First, its the added cost of the disconnecting combiner, RT breakers,
control boards, Main initiator, and extra labor for wiring and testing.
I'd say it ads another $2 to $3K of cost. Not a big deal on large
systems but for a smaller off grid project in the $10K range, its a huge
increase in cost. Folks are just going to go DIY with junk off the
internet, and the code is now under the bus.
We've successfully argued that 690.12 only applies to the PV array
circuit, not the inverter and battery output. Which has at least kept
refrigerators and heating system on during a trip. However, because
charge controllers hold residual voltage in capacitors after the array
is disconnected, we have had to add RT breakers at the charge
controllers to comply with the 30 v in 10 sec rule.
My main issue is safety: if the system trips, the customer must go onto
the roof to manually reset the combiner box to restore power. IMO, we
have inadvertently traded customer safety in the name of fire fighter
safety, not a fair bargain at all. There are numerous nuisance faults
that require reset, (CAT 5 loose connection or induced noise, faulty 9 v
battery, naughty neighbor) Firefighters will probably only ever be on
site to strap our poor customer to a back board after they fall off the
roof in the snow trying to reset their new 690.12 compliant system.
R. Ray Walters
Chief Technical Officer, RemoteSolar.com
BS Mech Engineering, 1988
Former NABCEP Certified, 2004-2016
Licensed Master ELectrician, Colorado
303 505-8760
On 3/26/17 9:22 AM, Dan Fink wrote:
Hello Ray -- Can you elaborate on why these battery-based projects are
getting killed here locally? Is it the misinterpretation by AHJs that
690.12 has to disconnect the inverter from the battery bank with giant
shunt-trip breakers? If that were the case...backup generators would
have to be controlled by rapid shutdown too, and I don't think that
can of worms has been opened yet.
Dan Fink
Professor of Solar Energy Technology, Ecotech Institute
IREC Certified Instructor™ for:
~ PV Installation Professional
~ Small Wind Installer
Executive Director, Buckville Energy
NABCEP Registered Continuing Education Providers™
970.672.4342 <tel:970.672.4342>
On Sat, Mar 25, 2017 at 8:04 PM, Ray <[email protected]
<mailto:[email protected]>> wrote:
Not to muddy the waters, but how does the SMA system deal with
690.12 Rapid Shutdown requirements in OG and GTB arrangements?
690.12 has been killing battery based projects left and right here
in Colorado.
Thanks,
R. Ray Walters
Chief Technical Officer, RemoteSolar.com
BS Mech Engineering, 1988
Former NABCEP Certified, 2004-2016
Licensed Master ELectrician, Colorado
303 505-8760 <tel:%28303%29%20505-8760>
On 3/25/17 6:46 PM, Jeff Clearwater wrote:
Hi Howie,
So Jay found this from previous posts (below). So apparently the
-40 series will work in Off-grid mode (as long as you program the
SBs separately to be in OG) but won't do the switching of modes
necessary for grid-tie backup. I plan on a call to SMA tech
support Monday morning to get to the bottom of what exactly is
lost without the RS485 comm. And to see if TLs are still going
to work as the new SIs tech sheet shows they are not supported.
why I have no idea but I intend to find out.
hope that helps.
Best,
Jeff
Begin forwarded message:
*From: *Drake <[email protected]
<mailto:[email protected]>>
*Subject: **Re: [RE-wrenches] SMA US 40 & AC coupling*
*Date: *March 13, 2017 at 10:23:56 AM PDT
*To: *RE-wrenches <[email protected]
<mailto:[email protected]>>
*Reply-To: *RE-wrenches <[email protected]
<mailto:[email protected]>>
I talked with Tim at SMA today, and the new Sunny Boy inverters
will provide taper charging with the Sunny Islands even though
no RS 485 communication is available. The Sunny Boys need to be
programmed in the off grid mode, and the Sunny Islands will take
care of the UL 1741 requirements.
The graph below shows the relation between frequency shift and %
power produced by the Sunny Boy inverters.
Emacs!
Drake Chamberlin
/Athens Electric LLC
OH License 44810
CO License 3773
NABCEP Certified Solar PV
740-448-7328 <tel:%28740%29%20448-7328>
/http://athens-electric.com/
At 11:36 AM 3/10/2017, you wrote:
I just checked with SMA and they do not have an RS485 card for
the -40 inverters. What this means is that you can set them up
to be permanently in off grid mode where the SB will follow the
frequency shift of the SI, ok for an off grid system. But for
grid tie with backup, the SB will not communicate with the SI
and will not change the SB to off grid mode. It will still work
like other generic AC coupled systems where the frequency shift
will cause the SB inverter to drop off line, but as far as I
know no throttling back will happen.
Brad
Howie Michaelson wrote:
I'm confused. Does this mean the -40 series are not compatible
with SI off grid mode? Or they don't adjust output due to
frequency shift? Or?
