You should always specify Sched 80 for those stubs out of the ground. Makes 
sense to me that an AHJ requires it -- protect the conductors from maintenance 
tractor, lawn mower, weed whip, show shovel (Minnesota), and temperature 
differentials (transitioning from underground temps to air). But I haven't ever 
seen a formal definition of "subject to physical damage" in the code. 230.5 
describes a few examples of physical damage areas for protection (although is 
specifically talking about service entrance conductor locations) which includes 
exactly your conductor locations. Also review Articles 300.4 and 300.5. 

> On September 13, 2017 at 3:02 PM Dana <[email protected]> wrote:
> 
> 
>     Same rule enforced here in Idaho & Colorado. In Idaho we even have to use 
> Sched 80 anywhere above the finished floor even the attic and in walls [if 
> required].
> 
>      
> 
>     
> ----------------------------------------------------------------------------
> 
>     Dana Orzel                       Great Solar Works, Inc.
> 
>     208.721.7003                       [email protected]
> 
>     Idaho Contractor - # 028765          Idaho PV # 028374
> 
>     NABCEP # 051112-136                       www.solarwork.biz
> 
>     "Responsible Technologies for Responsible People since 1988" 
> 
>     P Please consider the environment before printing this email.
> 
>      
> 
>      
> 
>         From: RE-wrenches [mailto:[email protected]] 
> On Behalf Of Jerry Caldwell
>         Sent: Wednesday, September 13, 2017 11:03 AM
>         To: RE-wrenches <[email protected]>
>         Subject: [RE-wrenches] definition of "areas of physical damage"
> 
>          
> 
>         Dear Wrenches,
> 
>          
> 
>         I have a residential ground mounted installation that did not pass 
> inspection due to schedule 40 PVC conduit stubbing up from a trench to the 
> inverters and subpanel.  The inverters and subpanel are hung on Unistrut, 
> which is attached to the rear posts of the ground rack.  There is a second 
> subpanel next to the main on the side of the house with schedule 40 stubbing 
> up into it as well.
> 
>          
> 
>         The inspector insists that conduit stubbing out of the ground is 
> subject to physical damage and needs to be replaced with schedule 80 even 
> though it is not in an area where vehicles or mobile equipment are used.  Is 
> there a generally accepted definition of "areas of physical damage" as seen 
> in 350.10 (F)?
> 
>          
> 
>         The inspector has said he would consider my argument if I can provide 
> language from the Code to back up my position.
> 
>          
> 
>         Any help is greatly appreciated.
> 
>         Jerry Caldwell
> 
>          
> 
>         On Saturday, October 4, 2008 8:28 AM, Geoff Greenfield 
> <[email protected] mailto:[email protected] > wrote:
> 
>          
> 
>         thanks for input Bill, and also for tip on zipties. We have dealt 
> with intermittent groundfaults caused by faulty xlp!  Had to spray water on 
> array to "find" it.  PITA!  Almost makes me want to submerge the spool next 
> time and do my own test.
> 
>          
> 
>          
> 
>          
> 
>         For a brighter energy future,
> 
>          
> 
>         Geoff Greenfield
> 
>         President
> 
>         Third Sun Solar & Wind Power Ltd.
> 
>         340 West State Street, Unit 25
> 
>         Athens, OH 45701
> 
>          
> 
>         740.597.3111    Fax 740.597.1548http://www.Third-Sun.com
> 
>          
> 
>         Clean Energy - Expertly Installed
> 
>          
> 
>          
> 
>          
> 
>          
> 
>          
> 
>          
> 
>         ----- Bill Brooks <[email protected] mailto:[email protected] 
> > wrote:
> 
>         > Geoff,
> 
>         >
> 
>         > SS zip ties are good, but you must be very careful not to pull them 
> tight.
> 
>         > They should only be snug, not tight. These SS zip ties have been 
> shown to
> 
>         > cause ground faults in many cases. Commercial rooftops are 
> accessible, but
> 
>         > not readily accessible. Conductors must be supported properly and 
