I realize this is a technical listserv, but it is interesting to compare the US practices with Europe's in this area. When one looks at the genesis of Rapid Shutdown, and how already it is changing with the most recent NECs, I see the solutions not helpful from an owner's, installers, and minimally from a firefighter's perspective.

What would really help firefighters is if the System Directoryincluded the current information AND system type: MicroInverter/AC Module, String w/oRPS, String w/ RPS, and Bimodal. It would provide firefighters with information on their level of exposure, far better than what exists today. We are adding this information to our directories.

Chris

On 3/26/2017 3:05 PM, [email protected] wrote:



Battery based rapid shut down is not simple. Much of it is up to the AHJ. You can shut down the AC output or the battery or both. Shunt trip battery breakers do not cost much more than regular battery breakers. You do need to control them though. That is what the Birdhouse and MNbattery disconnect module was designed to do. Yes, generators can also be shut down with the Birdhouse.

You may be able to use the upcoming Little SOB [Shut Off Box] soon just to shut down the PV array for battery based systems. The cost is very minimal, but you will still have to deal with PV input capacitor discharge times. Maybe 2 Little SOB’s, one on each end? They are very inexpensive. I do not mean to sound like a sales pitch here, but it seems like we are the only people working on solutions that fit these needs, so you need to know about them. MidNite has about the only solution at present for battery based shut down. You have all said it costs too much and is too complicated. We have listened.

Robin Gudgel

*MidNite solar*



On 3/26/2017 12:00 PM, Ray wrote:

First, its the added cost of the disconnecting combiner, RT breakers, control boards, Main initiator, and extra labor for wiring and testing. I'd say it ads another $2 to $3K of cost. Not a big deal on large systems but for a smaller off grid project in the $10K range, its a huge increase in cost. Folks are just going to go DIY with junk off the internet, and the code is now under the bus.

We've successfully argued that 690.12 only applies to the PV array circuit, not the inverter and battery output. Which has at least kept refrigerators and heating system on during a trip. However, because charge controllers hold residual voltage in capacitors after the array is disconnected, we have had to add RT breakers at the charge controllers to comply with the 30 v in 10 sec rule.

My main issue is safety: if the system trips, the customer must go onto the roof to manually reset the combiner box to restore power. IMO, we have inadvertently traded customer safety in the name of fire fighter safety, not a fair bargain at all. There are numerous nuisance faults that require reset, (CAT 5 loose connection or induced noise, faulty 9 v battery, naughty neighbor) Firefighters will probably only ever be on site to strap our poor customer to a back board after they fall off the roof in the snow trying to reset their new 690.12 compliant system.

R. Ray Walters
Chief Technical Officer, RemoteSolar.com
BS Mech Engineering, 1988
Former NABCEP Certified, 2004-2016
Licensed Master ELectrician, Colorado
303 505-8760
On 3/26/17 9:22 AM, Dan Fink wrote:
Hello Ray -- Can you elaborate on why these battery-based projects are getting killed here locally? Is it the misinterpretation by AHJs that 690.12 has to disconnect the inverter from the battery bank with giant shunt-trip breakers? If that were the case...backup generators would have to be controlled by rapid shutdown too, and I don't think that can of worms has been opened yet.

Dan Fink
Professor of Solar Energy Technology, Ecotech Institute
IREC Certified Instructor™ for:
~ PV Installation Professional
~ Small Wind Installer
Executive Director, Buckville Energy
NABCEP Registered Continuing Education Providers™
970.672.4342 <tel:970.672.4342>


On Sat, Mar 25, 2017 at 8:04 PM, Ray <[email protected] <mailto:[email protected]>> wrote:

    Not to muddy the waters, but how does the SMA system deal with
690.12 Rapid Shutdown requirements in OG and GTB arrangements? 690.12 has been killing battery based projects left and right
    here in Colorado.

