> My two cents
>
> Some of the AC side problems On xantrax, schieder, ... systems I have come
> across  were resolved after finding the right combination of firmware
> updates and/or full PCB swaps. If the SCP is relatively new compared to the
> inverter then they may not be "talking" the same xanbus language which
> could lead to "funny" translations of settings. I had a Conext 5548 that
> would not take programming commands from a combox in a grid sell situation.
>
> There were some trace inverters that had serious ac board failures, and
> even now I have found some Conext / Schieder 4024 inverters that decided to
> see the input from a 120/240v generator as 110/208v input, which then
> shutdown the system. In the end it was a firmware update that fixed the
> issue.
>
> J Troxell
>
>
> ---------- Forwarded message ----------
> From: John Blittersdorf <[email protected]>
> To: RE-wrenches <[email protected]>
> Cc:
> Bcc:
> Date: Wed, 27 Jun 2018 23:04:37 -0400
> Subject: [RE-wrenches] Xantrex XW4548 Grid tie sell and charge wildly out
> of control
> Hello Group.
>     I have a customer with an XW4548 grid tied with a Classic 200 CC, 16
> Evergreen ES-A210's,
> 8 Interstate L16 Batteries, with generator backup.  We have had issues
> with it not selling, selling and then charging at high rates way beyond the
> settings.  This has been an ongoing problem for 6 years and currrently are
> 18 months into the 2nd battery pack and showing depleted battery life.
> Xantrex tech support says that the battery capacity is too small and we are
> not setting it up correctly.  Before the first set of batteries had one
> battery explode, we had spent countless hours with their tech support
> trying to get this inverter to behave properly.  Even when going through
> every setting with tech support, we never got it to work quite right.
> Setting to factory defaults did not work. Found that the default absorption
> time was 6 hours and the inverter battery charger was pushing up to 75 amps
> into this battery, then selling at about 40 to 60 amps DC and then
> immediately charging and then selling.  I estimate this battery pack may
> have had thousands of massive charge and discharge cycles... good reason
> for the batteries to be weak now. After a few of these wild cycles, it
> would fault with DC overvoltage.  It would eventually clear the fault and
> do this crazy cycle again.  I programmed the inverter charger to the lowest
> setting of 10%,  Lowered the battery capacity setting to 200 ah from 360,
> set the charge timer to not run during the hours we were there.  None of
> these changes made any significant difference.  We also set the maximum
> Sell amps AC down to 3 amps which should have kept it at about 720 watts
> but we were still seeing it sell up to 2500 watts.  Before we reset that,,
> it was selling up to 4000 watts.
>
> Could it be a defective SCP. There is no internet there to allow us to see
> the past performance.
>
> Does anyone have a clue what is going on.  I have worked with Outback
> Radians in this same configuration with no problems at all.  I am about
> ready to rip it off the wall and replace it with a Radian.
>
> John Blittersdorf
> Rob Stubbins Electrical and Solar.
>
>
>
> ---------- Forwarded message ----------
> From: Kevin Pegg <[email protected]>
> To: RE-wrenches <[email protected]>
> Cc:
> Bcc:
> Date: Thu, 28 Jun 2018 04:01:23 +0000
> Subject: Re: [RE-wrenches] Xantrex XW4548 Grid tie sell and charge wildly
> out of control
>
> Hi John,
>
>
>
> Sounds like a nightmare. I'd call hogwash on tech support saying too small
> battery bank, it is small but shouldn't cause XW to ignore settings. I
> don't suspect the SCP, it is just a display not a brain.
>
>
>
> A full list of programmed parameters is useful.
>
>
>
> - have you disconnected BTS and checked if behavior changed?
>
> - setting charger = off may stop this wild charging behaviour, force it to
> just sell surplus PV, but would need manual intervention to charge up from
> grid ie after an outage if this is setup for backup as well.
>
>
>
> I had something along this line some years ago, ignoring programming.
> Ended up doing a complete software delete and reload via XDT and complete
> total system reprogram and it started to behave properly. This is not the
> same as resetting to factory.
>
>
>
> Kevin
>
>
>
>
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to