This discussion has been a great help. The house is built and the plumbing is in, but could be modified. Wood stoves are not a likely solution. I think we need a different water heating strategy.

Thank you all!

Drake



At 09:21 AM 3/15/2018, you wrote:
Content-Type: multipart/alternative;
 boundary="------------EE4E9806B711DEF636076840"
Content-Language: en-US

This is what I came up with:

The calculation is Q = mcp delta T

Water Temp out =Â  120

Water Temp in = ground source Temperature @ 50F?

delta T = 70F

m = mass flow rate. ASHRAE is the source for this. 20gals per person per day = 20 gallons x 8.34 lbs/gallon = 167lbs/day/person

cp =Â  1 BTU/lb-degree F

Q = 167 x 1 x 70 = 11,676 BTU/day/person

Divide this by the efficiency of the water heating system (I'll assume = .86)Â =11,676/.86 = 13, 577 BTU/person/day

convert to kWh if necessarym 13,577/3412 = ~4 kWh/person/day, 120 kWh/month

I checked this against one month and it seems reasonable.

Website assuming ~3.5 family size comes up with @ 400kWh per month. They approached it another way with assuming run times.

<https://www.google.com/search?safe=active&source=hp&ei=Z3KqWvXiNsGb5wKJ2Kf4DA&q=electric+water+heater+use+annual+consumption&oq=electric+water+heater+use+annually&gs_l=psy-ab.1.2.33i22i29i30k1l3.279.9222.0.12475.35.19.0.7.7.0.451.2360.0j6j4j0j1.11.0....0...1c.1.64.psy-ab..18.16.1952.0..0j0i67k1j0i131k1j0i22i30k1.0.CiU8wYZigpI>https://www.google.com/search?safe=active&source=hp&ei=Z3KqWvXiNsGb5wKJ2Kf4DA&q=electric+water+heater+use+annual+consumption&oq=electric+water+heater+use+annually&gs_l=psy-ab.1.2.33i22i29i30k1l3.279.9222.0.12475.35.19.0.7.7.0.451.2360.0j6j4j0j1.11.0....0...1c.1.64.psy-ab..18.16.1952.0..0j0i67k1j0i131k1j0i22i30k1.0.CiU8wYZigpI


Chris




On 3/15/2018 8:09 AM, Mike Kocsmiersky wrote:
Barton makes a good point with regards to the incoming ground water temperature and the amount of heat required to bring it up to shower temp.  My recollection is that ASHRAE states 20gal/person/day for the first 2 people, then 15gpd or 12gpd thereafter. However those rates vary wildly with consumers, from those that never bathe to the high schooler that needs 3 showers a day. In the northeast water heating can be up to 19% of the total household energy load for the year. Also, I would recommend the air source heat pump water heaters if you have significant humidity or an on demand unit. Water tanks are typically under insulated and can lose 2kWh/day in standby losses.
Â
Mike Kocsmiersky
Principal
Spirit Solar Inc.
(413) 734-1456
Â
Â
Â
From: Barton Churchill [<mailto:[email protected]>mailto:[email protected]]
Sent: Wednesday, March 14, 2018 7:31 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Electric Water kWh/ person
Â
You first need to know your ground temperature. Then figure a delta to 100 or so degrees. Most but not all showerheads flow 2.5gpm and showers are typically 10 minutes. You can then find a calculator online to calculate how many Btus are required to raise water temp for your delta per gallon. Convert to kWh, add some contingency and you should be good.Â

On Wednesday, March 14, 2018, <<mailto:[email protected]>[email protected]> wrote:
Hello Wrenches,

Is there a good way to estimate the power that will be consumed for electric water per person per day? We are estimating the amount of power that will be used by an all electric duplex, and the water heater amount seems high. The current model we have claims 3493 kWh/ year per 26 gallon tank will be consumed. With the two units, that would add up to 6986 kWh / year for hot water, pushing the system size to humongous for a 1300 ft sq building.

Does that seem high? There will be a maximum of 2 people per unit.

The owner is considering going to 115 V units with a 15 gallon tanks. I think the smaller tank would help, but it would seem that the amount of hot water consumed would be the main issue.

How can we get a good estimate for a per person energy usage for electric hot water? Any other suggestions are welcome.

Thank you,

Drake



--
--Â
Barton Churchill
406.587.5295 Â
2430 North 7th Bozeman, MT 59715
<http://www.solarips.com/>www.solarips.com
Image removed by sender.

Â



_______________________________________________
List sponsored by Redwood Alliance

List Address: <mailto:[email protected]>[email protected]

Change listserver email address & settings:
<http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: <http://www.mail-archive.com/[email protected]/maillist.html>http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
<http://www.re-wrenches.org/etiquette.htm>www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
<http://www.members.re-wrenches.org>www.members.re-wrenches.org


--

         Christopher Warfel, PE
       ENTECH Engineering, Inc.
PO Box 871, Block Island, RI 02807
               (401)466-8978
Â
<http://entech-engineering.com>
EEI logo



_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to