When they work the new programming options/features are really cool and if I 
may be so bold (or nerdy) to say Fun.

However, when they don't work and instead shut down the system...@&$! 
Absolutely Frustrating. Somehow I feel we are the constant guinea pigs.

I hope the firmware update glitches are remedied soon.


Wayne Irwin,
President
License #CVC56695
State Licensed Solar Contractor
Pure Energy Solar International Inc.
[email protected]
http://PureEnergySolar.com
http://SolarChargingStation.net
352 377-6527 Office
352 336-3299 Fax


The Sun Is Always Shining!

The content of this message is Pure Energy Solar Confidential. If you are not 
the intended recipient and have received this message in error, any use or 
distribution is prohibited. Please notify me immediately by reply e-mail and 
delete this message from your computer system. Thank you.
________________________________
From: RE-wrenches <[email protected]> on behalf of 
William Miller <[email protected]>
Sent: Saturday, November 12, 2016 12:17:11 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Firmware, Firmware, Firmaware was Outback 
Programming Ghost

 Ray:

Upgrading firmware on inverters and Mates requires either a board swap for 
inverters or a trip to the factory for a standard Mate. Only the Mate3 can be 
field upgraded.

Then, if you have mixed inverter firmware, there can be unintended 
consequences. For example, we upgraded a fourth inverter because of a failure. 
We were told to make it the master. When we did, the gen would disconnect after 
20 minutes. We changed it back to a slave and problem resolved.

In our society, the price for added features is added frustration.

William

On Nov 12, 2016, at 8:32 AM, Ray Walters 
<[email protected]<mailto:[email protected]>> wrote:

I second uprading all firmware on all devices.  I had a recent FXR install that 
was dropping one of the inverters (and its leg) whenever the system tried to 
sell.  Latest firmware cured the issues.
The industry is moving from us being electricians to becoming computer techs.  
Retirement looks better each day.

R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760

On 11/12/2016 6:08 AM, Wayne Irwin wrote:

Very strange that all the programming is scrambled.


Recently we had a FXR system which had been working fine for nearly six months 
come up with an incompatibility error with the slave inverter even though the 
firmware was the most recent and the same for both inverters. After several 
failed attempts to re-upgrade the inverter firmware, we took a shot at 
upgrading the Mate 3 firmware which did work. We then again tried the inverters 
and it worked. System is now working again (for now) and the programming is all 
still valid.



Wayne Irwin,
President
License #CVC56695
State Licensed Solar Contractor
Pure Energy Solar International Inc.
[email protected]<mailto:[email protected]>
http://PureEnergySolar.com
http://SolarChargingStation.net<https://solarchargingstation.net>
352 377-6527 Office
352 336-3299 Fax


The Sun Is Always Shining!


The content of this message is Pure Energy Solar Confidential. If you are not 
the intended recipient and have received this message in error, any use or 
distribution is prohibited. Please notify me immediately by reply e-mail and 
delete this message from your computer system. Thank you.


________________________________
From: RE-wrenches 
<[email protected]><mailto:[email protected]>
 on behalf of William Miller 
<[email protected]><mailto:[email protected]>
Sent: Thursday, November 10, 2016 11:26 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Outback Programming Ghost

Ray:

I have no reason to believe anyone has been meddling. No one knows the 
password. It does look like some serious glitch.

William

On Nov 10, 2016, at 6:25 PM, Ray Walters 
<[email protected]<mailto:[email protected]>> wrote:

It almost sounds like someone got in there and tried to reprogram stuff 
themselves.  Have you installed the proper anti-Gremlin devices?

R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760

On 11/10/2016 12:34 PM, William Miller wrote:
Colleagues:

I maintain an off-grid, 8 stack FX Outback system with 3 charge controllers.  
The system has been on line for about 6 years.  It got upgraded about 7 months 
ago with 2 Mate3s.

About a week ago the system shutdown, leaving the customer without power.  A 
maintenance worker started a generator and power was restored.  I did not hear 
about the situation for several days.

A maintenance supervisor was dispatched yesterday to work with me over the 
telephone to see if we could restart the system.  The system would only run if 
the inverter output breakers were all off.

I examined the system via Optics.  I was very surprised to see that the system 
programming was absolutely scrambled.  This was so much so that even the 
stacking settings were wrong.  For example, inverter 2 was set as a Master, 
which we all know will crash any system.  Other settings were also found with 
very random values.

This system was running prior to last Friday, so the stacking at least must 
have been right prior to the outage.  I am completely mystified as to how this 
could have happened.

I am in conversation with Outback who is taking this seriously.  I have not 
heard back from them yet but I am curious if anyone else has experienced this 
or anything similar.  I'd like to broaden my knowledge on this situation to 
enhance my understanding and to share any findings with the group.

Thank you in advance for any input.

William Miller



_______________________________________________
List sponsored by Redwood Alliance

List Address: 
[email protected]<mailto:[email protected]>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>

Check out or update participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org>



_______________________________________________
List sponsored by Redwood Alliance

List Address: 
[email protected]<mailto:[email protected]>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>

Check out or update participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org>




_______________________________________________
List sponsored by Redwood Alliance

List Address: 
[email protected]<mailto:[email protected]>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>

Check out or update participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org>



_______________________________________________
List sponsored by Redwood Alliance

List Address: 
[email protected]<mailto:[email protected]>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>

Check out or update participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org>

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to