inverter output breakers were all off.  

 

I examined the system via Optics.  I was very surprised to see that the system 
programming was absolutely scrambled.  This was so much so that even the 
stacking settings were wrong.  For example, inverter 2 was set as a Master, 
which we all know will crash any system.  Other settings were also found with 
very random values.

 

This system was running prior to last Friday, so the stacking at least must 
have been right prior to the outage.  I am completely mystified as to how this 
could have happened.  

 

I am in conversation with Outback who is taking this seriously.  I have not 
heard back from them yet but I am curious if anyone else has experienced this 
or anything similar.  I'd like to broaden my knowledge on this situation to 
enhance my understanding and to share any findings with the group.

 

Thank you in advance for any input.

 

William Miller






_______________________________________________
List sponsored by Redwood Alliance
 
List Address: [email protected]
 
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html
 
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
 
Check out or update participant bios:
www.members.re-wrenches.org
 

 

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

  _____  

No virus found in this message.
Checked by AVG - www.avg.com
Version: 2015.0.6201 / Virus Database: 4656/13091 - Release Date: 09/26/16
Internal Virus Database is out of date.

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to