This is not a knock on microinverters, but information to potentially help
save the next guy a bunch of time... This is not specific to any brand, but
for purposes of explaining I will mention it was an Enphase IQ6+ system.

One of the great advantages of microinverters, even over optimizers, in my
mind is how when a single unit fails the rest of the string just keeps on
running. I recently ran into a tripping breaker. My first diagnostic step
was to swap the string with another string's breaker to eliminate the
breaker itself as a source of the problem. That wasn't it. It just popped
the other breaker. So I probably had a dreaded wiring fault. Knowing that
pulling wires out of this particular conduit would be a nightmare, I hoped
to disconnect the string at the j-box on the roof and crossed my fingers
that the problem wasn't in the pipe. I was delighted to find out that there
was no fault in the home run wiring, so I suspected the trunk cable. To
check that I tested continuity line to line and line to ground. Nothing.
Next stop was the string terminator just to double check because I have
seen intermittent faults from a poorly installed terminator. It looked
great. I checked the waterproof caps on a couple of unused drops. Looked
good. I carefully inspected for any cuts and scuffs in the cable. No luck.
But I was convinced it was a trunk cable issue. I was just about to cut the
trunk cable in half to isolate the issue to one half of the trunk cable
when I decided to just try turning on the breaker once more.

Pop, sizzle, boom, smoke. Found the problem. It was a microinverter with an
internal fault. Fortunately, it tripped the breaker and damage was isolated
to that unit, which was swapped out and everything was fine. Problem solved.

It got me thinking about my approach to diagnosing this issue. I think next
time I will start with disconnecting the string in the junction box just
like I did this time, then test and reconnect it. My next step will be to
disconnect every micro in the string from the trunk cable and test again by
turning on the breaker. Then if it's not the trunk cable or home run wiring
I can narrow down the offending microinverter by plugging in subsets of the
string. I just got lucky because it finally failed catastrophically when I
had the modules off. The owner had reset the breaker several times before
and the system ran for hours or days without issue. There must have been an
intermittent AC fault within the bad micro that finally just manifest
itself in a more demonstrative way.

So a single point of failure can result in taking down a whole string.
That's the first time I've had that happen other than a straight-up wiring
fault.


Jason Szumlanski
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to