We do these all the time.  Relocation of the pv input from the load center
to the utility side of the generator transfer switch has always been our
solution.

Aaron Mandelkorn
President / Founder
Renewable Energy Outfitters
www.reosolar.com
Off Grid Depot
www.offgridnow.com
970-596-3744



On Jan 12, 2018 4:00 PM, "Jerry Shafer" <jerrysgarag...@gmail.com> wrote:

> Wayne
> We will not connect a grid tie inverter down stream of a gen-set, you
> don't want the inverter attempting to connect, when it comes right down to
> it, Why would you want to it would be a very small micro grid that if and
> when the demand is less then the inverter output would be then the gen-set
> would produce no power, volts yes amps no, then the volts climb the
> inverter discos and bam the genny has to make it all up. We have 8 k to 250
> k gennys and PV systems attached all are upstream or in switches to turn
> them off.
> Jerry
>
> On Thu, Jan 11, 2018 at 3:54 PM, Wayne Irwin <pureenergyso...@hotmail.com>
> wrote:
>
>> Hello All,
>>
>>
>> We have several customers adding generators to their homes on which we
>> have previously installed PV systems.
>>
>> Historically most generators didn't produce a clean enough 60Hz sinewave
>> to get the inverters to feed back.
>>
>> However, with the generator technology improving and the introduction of
>> inverter generators, I'm concerned that if the inverters feed back to the
>> generator it will smoke the stator.
>>
>>
>> I'm wondering if any of you have any experience/issues?  If so, what
>> solutions or recommendations do you have?
>>
>>
>> Thanks,
>>
>>
>>
>> Wayne Irwin,
>> President
>> License #CVC56695
>> State Licensed Solar Contractor
>> Pure Energy Solar International Inc.
>> wa...@pureenergysolar.com <pureenergyso...@hotmail.com>
>> <http://pureenergysolar.net/>http://PureEnergySolar.com
>> http://SolarChargingStation.net <https://solarchargingstation.net>
>> 352 377-6527 <(352)%20377-6527> Office
>> 352 336-3299 <(352)%20336-3299> Fax
>>
>>
>> The Sun Is Always Shining!
>>
>> The content of this message is Pure Energy Solar Confidential. If you are
>> not the intended recipient and have received this message in error, any use
>> or distribution is prohibited. Please notify me immediately by reply e-mail
>> and delete this message from your computer system. Thank you.
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive: http://www.mail-archive.com/re
>> -wrenc...@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>>
>>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
> org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to