Hi John,

Sounds like a nightmare. I'd call hogwash on tech support saying too small 
battery bank, it is small but shouldn't cause XW to ignore settings. I don't 
suspect the SCP, it is just a display not a brain.

A full list of programmed parameters is useful.

- have you disconnected BTS and checked if behavior changed?
- setting charger = off may stop this wild charging behaviour, force it to just 
sell surplus PV, but would need manual intervention to charge up from grid ie 
after an outage if this is setup for backup as well.

I had something along this line some years ago, ignoring programming. Ended up 
doing a complete software delete and reload via XDT and complete total system 
reprogram and it started to behave properly. This is not the same as resetting 
to factory.

Kevin

From: RE-wrenches [mailto:[email protected]] On Behalf 
Of John Blittersdorf
Sent: June-27-18 8:05 PM
To: RE-wrenches <[email protected]>
Subject: [RE-wrenches] Xantrex XW4548 Grid tie sell and charge wildly out of 
control

Hello Group.
    I have a customer with an XW4548 grid tied with a Classic 200 CC, 16 
Evergreen ES-A210's,
8 Interstate L16 Batteries, with generator backup.  We have had issues with it 
not selling, selling and then charging at high rates way beyond the settings.  
This has been an ongoing problem for 6 years and currrently are 18 months into 
the 2nd battery pack and showing depleted battery life.  Xantrex tech support 
says that the battery capacity is too small and we are not setting it up 
correctly.  Before the first set of batteries had one battery explode, we had 
spent countless hours with their tech support trying to get this inverter to 
behave properly.  Even when going through every setting with tech support, we 
never got it to work quite right.  Setting to factory defaults did not work. 
Found that the default absorption time was 6 hours and the inverter battery 
charger was pushing up to 75 amps into this battery, then selling at about 40 
to 60 amps DC and then immediately charging and then selling.  I estimate this 
battery pack may have had thousands of massive charge and discharge cycles... 
good reason for the batteries to be weak now. After a few of these wild cycles, 
it would fault with DC overvoltage.  It would eventually clear the fault and do 
this crazy cycle again.  I programmed the inverter charger to the lowest 
setting of 10%,  Lowered the battery capacity setting to 200 ah from 360,  set 
the charge timer to not run during the hours we were there.  None of these 
changes made any significant difference.  We also set the maximum Sell amps AC 
down to 3 amps which should have kept it at about 720 watts but we were still 
seeing it sell up to 2500 watts.  Before we reset that,, it was selling up to 
4000 watts.

Could it be a defective SCP. There is no internet there to allow us to see the 
past performance.

Does anyone have a clue what is going on.  I have worked with Outback Radians 
in this same configuration with no problems at all.  I am about ready to rip it 
off the wall and replace it with a Radian.

John Blittersdorf
Rob Stubbins Electrical and Solar.
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to