> protected
> 
>         > from physical damage. The conductors must follow structural 
> members. If they
> 
>         > leave structural members, they must be in a raceway of some kind. A 
> variety
> 
>         > of options there.
> 
>         >
> 
>         > Bill.
> 
>         >
> 
>         > -----Original Message-----
> 
>         > From: [email protected] 
> mailto:[email protected]
> 
>         > [mailto:[email protected] 
> mailto:[email protected] ] On Behalf Of Geoff
> 
>         > Greenfield
> 
>         > Sent: Friday, October 03, 2008 7:19 AM
> 
>         > To: RE-wrenches
> 
>         > Cc: Randy; Kent Phillips
> 
>         > Subject: [RE-wrenches] Protection of Conductors
> 
>         >
> 
>         > Hey wrenchers... we have an internal debate going about a code 
> section
> 
>         > interpretation... "subject to physical damage".  Code compliance is 
> a must,
> 
>         > best practice is an expectation (...weighed against material and 
> labor cost
> 
>         > (prevailing wage job)).
> 
>         >
> 
>         > Application is a flat roof with no public access (locked hatch).  
> We are
> 
>         > using DP+W "Power-tube" flat roofing system for the first time... 
> the
> 
>         > question is how to deal with the inter-row N-S wire runs... about 
> 100 gaps
> 
>         > about 24" between the E-W rows of panels.  There are plenty of 
> 2"x2" strut
> 
>         > members running under the array N-S. We will "exit" the array field 
> in
> 
>         > ridgid conduit to combiner boxes.
> 
>         >
> 
>         > The flat roof system we usually use has built in wire trays... 
> using this
> 
>         > new system has brought up this question... Our options include 
> dressing the
> 
>         > XLP bundles with SS zip ties alongside the N-S struts, or using 
> Galv. RMC,
> 
>         > strapped, with bushings (or S-80 PVC) at all these walkways... or 
> using
> 
>         > Unistrut (w/cap) as a lay in wireway (to speed up labor 
> (debatable)).
> 
>         >
> 
>         > Below are some of the code references... the basic question seems 
> to be:
> 
>         > does the limited access of this roof keep us out of "subject to 
> physical
> 
>         > damage"?  What is a "Readily accessible location?"
> 
>         >
> 
>         > Thanks everyone.
> 
>         >
> 
>         > For a brighter energy future,
> 
>         >
> 
>         > Geoff Greenfield
> 
>         > President
> 
>         > Third Sun Solar & Wind Power Ltd.
> 
>         > 340 West State Street, Unit 25
> 
>         > Athens, OH 45701
> 
>         >
> 
>         > 740.597.3111    Fax 740.597.1548
> 
>         >http://www.Third-Sun.com
> 
>         >
> 
>         > Clean Energy - Expertly Installed
> 
>         >
> 
>         >
> 
>         > >
> 
>         > > Next, one might argue, I suppose, that the racking system itself, 
> acts
> 
>         > > as
> 
>         > > protection and that the conductors should therefore, not be 
> considered
> 
>         > > to
> 
>         > > be exposed.  I disagree based on NEC definition.  That stated, I
> 
>         > > would
> 
>         > > consider these NEC references for more perspective:
> 
>         > >
> 
>         > > Pretty straightforward NEC 100 Definitions Exposed (as applied to
> 
>         > > wiring
> 
>         > > methods):  On or attached to the surface... 
> 
>         > >
> 
>         > > NEC 300.4 gives various cases for protection against physical 
> damage
> 
>         > > requirements.  Long article.  Worth a read.  Does not address our
> 
>         > > exact
> 
>         > > case, but I would say that the following methods would be 
> appropriate
> 
>         > > based on similar cases...   
> 
>         > >
> 
>         > > NEC 344.10 (A)(1) Galvanized steel and stainless steel RMC.  
> ...shall
> 
>         > > be
> 
>         > > permitted under all atmospheric conditions and occupancies.
> 
>         > >
> 
>         > > NEC 352.10(f) Exposed. PVC conduit shall be permitted for exposed
> 
>         > > work.
> 
>         > > PVC conduit used exposed in areas of physical damage shall be
