Wrenches,
I spoke with tech support at Outback recently and was told
the max output of the Radian at the output terminals is 8KW, even if
there is an external AC source connected to one of the AC IN terminals
of the Radian.
However, on page 18 of the GS8048 manual: "When it
(transfer relay) closes the L1 input and output terminals become
electrically common." ...same for L2 input and output. then, "the relay
contacts are limited to 55 amps per phase or leg". Since there is no 55
amp circuit breaker to protect that relay a 50 amp 2 pole breaker would
be used. This means you would have 50A X 240 Vac (12KW) at the output
terminals, correct?
Am I missing something? Thanks,
Bill