All great questions. Sounds like the battery voltage is below set-point
(29V) using the heat gun
which is the thing to do to drag its V down. The Kid should have gone
back to MPPT (Bulk, Float or EQ) in a few moments
after doing that.
The sanity check for tracking is to note the Voc (105V), which you
did... Then note the PV input voltage
while the CC is in MPPT mode. The input voltage should be somewhere
between around 75% to 83%
of that Voc. If it is higher than that (87V for 105V Voc) then the CC
is trying to reduce its output current
for some reason... Either it thinks the battery voltage is above
set-point voltage (battery temperature compensation?),
or is current limiting (not in your case)... OR, maybe the Kid is over
temperature and is throttling back its output ?
You swapped in another Kid so that is probably not it.
If the input voltage is below the set-point voltage, (less than a out 77
volts), then that is an indication of either
a shaded panel (not the issue it would seem) or maybe a bad panel or
high resistance connection or something else.
If the PV input voltage is where it should be (between around 80 volts),
then the array is putting out as much as it can
in the present conditions. So if that is the case, or the PV voltage is
below max power point (< ~77V), then I
would check for bad connections or current limiting from the PV array by
short circuiting the PV array and measuring
the current with a clamp on meter or whatever you have. Make sure to
turn off or disconnect one of the PV wires
from the Kid input when doing that. If you measure much lower than you
expect for that array then you've more
than likely got a bad connection in the array or wiring down on the
ground in the BOS box or PV breaker maybe.
Keep us posted.
Thanks,
boB Gudgel
On 6/20/2018 7:54 AM, Tump wrote:
Are your batteries fully charged? FLA batts?, check w/ a refractometer
or set the Kid to EQ. T
Also check/cycle the combiner box breakers to off then on as they are
center trip breakers and putting the cover on sometimes can trip them.
Also while in the combiner box check for individual polarity and V/I. T
On Jun 20, 2018, at 8:06 AM, [email protected]
<mailto:[email protected]> wrote:
Have you got another manufacturer's cc you could swap in temporarily?
Do you have a load on the batteries?
Sent from my 'smart' phone so please excuse spelling and typos.
------ Original message------
*From: *frenergy
*Date: *Wed, Jun 20, 2018 12:51 AM
*To: *[email protected]
<mailto:[email protected]>;
*Cc: *
*Subject:*[RE-wrenches] Low output
Off-gridders,
Small 24 volt off-grid install.....new installation, 3, 285
watt PVs in series, 4, L-16's in series, Midnight "Kid" CC. Problem: I
cannot get more than about 200 watts (8-9 amps battery side) out of the
Kid display in full noon sun, clean PVs. Should be 700 watts plus and
about 28 amps. Bulk/Absorb set at 29V, battery voltage at ~25 V (pulled
down with a heat gun). I changed that Kid out for another new one> Same
issue! I disconnected the PV wires where they land in the Kid and got
9.3 amps short circuit, 105 volts oc Called Midnight tech support but
we couldn't come up with a good solution. Ideas?
Thx,
Bill
Feather River Solar Electric
Bill Battagin, Owner
4291 Nelson St.
Taylorsville, CA95983 530.284.7849 <tel:95983530.284.7849>
CA Lic 874049
www.frenergy.net <http://www.frenergy.net/>
---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
_______________________________________________
List sponsored by Redwood Alliance
List Address:[email protected]
<mailto:%[email protected]>
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://www.mail-archive.com/[email protected]
<mailto:://www.mail-archive.com/[email protected]>/maillist.ht <http://maillist.ht/>ml
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
<http://www.re-wrenches.org/etiquette.htm>
Check out or update participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
_______________________________________________
List sponsored by Redwood Alliance
List Address: [email protected]
<mailto:[email protected]>
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/[email protected]/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
*[email protected]
<blocked::mailto:[email protected]%22%20%5Co%20%22blocked::mailto:[email protected]>**www.SWNL.net*
<blocked::http://www.swnl.net/%22%20%5Co%20%22blocked::http://www.swnl.net/>
Solarwinds Northernlights *//*
*/ Serving Mid Coast Maine & Northern California/**/
/**/ 207-832-7574 Cl. 610-517-8401 /*
*//**/Blair "TUMP" May/*
*/ ******** MAINE'S CHARTER ********
/**//**/NABCEP "Certified PV Installer"/**/
/**/
******** MAINE'S CHARTER ********
/**/Trace Xantrex "Certified" Dealer / Installer"/*
_______________________________________________
List sponsored by Redwood Alliance
List Address: [email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/[email protected]/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance
List Address: [email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/[email protected]/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org