On 8/30/2017 5:54 AM, Drake wrote:
Hi boB,

Would there be any issues with delayed control of the microinverters? We do  plan to  use disconnects for maintenance.

Thanks,

Drake



I highly doubt there would be enough delay to worry about anything regarding battery damage....

Even with Rule 21 or its cousins in a normal home installation.

boB






At 06:27 PM 8/29/2017, you wrote:
Content-Type: multipart/alternative;
 boundary="------------155C815B9802686293824DDD"
Content-Language: en-US


SSRs, especially AC SSRs made from thyrisotrs (scrs and/or triacs)Â are "leaky" in general

so when turned OFF, can cause a shock....  Maybe not enough to kill you but maybe enough

to make you fall off the roof !

I'm not sure why the disconnects aren't good enough which should already be in place ?

boB

On 8/29/2017 4:53 AM, Jason Szumlanski wrote:
My vote would still be to use two single pole relays as suggested previously to kill each leg. That way you build in redundancy and dropping either leg will do the trick. In fact, it sounds like this would be even better than a two pole relay for the redundancy reason.

The other factor is whether you are using NO or NC relays. My engineer requires NO relays in these cases so they would fail in the open position only. I'm not sure how this would work, or if it would work with solid state relays. I have never dug into this. My understanding is that solid state relays fail in the closed condition (shorted). This would preclude their use in a situation where opening the circuit is the preferred failure mode. Maybe someone with some more knowledge in this area can chime in on whether SSRs are a good idea in this scenario.

Jason Szumlanski


On Mon, Aug 28, 2017 at 10:19 PM, Nick Soleil <[email protected] <mailto:[email protected]>> wrote:

    The one-pole relay will work for de-energizing any of the
    Enphase microinverters.

    Nick Soleil
    Field Application Engineer
    Enphase Energy
    Cell: 707-321-2937 <tel:%28707%29%20321-2937>

    On Aug 28, 2017, at 6:03 PM, Drake
    <[email protected]
    <mailto:[email protected]>> wrote:

        Hi Nick,

        I should mention that the inverters being AC coupled are
        M-250s, not the new IQ series. Would that make any difference?

        Thanks,


        Drake


        At 03:12 PM 8/28/2017, Drake wrote:
            Hi Nick,


            At 11:20 AM 8/28/2017, you wrote:
                Content-Language: en-US
                Content-Type: multipart/alternative;
                Â Â Â Â Â Â Â Â
                
boundary="_000_56449940CA694DDAABB811FCC45A2070enphaseenergycom_"

                You can use a one-pole relay.  We show one-pole
                switching in our zero-export, self-consumption
                doc for PEL applications.

                Nick Soleil
                Field Application Engineer
                Enphase Energy
                Cell: 707-321-2937 <tel:%28707%29%20321-2937>

                On Aug 28, 2017, at 6:44 AM, Drake
                <[email protected]
                <mailto:[email protected]>> wrote:

                    Hello Wrenches,

                    I am going to AC couple some Enphase
                    inverters and found some really nice solid
                    state, single pole relays to control them
                    with. Enphase says I must use 2 pole relays
                    for the control current even though the
                    disconnects will turn off all power for
                    maintenance.

                    Enphase claims that the inverters will not
                    shut down reliably with only one line
                    opened. This does not make sense to me in
                    view of UL 1741. Is Enphase correct in their
                    claim, or are there other reasons that both
                    poles need to be opened

                    I want to use the solid state relays because
                    the coil voltage is between 3 and 32 volts.
                    This would avoid the need to add voltage
                    dropping series resistors to protect the
                    coil for higher battery voltages.

                    Alternatively, does anyone know of
                    reasonably priced, 2 pole solid state relays?

                    Thanks,

                    Drake

                    Â
                    Drake Chamberlin
                    Athens Electric LLC
                    OH License 44810
                    CO License 3773
                    NABCEP Certified Solar PV
                    740-448-7328 <tel:%28740%29%20448-7328>

                    _______________________________________________
                    List sponsored by Redwood Alliance

                    List Address:
                    [email protected]
                    <mailto:[email protected]>

                    Change listserver email address & settings:
                    
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
                    
<https://mailtrack.io/trace/link/3edab27b5ab293b8ed7e9b72f6b21719374c3d42?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=4d8b59c3f4041e3e>


                    List-Archive:
                    
http://www.mail-archive.com/[email protected]/maillist.html
                    
<https://mailtrack.io/trace/link/46525d1ae98ac2c9b206af627e181a5e7abef1f9?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=f1379328237c52bb>