Howie
Howie Michaelson
NABCEP Certified Solar PV Installer™
Sun Catcher
Renewable Energy Systems Sales and Service
VT Solar Electric Incentive Partner
802-272-0004 <tel:%28802%29%20272-0004>
On Mar 25, 2017 7:59 PM, "Tump" <[email protected]
<mailto:[email protected]>> wrote:
Jeff the bad news is yer outa luck BUT they "had a work
around" that was discussed on the list a few weeks ago. I
looked quickly but didn’t see it posted. You were going to
install a RS 485 card/ module that had the soft ware to make
it work. I found this out just as these “Newest latest n
greatest inverters" were just coming out, looked at the
manual, and much to my disappointment I had to send it back
and educate my salesperson to this. Lucky for me I was able
to get the TL series. Ill keep on looking, if you don’t have
any luck I do have a contact at SMA…. at least he was there
2 weeks ago, contact me off list. Tump
On Mar 25, 2017, at 12:10 PM, Jeff Clearwater
<[email protected]
<mailto:[email protected]>> wrote:
All,
Can anyone confirm for me that the SUNNY BOY 3.0-US /
3.8-US / 5.0-US / 6.0-US / 7.0-US / 7.7-US series is or is
not supported by the Sunny Island in off-grid AC coupling
mode? The technical paper on the subject here
http://files.sma.de/dl/7910/SB-OffGrid-TI-US-en-18.pdf
<http://files.sma.de/dl/7910/SB-OffGrid-TI-US-en-18.pdf>
does not list them but I'm hoping it's cause that paper is
dated Feb '16.
I sure hope they are because that paper shows they
discontinued support the the SUNNY BOY 3000TL-US /
3800TL-US / 4000TL-US / 5000TL-US / 6000TL-US / 7000TL-US /
7700TL-US series! Why!??
Hope you have good news for me!
Best,
Jeff
--
Jeff Clearwater
Village Power Design
Renewable Energy Design & Installation
Ecovillage Design Consultant
Licensed Solar Contractor in CA - C-46
www.villagepowerdesign.com <http://www.villagepower.com/>
413-559-9763 <tel:%28413%29%20559-9763>
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
_______________________________________________
List sponsored by Redwood Alliance
List Address: [email protected]
<mailto:[email protected]>
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
<http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
List-Archive:
http://www.mail-archive.com/[email protected]/maillist.html
<http://www.mail-archive.com/[email protected]/maillist.html>
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
<http://www.re-wrenches.org/etiquette.htm>
Check out or update participant bios:
www.members.re-wrenches.org
<http://www.members.re-wrenches.org>
*[email protected]**www.SWNL.net*
Solarwinds Northernlights *//*
*/ Serving Mid Coast Maine & Northern California/**/
/**/207-832-7574 <tel:%28207%29%20832-7574> Cl.
610-517-8401 <tel:%28610%29%20517-8401> /*
*//**/Blair "TUMP" May/*
*/ ******** MAINE'S CHARTER ********
/**//**/ NABCEP "Certified PV Installer"/**/
/**/
******** MAINE'S CHARTER ********
/**/ Trace Xantrex "Certified" Dealer / Installer"/*
_______________________________________________
List sponsored by Redwood Alliance
List Address: [email protected]
<mailto:[email protected]>
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
<http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
List-Archive:
http://www.mail-archive.com/[email protected]/maillist.html
<http://www.mail-archive.com/[email protected]/maillist.html>
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
<http://www.re-wrenches.org/etiquette.htm>
Check out or update participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org>
_______________________________________________
List sponsored by Redwood Alliance
List Address:[email protected]
<mailto:[email protected]>
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
<http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
List-Archive:http://www.mail-archive.com/[email protected]/maillist.html
<http://www.mail-archive.com/[email protected]/maillist.html>
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
<http://www.re-wrenches.org/etiquette.htm>
Check out or update participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org>
-- Jeff Clearwater Village Power Design Renewable Energy Design &
Installation Ecovillage Design Consultant NABCEP™ Certified Solar
PV Installer Licensed Solar Contractor in CA - C-46
www.villagepowerdesign.com <http://www.villagepower.com>
413-559-9763 <tel:%28413%29%20559-9763>
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
_______________________________________________
List sponsored by Redwood Alliance
List Address:[email protected]
<mailto:[email protected]>
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
<http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
List-Archive:http://www.mail-archive.com/[email protected]/maillist.html
<http://www.mail-archive.com/[email protected]/maillist.html>
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
<http://www.re-wrenches.org/etiquette.htm>
Check out or update participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org>
_______________________________________________ List sponsored by
Redwood Alliance List Address: [email protected]
<mailto:[email protected]> Change listserver email
address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
<http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
List-Archive:
http://www.mail-archive.com/[email protected]/maillist.html
<http://www.mail-archive.com/[email protected]/maillist.html>
List rules & etiquette: www.re-wrenches.org/etiquette.htm
<http://www.re-wrenches.org/etiquette.htm> Check out or update
participant bios: www.members.re-wrenches.org
<http://www.members.re-wrenches.org>
_______________________________________________
List sponsored by Redwood Alliance
List Address: [email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/[email protected]/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance
List Address: [email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/[email protected]/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org