Same rule enforced here in Idaho & Colorado. In Idaho we even have to use Sched 
80 anywhere above the finished floor even the attic and in walls [if required].

 

----------------------------------------------------------------------------

Dana Orzel                       Great Solar Works, Inc. 

208.721.7003                       [email protected]

Idaho Contractor - # 028765          Idaho PV # 028374

NABCEP # 051112-136                       www.solarwork.biz

"Responsible Technologies for Responsible People since 1988"  

P Please consider the environment before printing this email.

 

 

From: RE-wrenches [mailto:[email protected]] On Behalf 
Of Jerry Caldwell
Sent: Wednesday, September 13, 2017 11:03 AM
To: RE-wrenches <[email protected]>
Subject: [RE-wrenches] definition of "areas of physical damage"

 

Dear Wrenches,

 

I have a residential ground mounted installation that did not pass inspection 
due to schedule 40 PVC conduit stubbing up from a trench to the inverters and 
subpanel.  The inverters and subpanel are hung on Unistrut, which is attached 
to the rear posts of the ground rack.  There is a second subpanel next to the 
main on the side of the house with schedule 40 stubbing up into it as well.

 

The inspector insists that conduit stubbing out of the ground is subject to 
physical damage and needs to be replaced with schedule 80 even though it is not 
in an area where vehicles or mobile equipment are used.  Is there a generally 
accepted definition of "areas of physical damage" as seen in 350.10 (F)?

 

The inspector has said he would consider my argument if I can provide language 
from the Code to back up my position.

 

Any help is greatly appreciated.

Jerry Caldwell

 

On Saturday, October 4, 2008 8:28 AM, Geoff Greenfield <[email protected] 
<mailto:[email protected]> > wrote:

 

thanks for input Bill, and also for tip on zipties. We have dealt with 
intermittent groundfaults caused by faulty xlp!  Had to spray water on array to 
"find" it.  PITA!  Almost makes me want to submerge the spool next time and do 
my own test. 

 

 

 

For a brighter energy future,

 

Geoff Greenfield

President

Third Sun Solar & Wind Power Ltd.

340 West State Street, Unit 25

Athens, OH 45701

 

740.597.3111    Fax 740.597.1548

www.Third-Sun.com

 

Clean Energy - Expertly Installed

 

 

 

 

 

 

----- Bill Brooks <[email protected] <mailto:[email protected]> > wrote:

> Geoff,

> 

> SS zip ties are good, but you must be very careful not to pull them tight.

> They should only be snug, not tight. These SS zip ties have been shown to

> cause ground faults in many cases. Commercial rooftops are accessible, but

> not readily accessible. Conductors must be supported properly and protected

> from physical damage. The conductors must follow structural members. If they

> leave structural members, they must be in a raceway of some kind. A variety

> of options there.

> 

> Bill.

> 

> -----Original Message-----

> From: [email protected] 
> <mailto:[email protected]> 

> [mailto:[email protected] 
> <mailto:[email protected]> ] On Behalf Of Geoff

> Greenfield

> Sent: Friday, October 03, 2008 7:19 AM

> To: RE-wrenches

> Cc: Randy; Kent Phillips

> Subject: [RE-wrenches] Protection of Conductors

> 

> Hey wrenchers... we have an internal debate going about a code section

> interpretation... "subject to physical damage".  Code compliance is a must,

> best practice is an expectation (...weighed against material and labor cost

> (prevailing wage job)). 

> 

> Application is a flat roof with no public access (locked hatch).  We are

> using DP+W "Power-tube" flat roofing system for the first time... the

> question is how to deal with the inter-row N-S wire runs... about 100 gaps

> about 24" between the E-W rows of panels.  There are plenty of 2"x2" strut

> members running under the array N-S. We will "exit" the array field in

> ridgid conduit to combiner boxes.

