HI Dave and Chris,

Good points, however.

I’ve had radian board failures which shut it all down.  You are correct if a 
power module goes down then it will still continue working.  

This project doesn’t need  telecomm  redundancy but close.  
And if the inverter shuts down then the AGS won’t start.  

So yea maybe a bit overkill but its a long long ways to go for a site visit.

And again,
50 amps max ( 30 really) and would be good to have built in mechanical bypass. 
Nema 1

thanks,

jay





> On Jan 19, 2018, at 7:36 AM, Dave Angelini Offgrid Solar 
> <[email protected]> wrote:
> 
> I think so also for the same reason Chris! So I guess I don't understand
> why you need the external transfer switch Jay?
> Is not the internal radian transfer switch the less is more for offgrid?  
> --Dave
> 
>> I think Radians are redundant anyway, if you parallel the output they will
>> keep going when one fails. Also, the 8KW are two x 4KW modules, both can
>> function independently. I know this because we lost one at home and kept
>> going until a replacement arrived.
>> 
>> On Thu, Jan 11, 2018 at 7:03 PM, jay <[email protected] 
>> <mailto:[email protected]>> wrote:
>> 
>>> HI all,
>>> 
>>> I’m doing a project with 2 radians in a redundant configuration.
>>> Each one would go into a transfer switch to power the common load.
>>> 
>>> I’m looking for a good, fast transfer switch.  30amp 120/240 is fine.
>>> And maybe a mechanical feature as well.
>>> Code isn’t an issue
>>> Will be off grid, remote mexico.
>>> 
>>> There is the Iota of course, but was just looking for options.
>>> 
>>> thx in advance,
>>> 
>>> jay
>>> 
>>> peltz power
>>> 
>>> 
>>> 
>>> 
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>> 
>>> List Address: [email protected] 
>>> <mailto:[email protected]>
>>> 
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
>>> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>>> 
>>> List-Archive: http://www.mail-archive.com/[email protected] 
>>> <http://www.mail-archive.com/[email protected]>.
>>> org/maillist.html
>>> 
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>
>>> 
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>>> 
>>> 
>> 
>> 
>> --
>> Chris Mason
>> NABCEP Certified Solar PV Installerâ„¢
>> Solar Design Engineer
>> Generac Generators Industrial technician
>> 
>> www.cometsolar.com <http://www.cometsolar.com/> 
>> <http://www.cometenergysystems.com <http://www.cometenergysystems.com/>>
>> 264.235.5670
>> 869.662.5670
>> Skype: netconcepts
>> _______________________________________________

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to