Hi boB,

Would there be any issues with delayed control of the microinverters? We do plan to use disconnects for maintenance.

Thanks,

Drake

At 06:27 PM 8/29/2017, you wrote:
Content-Type: multipart/alternative;
 boundary="------------155C815B9802686293824DDD"
Content-Language: en-US


SSRs, especially AC SSRs made from thyrisotrs (scrs and/or triacs)Â are "leaky" in general

so when turned OFF, can cause a shock.... Maybe not enough to kill you but maybe enough

to make you fall off the roof !

I'm not sure why the disconnects aren't good enough which should already be in place ?

boB

On 8/29/2017 4:53 AM, Jason Szumlanski wrote:
My vote would still be to use two single pole relays as suggested previously to kill each leg. That way you build in redundancy and dropping either leg will do the trick. In fact, it sounds like this would be even better than a two pole relay for the redundancy reason.

The other factor is whether you are using NO or NC relays. My engineer requires NO relays in these cases so they would fail in the open position only. I'm not sure how this would work, or if it would work with solid state relays. I have never dug into this. My understanding is that solid state relays fail in the closed condition (shorted). This would preclude their use in a situation where opening the circuit is the preferred failure mode. Maybe someone with some more knowledge in this area can chime in on whether SSRs are a good idea in this scenario.

Jason Szumlanski


On Mon, Aug 28, 2017 at 10:19 PM, Nick Soleil <<mailto:[email protected]>[email protected]> wrote: The one-pole relay will work for de-energizing any of the Enphase microinverters.

Nick Soleil
Field Application Engineer
Enphase Energy
Cell: <tel:%28707%29%20321-2937>707-321-2937

On Aug 28, 2017, at 6:03 PM, Drake <<mailto:[email protected]>[email protected]> wrote:

Hi Nick,

I should mention that the inverters being AC coupled are M-250s, not the new IQ series. Would that make any difference?

Thanks,


Drake


At 03:12 PM 8/28/2017, Drake wrote:
Hi Nick,


At 11:20 AM 8/28/2017, you wrote:
Content-Language: en-US
Content-Type: multipart/alternative;
        boundary="_000_56449940CA694DDAABB811FCC45A2070enphaseenergycom_"

You can use a one-pole relay. We show one-pole switching in our zero-export, self-consumption doc for PEL applications.

Nick Soleil
Field Application Engineer
Enphase Energy
Cell: <tel:%28707%29%20321-2937>707-321-2937

On Aug 28, 2017, at 6:44 AM, Drake <<mailto:[email protected] > [email protected]> wrote:

Hello Wrenches,

I am going to AC couple some Enphase inverters and found some really nice solid state, single pole relays to control them with. Enphase says I must use 2 pole relays for the control current even though the disconnects will turn off all power for maintenance.

Enphase claims that the inverters will not shut down reliably with only one line opened. This does not make sense to me in view of UL 1741. Is Enphase correct in their claim, or are there other reasons that both poles need to be opened

I want to use the solid state relays because the coil voltage is between 3 and 32 volts. This would avoid the need to add voltage dropping series resistors to protect the coil for higher battery voltages.

Alternatively, does anyone know of reasonably priced, 2 pole solid state relays?

Thanks,

Drake

Â
Drake Chamberlin
Athens Electric LLC
OH License 44810
CO License 3773
NABCEP Certified Solar PV
<tel:%28740%29%20448-7328>740-448-7328

_______________________________________________
List sponsored by Redwood Alliance

List Address: <mailto:[email protected]>[email protected]

Change listserver email address & settings:
<https://mailtrack.io/trace/link/3edab27b5ab293b8ed7e9b72f6b21719374c3d42?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=4d8b59c3f4041e3e>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: <https://mailtrack.io/trace/link/46525d1ae98ac2c9b206af627e181a5e7abef1f9?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=f1379328237c52bb>http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
<https://mailtrack.io/trace/link/37c2fa3cce2cec32c9af29b35805b1166887102d?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=f5a9d67705ba6495>www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
<https://mailtrack.io/trace/link/42b8962882456a240060cea7f870a550cf549bc6?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=8682c7a34db623bd>www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance

List Address: <mailto:[email protected]>[email protected]

Change listserver email address & settings:
<https://mailtrack.io/trace/link/3edab27b5ab293b8ed7e9b72f6b21719374c3d42?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=4d8b59c3f4041e3e>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: <https://mailtrack.io/trace/link/46525d1ae98ac2c9b206af627e181a5e7abef1f9?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=f1379328237c52bb>http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
<https://mailtrack.io/trace/link/37c2fa3cce2cec32c9af29b35805b1166887102d?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=f5a9d67705ba6495>www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
<https://mailtrack.io/trace/link/9b840d0d9b3573fe10be9ca23650f9910436d5fb?url=http%3A%2F%2Fwww.members.re-wrenches.org%2F&userId=1613865&signature=125e41a41f5138ad>www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance

List Address: <mailto:[email protected]>[email protected]

Change listserver email address & settings:
<https://mailtrack.io/trace/link/3edab27b5ab293b8ed7e9b72f6b21719374c3d42?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=4d8b59c3f4041e3e>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: <https://mailtrack.io/trace/link/46525d1ae98ac2c9b206af627e181a5e7abef1f9?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=f1379328237c52bb>http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
<https://mailtrack.io/trace/link/37c2fa3cce2cec32c9af29b35805b1166887102d?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=f5a9d67705ba6495>www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
<https://mailtrack.io/trace/link/9b840d0d9b3573fe10be9ca23650f9910436d5fb?url=http%3A%2F%2Fwww.members.re-wrenches.org%2F&userId=1613865&signature=125e41a41f5138ad>www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance

List Address: <mailto:[email protected]>[email protected]

Change listserver email address & settings:
<https://mailtrack.io/trace/link/3edab27b5ab293b8ed7e9b72f6b21719374c3d42?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=4d8b59c3f4041e3e>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: <https://mailtrack.io/trace/link/46525d1ae98ac2c9b206af627e181a5e7abef1f9?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=f1379328237c52bb>http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
<https://mailtrack.io/trace/link/e5dd443e106ab9262a64531e245e33cacc6439c3?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=1ff02acb7afaa5ce>www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
<https://mailtrack.io/trace/link/df1a46cc62f80e77abb320b6b58d2daa1df33313?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=5658938ab50f2b2d>www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

List Address: <mailto:[email protected]>[email protected]

Change listserver email address & settings:
<https://mailtrack.io/trace/link/d637b44281f438904170f585d45de0c029d858d0?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=4e891bb2cdab5fbc>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: <https://mailtrack.io/trace/link/e6c3b50ab784871396cf8aa61952a354fd078c8c?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=5c6459243bdea642>http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
<https://mailtrack.io/trace/link/e5dd443e106ab9262a64531e245e33cacc6439c3?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=1ff02acb7afaa5ce>www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
<https://mailtrack.io/trace/link/df1a46cc62f80e77abb320b6b58d2daa1df33313?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=5658938ab50f2b2d>www.members.re-wrenches.org






_______________________________________________
List sponsored by Redwood Alliance

List Address: <mailto:[email protected]>[email protected]

Change listserver email address & settings:
<http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: <http://www.mail-archive.com/[email protected]/maillist.html>http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
<http://www.re-wrenches.org/etiquette.htm>www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
<http://www.members.re-wrenches.org>www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to