> 
>         > > identified
> 
>         > > for the use.  FPN:  PVC conduit, Type Schedule 80, is identified 
> for
> 
>         > > areas
> 
>         > > of physical damage.
> 
>         > >
> 
>         > > Also,
> 
>         > >
> 
>         > > NEC 690.31(A) ...Where photovoltaic source and output circuits
> 
>         > > operating
> 
>         > > at maximum system voltages greater than 30 volts are installed in
> 
>         > > readily
> 
>         > > accesible locations, circuit conductors shall be installed in a
> 
>         > > raceway.
> 
>         > >
> 
>         > > One might argue, then, why don't the module interconnects have to 
> be
> 
>         > > protected, also...
> 
>         > >
> 
>         > > NEC 690.31(B) is really the key to all of this:  Single-Conductor
> 
>         > > Cable.
> 
>         > > Single-conductor cable type USE-2, and single-conductor cable 
> listed
> 
>         > > and
> 
>         > > labeled as photovoltaic (PV) wire shall be permitted in exposed
> 
>         > > outdoor
> 
>         > > locations in photovoltaic source circuits FOR PHOTOVOLTAIC MODULE
> 
>         > > INTERCONNECTIONS within the photovoltaic array. 
> 
>         > >
> 
>         > > So, I suppose that if our source circuit interconnections extend 
> from
> 
>         > > row
> 
>         > > to row, then we can leave those exposed.  I don't like it, but it
> 
>         > > would
> 
>         > > probably have to be accepted.   
> 
>         > >
> 
>         > >
> 
>         > _______________________________________________
> 
>         > List sponsored by Home Power magazine
> 
>         >
> 
>         > List Address: [email protected] 
> mailto:[email protected]
> 
>         >
> 
>         > Options & settings:
> 
>         > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
>         >
> 
>         > List-Archive:
> 
>         > http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
>         >
> 
>         > List rules & etiquette:
> 
>         >http://www.re-wrenches.org/etiquette.htm
> 
>         >
> 
>         > Check out participant bios:
> 
>         >http://www.members.re-wrenches.org
> 
>         >
> 
>         > _______________________________________________
> 
>         > List sponsored by Home Power magazine
> 
>         >
> 
>         > List Address: [email protected] 
> mailto:[email protected]
> 
>         >
> 
>         > Options & settings:
> 
>         > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
>         >
> 
>         > List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
>         >
> 
>         > List rules & etiquette:
> 
>         >http://www.re-wrenches.org/etiquette.htm
> 
>         >
> 
>         > Check out participant bios:
> 
>         >http://www.members.re-wrenches.org
> 
>         >
> 
>          
> 
>         _______________________________________________
> 
>         List sponsored by Home Power magazine
> 
>          
> 
>         List Address: [email protected] 
> mailto:[email protected]
> 
>          
> 
>         Options & settings:
> 
>         http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
>          
> 
>         List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
>          
> 
>         List rules & etiquette:http://www.re-wrenches.org/etiquette.htm
> 
>          
> 
>         Check out participant bios:http://www.members.re-wrenches.org
> 
>          
> 
>          
> 


 

> _______________________________________________
>     List sponsored by Redwood Alliance
> 
>     List Address: [email protected]
> 
>     Change listserver email address & settings:
>     http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
>     List-Archive: 
> http://www.mail-archive.com/[email protected]/maillist.html
> 
>     List rules & etiquette:
>     www.re-wrenches.org/etiquette.htm
> 
>     Check out or update participant bios:
>     www.members.re-wrenches.org
> 
> 


Charlie Pickard

NABCEP Certified PV Installer

952-567-4479 (cell)

952-401-7073 (office)

[email protected] mailto:[email protected]
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to