I must have missed this in your post!

https://solar.schneider-electric.com/solution/centralised-solar-power-plants-1500v/

You can navigate to their engineering team. I have found that once you
have a case number you communicate easily with e-mail.

--Dave

> I appreciate everyone's replies so far. First, we already have an
> electronic soft start control, it just needs to be reprogrammed to
> reduce the starting surge more.  Second, we are way beyond 48v land.  We
> are in the realm of commercial scale inverters of at least 500 kW to 1.5
> MW.  They will be running at 600 vdc min and probably 1500 v range. 
> Output is 480v 3 phase.
>
> When I mentioned SMA, it was not their Sunny Island, its their larger
> scale Grid tie equipment syncing to a generator.
>
> https://www.sma-america.com/industrial-systems/pv-diesel-hybrid-applications.html
>
> Most of the inverters we are looking at are primarily being used with
> batteries for peak shaving to reduce demand charges on grid. Some, such
> as Dynapower can work off grid, but I am not finding evidence that
> anyone has much real life field experience off grid.  Princeton Power
> has their 100 kW inverter in Haiti forming a micro-grid, but I have very
> few details at the moment.
>
> Even if your experience with these large battery inverters is just on
> grid, I'd love to hear about it. Offline is fine, if its not all good
> news.
>
> Thanks,
>
> Ray Walters
>
> Remote Solar
>
>
> On 4/26/18 5:23 PM, Kevin Pegg wrote:
>> Hello Ray,
>>
>> I have a couple 60/100 kW SMA Sunny Island systems out there, systems
>> with 100 kW generators, 400 kWh battery banks and generally token
>> renewable inputs. I feel with this configuration we close maxing out
>> what can be done with 48VDC.
>>
>> Getting into the MW scale scares me to be honest. I think that will be
>> well beyond what can be handled at 48VDC and is well beyond capacity of
>> the SMA systems. Really need to look into higher DC voltages to handle
>> this kind of current.
>>
>> If this was my client I would first look to the loads and see if there
>> are any alternatives to the 250 HP motor. I have learned there are often
>> massive levels of engineering overkill in the industrial world. What is
>> the duty cycle of that motor, what does it do, etc? Would they be better
>> to go directly diesel for that?
>>
>> In terms of system designs I'd investigate a direct diesel/PV interface
>> skipping battery storage. Perhaps a group of 250 kW synchronized
>> generators that can ramp up/down based on demand. Perhaps similar tech
>> to what Tesla is doing in Australia.
>>
>> Kevin
>>
>>
>> -----Original Message-----
>> From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On
>> Behalf Of Ray
>> Sent: April-25-18 12:37 PM
>> To: RE-wrenches <re-wrenches@lists.re-wrenches.org>
>> Subject: [RE-wrenches] Large Off Grid Inverter?
>>
>> Greetings Fellow Wrenches;
>>
>> We are consulting on a power system for a large off grid facility that
>> is currently operating on a 1500 kW gen set.  The loads are enormous
>> for normal off grid: in the neighborhood of 600 amps continuous at 480 v
>> 3 phase.  Surges are close to 2000 amps, but we are working on control
>> programming to bring that number down substantially.  That is due
>> primarily to a 250 Hp motor start. (that's not a typo!). EPA and local
>> regulations are dictating that the current generator be retired in the
>> near future.  Grid power is a possibility, but we need to offer a
>> viable off grid option as well.
>>
>> My question to the group: does anyone have real off grid experience with
>> large format battery based inverters?   I've heard of some micro-grid
>> systems running in Haiti on Princeton Power inverters, and Dynapower has
>> a 250 kW inverter that has a "grid forming" mode.  As we all know, it
>> is easier to make claims in spec sheets than to deliver hard motor
>> starting power in a remote location.  We need proven products, with a
>> track record of reliability.
>>
>> We are considering SMA type systems that use AC coupled PV to offset
>> fuel consumption of a generator, but those seem dependent on the
>> generator to maintain the stability of the micro grid during hard
>> starting loads. Ideally we would want to reduce the generator run time
>> to under 200 hrs/ yr and reduce its size to 500 kW.  We have excellent
>> solar resources year round, and the possibility of  limiting operations
>> during cloudy weather to meet these goals.
>>
>> Thanks,
>>
>> Ray Walters
>>
>> Remote Solar
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>


Dave Angelini Offgrid Solar
"we go where powerlines don't"
http://members.sti.net/offgridsolar/
e-mail  offgridso...@sti.net
text 209 813 0060

_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to