JERRY:

I always specify separate breakers per string (175A or 250A, depending on string ampacity) mounted as close to the battery bank as possible. And I require that if I am to be engaged for maintenance (planned or unplanned) after commissioning. Shunt-trip breakers facilitate meeting Rapid Shutdown requirements.

Separate string breakers make battery maintenance and trouble shooting so much easier and well worth the first cost investment. Especially so when you have bad or weak cells/batteries, uneven string discharge/charge current, and need to isolate the culprit(s).

If I have a maintenance arrangement with the customer, individual string breakers allow me to quickly/safely perform string/battery SOH (state of Health) testing with an internal resistance tester and/or a load test on individual batteries without removing wiring/busbars/etc.

Regards,

Gary Willett PE
Icarus Engineering / Solar Services LLC

On 12/1/17 7:46 PM, Jerry Shafer wrote:
More then two banks require fusing or breakers, its best on anything amount
including one all to be located at or near the battery.
Jerry

On Dec 1, 2017 10:03 AM, "jay" <[email protected]> wrote:

HI All,

I’m wondering if anyone has a good source for battery buss bar stock.
Either pre made ones or stock I can use to make myself.

It would be for larger Rolls GEL 2v in this case but other battery
sizes/types as well.

thanks

jay

peltz power


_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://www.mail-archive.com/[email protected].
org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to