    Thanks,

    R. Ray Walters
    Chief Technical Officer, RemoteSolar.com
    BS Mech Engineering, 1988
    Former NABCEP Certified, 2004-2016
    Licensed Master ELectrician, Colorado
    303 505-8760 <tel:%28303%29%20505-8760>

    On 3/25/17 6:46 PM, Jeff Clearwater wrote:
    Hi Howie,

    So Jay found this from previous posts (below).  So apparently
    the -40 series will work in Off-grid mode (as long as you
    program the SBs separately to be in OG) but won't do the
    switching of modes necessary for grid-tie backup.  I plan on a
    call to SMA tech support Monday morning to get to the bottom of
    what exactly is lost without the RS485 comm.  And to see if TLs
    are still going to work as the new SIs tech sheet shows they
    are not supported.  why I have no idea but I intend to find out.

    hope that helps.

    Best,

    Jeff

    Begin forwarded message:

    *From: *Drake <[email protected]
    <mailto:[email protected]>>
    *Subject: **Re: [RE-wrenches] SMA US 40 & AC coupling*
    *Date: *March 13, 2017 at 10:23:56 AM PDT
    *To: *RE-wrenches <[email protected]
    <mailto:[email protected]>>
    *Reply-To: *RE-wrenches <[email protected]
    <mailto:[email protected]>>

    I talked with Tim at SMA today, and the new  Sunny Boy
    inverters will  provide taper charging with the Sunny Islands
    even though no RS 485 communication is available. The Sunny
    Boys need to be programmed in the off grid mode, and the Sunny
    Islands will take care of the UL 1741 requirements.

    The graph below shows the relation between frequency shift and
    % power produced by the Sunny Boy inverters.
    Emacs!

    Drake Chamberlin
    /Athens Electric LLC
    OH License 44810
    CO License 3773
    NABCEP Certified Solar PV
    740-448-7328 <tel:%28740%29%20448-7328>
    /http://athens-electric.com/
    At 11:36 AM 3/10/2017, you wrote:
    I just checked with SMA and they do not have an RS485 card for
    the -40 inverters. What this means is that you can set them up
    to be permanently in off grid mode where the SB will follow
    the frequency shift of the SI, ok for an off grid system. But
    for grid tie with backup, the SB will not communicate with the
    SI and will not change the SB to off grid mode. It will still
    work like other generic AC coupled systems where the frequency
    shift will cause the SB inverter to drop off line, but as far
    as I know no throttling back will happen.

    Brad


    Howie Michaelson wrote:
    I'm confused. Does this mean the -40 series are not compatible
    with SI off grid mode? Or they don't adjust output due to
    frequency shift? Or?

    Howie
    Howie Michaelson
    NABCEP Certified Solar PV Installer™

    Sun Catcher
    Renewable Energy Systems Sales and Service
    VT Solar Electric Incentive Partner
    802-272-0004 <tel:%28802%29%20272-0004>

    On Mar 25, 2017 7:59 PM, "Tump" <[email protected]
    <mailto:[email protected]>> wrote:

        Jeff the bad news is yer outa luck BUT they "had a work
        around" that was discussed on the list a few weeks ago. I
        looked quickly but didn’t see it posted. You were going to
        install a RS 485 card/ module that had the soft ware to
        make it work. I found this out just as these “Newest
        latest n greatest inverters" were just coming out, looked
        at the manual, and much to my disappointment I had to send
        it back and educate my salesperson to this. Lucky for me I
        was able to get the TL series. Ill keep on looking, if you
        don’t have any luck I do have a contact at SMA…. at least
        he was there 2 weeks ago, contact me off list. Tump
        On Mar 25, 2017, at 12:10 PM, Jeff Clearwater
        <[email protected]
        <mailto:[email protected]>> wrote:

        All,

        Can anyone confirm for me that the SUNNY BOY 3.0-US /
        3.8-US / 5.0-US / 6.0-US / 7.0-US / 7.7-US series is or
        is not supported by the Sunny Island in off-grid AC
        coupling mode?  The technical paper on the subject here
        http://files.sma.de/dl/7910/SB-OffGrid-TI-US-en-18.pdf
        <http://files.sma.de/dl/7910/SB-OffGrid-TI-US-en-18.pdf>
        does not list them but I'm hoping it's cause that paper
        is dated Feb '16.

        I sure hope they are because that paper shows they
        discontinued support the the  SUNNY BOY 3000TL-US /
        3800TL-US / 4000TL-US / 5000TL-US / 6000TL-US / 7000TL-US
        / 7700TL-US series! Why!??

