Wrenches:

I am wondering why the proliferation of splices in PV leads?  We all know 
splices are a weak link. 

We allow only one connection between a module and the feeder destination-- be 
it a combiner, inverter or optimizer-- and it is an MC connector, one side of 
which is factory-made and provided by the module manufacturer. 

If one plans and pulls PV circuits with forethought, splices should not be 
necessary.   

If anyone wants to know more about how this can be accomplished, look at our 
web site or contact me off list. 

William

> On Apr 8, 2017, at 10:05 AM, Glenn Burt <[email protected]> wrote:
> 
> It is also worth noting that many of the SMA installation manuals 
> specifically say do not use wire nuts on DC wiring. 
> Of course choosing to ignore the manufacturers installation instructions 
> would be a NEC violation.
> From: Drake
> Sent: ‎4/‎8/‎2017 12:10
> To: RE-wrenches
> Subject: Re: [RE-wrenches] Polaris gone bad?
> 
> 
> At 01:35 PM 4/6/2017, you wrote:
>> Recently we interfaced with another solar install firm that has gone back to 
>> wire nuts due to this same problem.
> 
> Wire nuts have the advantage of holding the wires tight with a spring. The 
> spring follows the cold flow of the copper over the years. A screw type 
> connection does not. 
> 
> When I service an old breaker box, usually the wires are loose under the 
> screw connections, especially on the neutral and grounding bars. Often they 
> are very loose, and I bet that the screws were tight after the initial 
> installation of the equipment. 
> 
> On old industrial control equipment, I've learned the hard way to tighten all 
> screws before doing anything in the box, as wires are prone to fall out of 
> the loose screw connections. Again, these connections have the weakness of 
> being held by terminal screws, with no spring to follow the cold flow of the 
> metal. 
> 
> With wire nuts, it can be a bit tricky to know if you have a good connection, 
> as the connection is hidden under the plastic cap. It is good to pull hard on 
> each wire separately to be sure it is securely under the spring. It is 
> crucial never to mix copper and aluminum under a wire nut unless it is one 
> specifically designed for the purpose. Unless specifically listed, all out 
> door wire nuts should be in a weather proof box, and preferably taped. 
> 
> Drake Chamberlin
> Athens Electric LLC
> OH License 44810
> CO License 3773
> NABCEP Certified Solar PV 
> 740-448-7328
> http://athens-electric.com/ 
> 
>       Virus-free. www.avast.com
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/[email protected]/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to