> 

> The flat roof system we usually use has built in wire trays... using this

> new system has brought up this question... Our options include dressing the

> XLP bundles with SS zip ties alongside the N-S struts, or using Galv. RMC,

> strapped, with bushings (or S-80 PVC) at all these walkways... or using

> Unistrut (w/cap) as a lay in wireway (to speed up labor (debatable)).

> 

> Below are some of the code references... the basic question seems to be:

> does the limited access of this roof keep us out of "subject to physical

> damage"?  What is a "Readily accessible location?"

> 

> Thanks everyone.

> 

> For a brighter energy future,

> 

> Geoff Greenfield

> President

> Third Sun Solar & Wind Power Ltd.

> 340 West State Street, Unit 25

> Athens, OH 45701

> 

> 740.597.3111    Fax 740.597.1548

> www.Third-Sun.com <http://www.Third-Sun.com> 

> 

> Clean Energy - Expertly Installed

> 

> 

> > 

> > Next, one might argue, I suppose, that the racking system itself, acts

> > as

> > protection and that the conductors should therefore, not be considered

> > to

> > be exposed.  I disagree based on NEC definition.  That stated, I

> > would

> > consider these NEC references for more perspective:

> > 

> > Pretty straightforward NEC 100 Definitions Exposed (as applied to

> > wiring

> > methods):  On or attached to the surface...  

> > 

> > NEC 300.4 gives various cases for protection against physical damage

> > requirements.  Long article.  Worth a read.  Does not address our

> > exact

> > case, but I would say that the following methods would be appropriate

> > based on similar cases...    

> > 

> > NEC 344.10 (A)(1) Galvanized steel and stainless steel RMC.  ...shall

> > be

> > permitted under all atmospheric conditions and occupancies. 

> > 

> > NEC 352.10(f) Exposed. PVC conduit shall be permitted for exposed

> > work.

> > PVC conduit used exposed in areas of physical damage shall be

> > identified

> > for the use.  FPN:  PVC conduit, Type Schedule 80, is identified for

> > areas

> > of physical damage. 

> > 

> > Also,

> > 

> > NEC 690.31(A) ...Where photovoltaic source and output circuits

> > operating

> > at maximum system voltages greater than 30 volts are installed in

> > readily

> > accesible locations, circuit conductors shall be installed in a

> > raceway.

> > 

> > One might argue, then, why don't the module interconnects have to be

> > protected, also...

> > 

> > NEC 690.31(B) is really the key to all of this:  Single-Conductor

> > Cable.

> > Single-conductor cable type USE-2, and single-conductor cable listed

> > and

> > labeled as photovoltaic (PV) wire shall be permitted in exposed

> > outdoor

> > locations in photovoltaic source circuits FOR PHOTOVOLTAIC MODULE

> > INTERCONNECTIONS within the photovoltaic array.  

> > 

> > So, I suppose that if our source circuit interconnections extend from

> > row

> > to row, then we can leave those exposed.  I don't like it, but it

> > would

> > probably have to be accepted.    

> > 

> >

> _______________________________________________

> List sponsored by Home Power magazine

> 

> List Address: [email protected] 
> <mailto:[email protected]> 

> 

> Options & settings:

> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

> 

> List-Archive:

> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

> 

> List rules & etiquette:

> www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm> 

> 

> Check out participant bios:

> www.members.re-wrenches.org <http://www.members.re-wrenches.org> 

> 

> _______________________________________________

> List sponsored by Home Power magazine

> 

> List Address: [email protected] 
> <mailto:[email protected]> 

> 

> Options & settings:

> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

> 

> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

> 

> List rules & etiquette:

> www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm> 

> 

> Check out participant bios:

> www.members.re-wrenches.org <http://www.members.re-wrenches.org> 

> 

 

_______________________________________________

List sponsored by Home Power magazine

 

List Address: [email protected] 
<mailto:[email protected]> 

 

Options & settings:

http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 

List rules & etiquette:

www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm> 

 

Check out participant bios:

www.members.re-wrenches.org <http://www.members.re-wrenches.org> 

 

 

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to