All great questions.  Sounds like the battery voltage is below set-point (29V) using the heat gun

which is the thing to do to drag its V down.  The Kid should have gone back to MPPT (Bulk, Float or EQ) in a few moments

after doing that.

The sanity check for tracking is to note the Voc (105V), which you did...  Then note the PV input voltage

while the CC is in MPPT mode.  The input voltage should be somewhere between around 75% to 83%

of that Voc.  If it is higher than that (87V for 105V Voc)  then the CC is trying to reduce its output current

for some reason...  Either it thinks the battery voltage is above set-point voltage (battery temperature compensation?),

or is current limiting  (not in your case)...  OR, maybe the Kid is over temperature and is throttling back its output ?

You swapped in another Kid so that is probably not it.

If the input voltage is below the set-point voltage, (less than a out 77 volts), then that is an indication of either

a shaded panel (not the issue it would seem) or maybe a bad panel or high resistance connection or something else.

If the PV input voltage is where it should be (between around 80 volts), then the array is putting out as much as it can

in the present conditions.  So if that is the case, or the PV voltage is below max power point (< ~77V), then I

would check for bad connections or current limiting from the PV array by short circuiting the PV array and measuring

the current with a clamp on meter or whatever you have.  Make sure to turn off or disconnect one of the PV wires

from the Kid input when doing that.  If you measure much lower than you expect for that array then you've more

than likely got a bad connection in the array or wiring down on the ground in the BOS box or PV breaker maybe.

Keep us posted.

Thanks,

boB Gudgel





On 6/20/2018 7:54 AM, Tump wrote:
Are your batteries fully charged? FLA batts?, check w/ a refractometer or set the Kid to EQ. T Also check/cycle the combiner box breakers to off then on as they are center trip breakers and putting the cover on sometimes can trip them. Also while in the combiner box check for individual polarity and V/I. T
On Jun 20, 2018, at 8:06 AM, [email protected] <mailto:[email protected]> wrote:

Have you got another manufacturer's cc you could swap in temporarily?

Do you have a load on the batteries?

Sent from my 'smart' phone so please excuse spelling and typos.

------ Original message------
*From: *frenergy
*Date: *Wed, Jun 20, 2018 12:51 AM
*To: *[email protected] <mailto:[email protected]>;
*Cc: *
*Subject:*[RE-wrenches] Low output

Off-gridders,

              Small 24 volt off-grid install.....new installation, 3, 285
watt PVs in series, 4, L-16's in series, Midnight "Kid" CC.  Problem: I
cannot get more than about 200 watts (8-9 amps battery side) out of the
Kid display in full noon sun, clean PVs. Should be 700 watts plus and
about 28 amps.  Bulk/Absorb set at 29V, battery voltage at ~25 V (pulled
down with a heat gun).  I changed that Kid out for another new one> Same
issue!  I disconnected the PV wires where they land in the Kid and got
9.3 amps short circuit, 105 volts oc  Called Midnight tech support but
we couldn't come up with a good solution.  Ideas?

Thx,

Bill

Feather River Solar Electric
Bill Battagin, Owner
4291 Nelson St.
Taylorsville, CA95983 530.284.7849 <tel:95983530.284.7849>
CA Lic 874049
www.frenergy.net <http://www.frenergy.net/>


---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus


_______________________________________________
List sponsored by Redwood Alliance

List Address:[email protected] <mailto:%[email protected]>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://www.mail-archive.com/[email protected] <mailto:://www.mail-archive.com/[email protected]>/maillist.ht <http://maillist.ht/>ml

List rules & etiquette:
www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>

Check out or update participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org/>

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected] <mailto:[email protected]>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


*[email protected] <blocked::mailto:[email protected]%22%20%5Co%20%22blocked::mailto:[email protected]>**www.SWNL.net* <blocked::http://www.swnl.net/%22%20%5Co%20%22blocked::http://www.swnl.net/>
Solarwinds Northernlights *//*
*/       Serving Mid Coast Maine & Northern California/**/
/**/   207-832-7574   Cl. 610-517-8401 /*
*//**/Blair "TUMP" May/*

*/             ******** MAINE'S CHARTER ********
/**//**/NABCEP    "Certified PV Installer"/**/
/**/
              ******** MAINE'S CHARTER ********
/**/Trace Xantrex "Certified" Dealer / Installer"/*






_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to