Hi August, We have understood that exception to apply only to the DC side. The inverter output circuit would fall into typical ground sizing requirements which do state that the EGC should be upsized proportionally to the other conductors that are upsized for a voltage drop.
Cheers, Dave *--* *Dave Tedeyan* *Project Engineer* *Taitem Engineering, PC* 10 Verizon Lane, Lansing, NY 14882 Voice: (607) 930-3481 x6 www.taitem.com On Mon, Oct 16, 2017 at 4:54 PM, August Goers <[email protected]> wrote: > Hi Wrenches, > > Occasionally, we need to up-size the inverter output circuit conductor > sizes (on the inverter AC side) to avoid excessive voltage drop. For > example, we typically use # 10 conductors for a microinverter branch > circuit but occasionally need to up-size to # 8s. A similar scenario might > apply when we have inverters out on on a ground mount array and then have > really long AC runs back to the main service panel location. > > Do you think the exception in NEC 690.45 to up-sizing the equipment grounds > applies to these inverter output circuits or not? It is hard to tell > whether 690.45 is meant to only include PV source and PV output circuits: > > [image: Inline image 1] > > [image: Inline image 2] > > Best, > > August > > *August Goers* > > Luminalt Energy Corporation > > o: 415.641.4000 > > www.luminalt.com > _______________________________________________ > List sponsored by Redwood Alliance > > List Address: [email protected] > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > List-Archive: http://www.mail-archive.com/[email protected]. > org/maillist.html > > List rules & etiquette: > www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > www.members.re-wrenches.org > > _______________________________________________ List sponsored by Redwood Alliance List Address: [email protected] Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/[email protected]/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org