                    List rules & etiquette:
                    www.re-wrenches.org/etiquette.htm
                    
<https://mailtrack.io/trace/link/37c2fa3cce2cec32c9af29b35805b1166887102d?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=f5a9d67705ba6495>

                    Check out or update participant bios:
                    www.members.re-wrenches.org
<https://mailtrack.io/trace/link/42b8962882456a240060cea7f870a550cf549bc6?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=8682c7a34db623bd>
                _______________________________________________
                List sponsored by Redwood Alliance

                List Address: [email protected]
                <mailto:[email protected]>

                Change listserver email address & settings:
                
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
                
<https://mailtrack.io/trace/link/3edab27b5ab293b8ed7e9b72f6b21719374c3d42?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=4d8b59c3f4041e3e>


                List-Archive:
                
http://www.mail-archive.com/[email protected]/maillist.html
                
<https://mailtrack.io/trace/link/46525d1ae98ac2c9b206af627e181a5e7abef1f9?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=f1379328237c52bb>


                List rules & etiquette:
                www.re-wrenches.org/etiquette.htm
                
<https://mailtrack.io/trace/link/37c2fa3cce2cec32c9af29b35805b1166887102d?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=f5a9d67705ba6495>

                Check out or update participant bios:
                www.members.re-wrenches.org
<https://mailtrack.io/trace/link/9b840d0d9b3573fe10be9ca23650f9910436d5fb?url=http%3A%2F%2Fwww.members.re-wrenches.org%2F&userId=1613865&signature=125e41a41f5138ad>
            _______________________________________________
            List sponsored by Redwood Alliance

            List Address: [email protected]
            <mailto:[email protected]>

            Change listserver email address & settings:
            http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
            
<https://mailtrack.io/trace/link/3edab27b5ab293b8ed7e9b72f6b21719374c3d42?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=4d8b59c3f4041e3e>


            List-Archive:
            
http://www.mail-archive.com/[email protected]/maillist.html
            
<https://mailtrack.io/trace/link/46525d1ae98ac2c9b206af627e181a5e7abef1f9?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=f1379328237c52bb>


            List rules & etiquette:
            www.re-wrenches.org/etiquette.htm
            
<https://mailtrack.io/trace/link/37c2fa3cce2cec32c9af29b35805b1166887102d?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=f5a9d67705ba6495>

            Check out or update participant bios:
            www.members.re-wrenches.org
<https://mailtrack.io/trace/link/9b840d0d9b3573fe10be9ca23650f9910436d5fb?url=http%3A%2F%2Fwww.members.re-wrenches.org%2F&userId=1613865&signature=125e41a41f5138ad>
        _______________________________________________
        List sponsored by Redwood Alliance

        List Address: [email protected]
        <mailto:[email protected]>

        Change listserver email address & settings:
        http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
        
<https://mailtrack.io/trace/link/3edab27b5ab293b8ed7e9b72f6b21719374c3d42?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=4d8b59c3f4041e3e>


        List-Archive:
        
http://www.mail-archive.com/[email protected]/maillist.html
        
<https://mailtrack.io/trace/link/46525d1ae98ac2c9b206af627e181a5e7abef1f9?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=f1379328237c52bb>


        List rules & etiquette:
        www.re-wrenches.org/etiquette.htm
        
<https://mailtrack.io/trace/link/e5dd443e106ab9262a64531e245e33cacc6439c3?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=1ff02acb7afaa5ce>

        Check out or update participant bios:
        www.members.re-wrenches.org
        
<https://mailtrack.io/trace/link/df1a46cc62f80e77abb320b6b58d2daa1df33313?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=5658938ab50f2b2d>

    _______________________________________________
    List sponsored by Redwood Alliance

    List Address: [email protected]
    <mailto:[email protected]>

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
    
<https://mailtrack.io/trace/link/d637b44281f438904170f585d45de0c029d858d0?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=4e891bb2cdab5fbc>


    List-Archive:
    http://www.mail-archive.com/[email protected]/maillist.html
    
<https://mailtrack.io/trace/link/e6c3b50ab784871396cf8aa61952a354fd078c8c?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=5c6459243bdea642>


    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm
    
<https://mailtrack.io/trace/link/e5dd443e106ab9262a64531e245e33cacc6439c3?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=1ff02acb7afaa5ce>

    Check out or update participant bios:
    www.members.re-wrenches.org
    
<https://mailtrack.io/trace/link/df1a46cc62f80e77abb320b6b58d2daa1df33313?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=5658938ab50f2b2d>






_______________________________________________
List sponsored by Redwood Alliance

List Address:
[email protected] <mailto:[email protected]>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>

Check out or update participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org>


_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>

Check out or update participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org/>


_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to