Hi Kirk,
Yes that is correct. On a three-input inverter, you could have as many as 6 strings of modules, 2 per MPPT input, and you would not need any overcurrent protection on any of the strings. One of the beauties of inverters with multiple MPPT inputs. Along with the fact that the strings can be different lengths, orientations, and even be different modules in each string. Brian Teitelbaum AEE Solar *From:* RE-wrenches [mailto:[email protected]] *On Behalf Of *Kirk Herander *Sent:* Friday, May 26, 2017 1:01 PM *To:* RE-wrenches *Subject:* [RE-wrenches] string fusing with 3-channel MPPT inverters I’m installing a 3-input SMA 7.7kw inverter. Someone just mentioned to me string fusing, normally required for >2 inputs may not be required since each input has it’s own MPPT circuit. In essence treated like separate single MPPT inverters for fusing’s sake. I don’t believe it, but opinions? Thanks. *Kirk Herander* *Owner|Principal, VT Solar, LLC * *Celebrating our 26th Anniversary 1991-2017* *www.vermontsolarnow.com <www.vermontsolarnow.com>* dba Vermont Solar Engineering NABCEPTM 2003 Inaugural Certificant VT RE Incentive Program Partner 802.863.1202
_______________________________________________ List sponsored by Redwood Alliance List Address: [email protected] Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/[email protected]/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org