        Hope you have good news for me!

        Best,

        Jeff

-- Jeff Clearwater
        Village Power Design
        Renewable Energy Design & Installation
        Ecovillage Design Consultant

        Licensed Solar Contractor in CA - C-46
        www.villagepowerdesign.com <http://www.villagepower.com/>
        413-559-9763 <tel:%28413%29%20559-9763>
        ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

        _______________________________________________
        List sponsored by Redwood Alliance

        List Address: [email protected]
        <mailto:[email protected]>

        Change listserver email address & settings:
        http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
        <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>

        List-Archive:
        
http://www.mail-archive.com/[email protected]/maillist.html
        
<http://www.mail-archive.com/[email protected]/maillist.html>

        List rules & etiquette:
        www.re-wrenches.org/etiquette.htm
        <http://www.re-wrenches.org/etiquette.htm>

        Check out or update participant bios:
        www.members.re-wrenches.org
        <http://www.members.re-wrenches.org>


        *[email protected]**www.SWNL.net*
        Solarwinds Northernlights *//*
        */     Serving Mid Coast Maine & Northern California/**/
        /**/207-832-7574 <tel:%28207%29%20832-7574>   Cl.
        610-517-8401 <tel:%28610%29%20517-8401> /*
        *//**/Blair "TUMP" May/*

        */ ******** MAINE'S CHARTER ********
        /**//**/  NABCEP    "Certified PV Installer"/**/
        /**/
        ******** MAINE'S CHARTER ********
        /**/        Trace Xantrex "Certified" Dealer / Installer"/*





        _______________________________________________
        List sponsored by Redwood Alliance

        List Address: [email protected]
        <mailto:[email protected]>

        Change listserver email address & settings:
        http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
        <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>

        List-Archive:
        
http://www.mail-archive.com/[email protected]/maillist.html
        
<http://www.mail-archive.com/[email protected]/maillist.html>

        List rules & etiquette:
        www.re-wrenches.org/etiquette.htm
        <http://www.re-wrenches.org/etiquette.htm>

        Check out or update participant bios:
        www.members.re-wrenches.org
        <http://www.members.re-wrenches.org>


    _______________________________________________
    List sponsored by Redwood Alliance

    List Address:[email protected]
    <mailto:[email protected]>

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
    <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>

    
List-Archive:http://www.mail-archive.com/[email protected]/maillist.html
    
<http://www.mail-archive.com/[email protected]/maillist.html>

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm
    <http://www.re-wrenches.org/etiquette.htm>

    Check out or update participant bios:
    www.members.re-wrenches.org <http://www.members.re-wrenches.org>

    -- Jeff Clearwater Village Power Design Renewable Energy Design
    & Installation Ecovillage Design Consultant NABCEP™ Certified
    Solar PV Installer Licensed Solar Contractor in CA - C-46
    www.villagepowerdesign.com <http://www.villagepower.com>
    413-559-9763 <tel:%28413%29%20559-9763>
    ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

    _______________________________________________
    List sponsored by Redwood Alliance

    List Address:[email protected]
    <mailto:[email protected]>

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
    <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>

    
List-Archive:http://www.mail-archive.com/[email protected]/maillist.html
    
<http://www.mail-archive.com/[email protected]/maillist.html>

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm
    <http://www.re-wrenches.org/etiquette.htm>

    Check out or update participant bios:
    www.members.re-wrenches.org <http://www.members.re-wrenches.org>

    _______________________________________________ List sponsored
    by Redwood Alliance List Address:
    [email protected]
    <mailto:[email protected]> Change listserver
    email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
    <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
    List-Archive:
    http://www.mail-archive.com/[email protected]/maillist.html
    
<http://www.mail-archive.com/[email protected]/maillist.html>
    List rules & etiquette: www.re-wrenches.org/etiquette.htm
    <http://www.re-wrenches.org/etiquette.htm> Check out or update
    participant bios: www.members.re-wrenches.org
<http://www.members.re-wrenches.org>
_______________________________________________
List sponsored by Redwood Alliance

List Address:[email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

List Address:[email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

--
Christopher Warfel, PE
Entech Engineering, Inc.
401-466-8978
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to