Eric:

Any reason not putting these loads on a gen-fed panel?

William

> On May 23, 2018, at 12:28 PM, Eric Youngren <[email protected]> wrote:
> 
> Howdy Wrenches,
> 
> I'm working on a generator powered mini-grid for an island fishing resort in 
> Alaska. They have 3 XW6048 inverter/chargers to charge batteries while the 
> diesel runs and power the loads from the batteries when the diesel shuts 
> down.  
> 
> They have several high power heating loads not typically seen in 
> battery-based off-grid electrical systems. Two 4kW hot tub heaters and six 
> 1kW infrared space heaters.  We have the 46 kW generator run-times set so 
> that the infrared heaters are (in theory) powered only while the generator is 
> running, but the hot tubs are thermostatically controlled and cycle on and 
> off every 4-5 hours or so.  
> 
> I want to make it so that these big heating loads can never be powered from 
> the batteries, and will only come on while the generator is running.  The 
> current plan is to use the Auxillary output 12V terminals from one of the XWs 
> to control power relays to switch the hot tub circuits, based on battery 
> voltage triggers. One of those hot tub circuits is fed from the main panel 
> right next to the inverters so that is easy enough.  But the other hot tub is 
> fed from a sub-panel located in a different building around 200 feet away 
> from the inverters. Pulling a pair of wires to control the second relay at 
> that sub-panel is not practical.  So, I'm looking for wireless options that 
> could control a power relay for the hot tub circuit in the remote sub-panel. 
> Ideally, the control signal would come from the same AUX terminal so both hot 
> tubs will not receive power when the battery voltage is below 50 volts or so, 
> which would indicate that the generator is not running.  
> 
> I would also like to put the infrared heaters on a similar control system so 
> that we are not dependent on people remembering to switch off the heaters 
> before the generator shuts down.  
> 
> Has any of you done this kind of thing?  Any suggestions on equipment or best 
> practices?  THANKS!
> 
> Eric Youngren
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/[email protected]/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to