Answers to questions:

 

The batteries are Discover EVL16A-A batteries. A single string of 8: 390AH @48V 
nominal. We had one fail last year, showing a significantly raised internal 
resistance when tested under a load then under charge. There is another one 
showing signs of weakness, but currently under a 30A draw it is only 0.12V 
lower than the highest battery in the mix, and 0.05V from the average battery 
voltage. Readings were: 6.0, 5.88, 6.0, 5.93, 5.92, 5.91, 5.93, 5.94 using a 
1500W space heater as a constant load during the test.

 

There are more loads than just networking and security that the client just 
recently disclosed. Gotta love the added loads to the design. There is a 
satellite DVR, 2x4 camera webcam systems, cell modem, simplisafe security 
system, chest freezer, 4 wifi range extenders to serve the less reliable 
security camera system, and 26W LED dusk-dawn light. I have already talked to 
them about thinking hard on what items can be removed for the winter at least 
(DVR is going away, and one of the camera systems too, likely the one requiring 
the wifi range extenders). All other seasons the system is fine.

 

As for the DC converter(s) we would get a voltage specific converter for any 
unique voltages, depending on the # of unique items, we would likely abandon 
that approach if it got to bee too complicated. But thank you to all that 
provided guidance there. The meanwell units seemed to have the right specs to 
do the job if we go that route. We would also install them using a LVD of some 
sort, set somewhere above the standard low voltage cutoff of the rest of the 
system. We would also only go this route if all AC loads could be removed by 
doing this, allowing us to remove the 36w idle draw of the Outback.

 

With Regards,

 

Daniel Young, 

NABCEP Certified PV Installation ProfessionalTM: Cert #031508-90

 

Lead Systems Designer for:



 <http://www.dovetailsolar.com/> www.dovetailsolar.com

Ph: 740-274-0139

 

We’ve completed nearly 400 renewable energy projects!  Check out a few in our 
photo gallery:   
<http://www.dovetailsolar.com/Our-Work.aspx?path=commercial+-+solar+electric> 
http://www.dovetailsolar.com/Our-Work.aspx?path=commercial+-+solar+electric

This email message and attachments are intended only for the addressee.  It may 
contain information which is legally privileged, confidential and exempt from 
disclosure.  If you are not the intended recipient of this message, you may not 
disclose, print, copy or disseminate this message and/or the information 
contained in the message.  If you have received this message in error, please 
reply and notify the sender (only) and delete this message along with any 
attachments.  Unauthorized interception of this email is a violation of 
criminal laws and laws covering electronic communications privacy matters. 

 

From: RE-wrenches [mailto:[email protected]] On Behalf 
Of Starlight Solar Power Systems
Sent: Tuesday, January 16, 2018 11:08 AM
To: RE-wrenches <[email protected]>
Subject: Re: [RE-wrenches] Off grid DC Loads: DC Converter

 

I too would like to know the make and model of batteries that are loosing 
capacity. In the past 5 years we have experienced abnormally high failures from 
2 brands. 

 

Larry

On Jan 15, 2018, at 2:00 PM, Jay <[email protected] 
<mailto:[email protected]> > wrote:

 

Can you tell us:

 

Battery make,model and size?

 

Jay

Peltz power. 


On Jan 15, 2018, at 12:32 PM, Daniel Young < <mailto:[email protected]> 
[email protected]> wrote:

Hello Wrenches,

 

I have a client that is running into an issue with his off grid system. The 
system is 3yrs old and they are starting to notice their AGM battery bank is 
loosing capacity, in reality they are noticing the generator is triggering more 
often. They want to try to lower the frequency of the generator triggering if 
possible.

 

The system is not occupied during much of the winter (unconditioned, which 
further hurts the battery bank capacity), but the client has a security system 
with a cell modem installed and always on. This fortunately allows Optics-RE 
access, but unfortunately based on the FNDC shunt readings, is pulling a 
consistent 150w from the battery bank. Currently the network and security 
equipment is powered from standard wall-warts running on AC.

 

I’d like to help the client extend the time between generator cycles by taking 
the network loads and powering them directly from the battery bank (the loads 
are all 12Vdc). Does anyone have any recommendations for a decent quality DC_DC 
converter that would be applicable? Given inverter losses and the efficiency of 
the typical wall-wart, I’d expect the running loads to be closer to 80-100w 
rather than the 150w we see now. The intent is to then take the inverter into 
search mode, or even switch it off, to remove the tare losses there, and also 
to take all the wasted power from the standard wall-warts and go to a single, 
more efficient dc power supply.

 

Any recommendations on a good DC_DC converter are appreciated.

 

With Regards,

 

Daniel Young, 

NABCEP Certified PV Installation ProfessionalTM: Cert #031508-90

Dovetail Solar and Wind

 

__________________________

_______________________________________________
List sponsored by Redwood Alliance

List Address:  <mailto:[email protected]> 
[email protected]

Change listserver email address & settings:
 <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org> 
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:  
<http://www.mail-archive.com/[email protected]/maillist.html> 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
 <http://www.re-wrenches.org/etiquette.htm> www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
 <http://www.members.re-wrenches.org/> www.members.re-wrenches.org

 

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to