Hello wrenches,

I'm working on 3 off-grid telecom sites.  They are designed to operate
solar only under most conditions but the project manager ordered a
custom-built 48 VDC generators, intended to be used as the battery
charger/backup power for the site.  These are ~20 kW generators, and can
probably do about ~350Adc at 48 Vdc at the elevation that these are sited.
The battery banks are 4 x 1000 Ahr GS Nanocarbon 48 battery strings and can
gobble up the 350Adc easily when they are discharged.

While discussing the generator operation with the generator supplier, we
have found this generator isn't capable of charge control, or limiting its
own output.  The charge control functionality isn't necessary at this site
because we really just need it to keep things online until the sun returns,
a simple 54 VDC float voltage would work.  However, without the generator
being able to self-limit its output, we expect this generator to stall when
started because it can't regulate its output current and will immediately
become overloaded by the discharged batteries.

I am trying to come up with some options to rectify this serious design
issue.  One idea that immediately came to mind was putting in some parallel
solar charge controllers between the DC generator output and the battery
bank.  If the generator output could be dialed up to around 60-70 VDC,
could parallel solar charge controllers be used for charge regulation?  It
would be kind of like charging a 48 V battery bank from a 70 V battery
bank.  MPPT isn't applicable, could the max current limit in the charge
controller(s) be used to regulate charge rate?  Will the charge controllers
blow up?  If not, what brand might work.  Each site has 8 x Midnite Classic
150s but I'm open to other manufacturers if it would work.  I am open to
blowing up a charge controller in the shop but I thought it best to ask
first.

What are other ways to put this generator to use, and limit its load?



Thanks for your input/comments






-- 



Mac Lewis

*"Yo solo sé que no sé nada." -Sócrates*
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to