So I”m curious about the location of your breakers.  Can you elaborate about 
that?

Thanks
jay

peltz power


> On Dec 2, 2017, at 1:51 PM, Gary Willett <g...@icarussolarservices.com> wrote:
> 
> JERRY:
> 
> I always specify separate breakers per string (175A or 250A, depending on 
> string ampacity) mounted as close to the battery bank as possible. And I 
> require that if I am to be engaged for maintenance (planned or unplanned) 
> after commissioning. Shunt-trip breakers facilitate meeting Rapid Shutdown 
> requirements.
> 
> Separate string breakers make battery maintenance and trouble shooting so 
> much easier and well worth the first cost investment. Especially so when you 
> have bad or weak cells/batteries, uneven string discharge/charge current, and 
> need to isolate the culprit(s).
> 
> If I have a maintenance arrangement with the customer, individual string 
> breakers allow me to quickly/safely perform string/battery SOH (state of 
> Health) testing with an internal resistance tester and/or a load test on 
> individual batteries without removing wiring/busbars/etc.
> 
> Regards,
> 
> Gary Willett PE
> Icarus Engineering / Solar Services LLC
> 
> 

_______________________________________________