Wrenches:


I think the trick is to remove the roofing from the category of “likely to
become energized.”  If your wire management is such that there is no way
that any PV wire can come into contact with the metal roofing, then you are
not obligated under 250.4(A)4 to bond.



How one accomplishes this relies on one’s own ingenuity, seeing as how the
industry is way behind on developing wire management hardware.  I do not
believe ties and clips are adequate.  Instead some form of raceway is
required.  We love Snap-n-rack racking because the channel is deep enough
to accept PV wire and Gen4 MC connectors and has snap-on covers available.
The racking is your raceway and contains PV wire absolutely.  You of course
need to bond the racking and module frames, all of which is accomplished
using the SnR hardware.



We mount transition boxes near enough to the end of a string that the
factory module wire connects directly to the box without extensions
required.  We order MC connectors as bulkhead mounts and then drill and tap
Schedule 80 plugs to accept the MC connector threads.



If you invite an inspector to look under your array and nary a hint of PV
wire can be seen, you can make the case that the roofing is not likely to
become energized.



William Miller



[image: Gradient Cap_mini]
Lic 773985
millersolar.com <http://www.millersolar.com/>
805-438-5600



*From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
Behalf Of *Glenn Burt
*Sent:* Monday, June 18, 2018 11:28 AM
*To:* 'RE-wrenches'; 'AE Solar'
*Subject:* Re: [RE-wrenches] grounding on metal roofs



NEC 250.4(A)4 Also states that normally non-current-carrying electrically
conductive materials that are likely to become energized shall be connected
together and to the electrical supply source in a manner that establishes
an effective ground-fault current path.



So the logic goes if an array develops a ground fault, and the faulted
conductor contacts a metal roof surface, there is a possibility that the
roof may become energized. So for many reasons, bond the roof to ground.



-Glenn

Renewable Energy Engineer – Cadmus

Principal Engineer – Power Guru

Principal – glb, Consulting Company



*From:* RE-wrenches <re-wrenches-boun...@lists.re-wrenches.org> *On Behalf
Of *br...@willpowerelect.com
*Sent:* Monday, June 18, 2018 1:42 PM
*To:* RE-wrenches <re-wrenches@lists.re-wrenches.org>; AE Solar <
autonomousenerg...@gmail.com>
*Subject:* Re: [RE-wrenches] grounding on metal roofs



NEC 690.47 (A) requires the array to be grounded, not necessarily the roof.
If you have bonded the rails and modules and your grounding conductor goes
back to the service you should be good. 690.47 (B) allows installation of
an auxiliary grounding electrode (ground rod or building steel). Not a bad
idea in lightning prone areas. ;) Local AHJ may have different opinions.



Bruce Fiero-RMI





*"Energizing the Rogue Valley"*



*4115 S Pacific Hwy*

*Medford, OR 97501*



*P:* 541.535.3965
*F:* 541.512.0061
*E:* br...@willpowerelect.com
*W:* Willpower Electric, LLC <http://www.willpower-electric.com>



*CCB **191852*
*Oregon Electrical Contractor **C681*
*NABCEP Certified Solar (PV) Installer **031409-38*

*DUNS* *191470363*

*Energy Trust of Oregon Trade Ally **Solar (PV) Installation & Energy
Efficient Commercial Lighting Programs  *




***This email may contain information that is privileged, confidential, or
otherwise exempt from disclosure under applicable law. If you are not the
addressee, or if it appears that you have received this email in error,
please advise me immediately by reply email, keep the contents
confidential, and immediately delete the message and any attachments from
your system. *





-------- Original Message --------
Subject: Re: [RE-wrenches] grounding on metal roofs
From: "glenn.b...@glbcc.com" <glenn.b...@glbcc.com>
Date: Sun, June 17, 2018 6:17 pm
To: AE Solar <autonomousenerg...@gmail.com>
Cc: RE-wrenches <re-wrenches@lists.re-wrenches.org>

Depends on the seam profile. Same device may be used in many cases. We have
Also drilled and used the standard direct burial lugs on the underside of
the pans, at the wave when they hang over enough to get working space. Then
a horizontal run of copper wire to connect.



Don't be lulled into thinking that S-5 clamps are listed for grounding roof
pans - they are not. They are only listed for module bonding to ground.



Sent from my 'smart' phone so please excuse spelling and typos.



------ Original message------

*From: *AE Solar

*Date: *Sun, Jun 17, 2018 8:46 PM

*To: glenn.b...@glbcc.com <glenn.b...@glbcc.com>;*

*Cc: RE-wrenches;*

*Subject:Re: [RE-wrenches] grounding on metal roofs*



*thanks glenn. and what about commercial? anyone have code references
regarding grounding when doing solar on metal roofs? i thought a few years
back there was a conversation on this but i can't seem to find it.*




*Adam KatzmanAutonomous EnergiesPO Box 1245*



*Kingston, NY 12402www.autonomousenergies.com
<http://www.autonomousenergies.com>(518) 567-1468 <(518)%20567-1468>*



*On Sun, Jun 17, 2018 at 1:46 PM, glenn.b...@glbcc.com
<glenn.b...@glbcc.com> <glenn.b...@glbcc.com <glenn.b...@glbcc.com>> wrote:*

*We use the Ilsco SGB-4 ground lug on every pan under the array for
residential systems.*



*-Glenn*



*Sent from my Verizon LG Smartphone*



*------ Original message------*

*From: AE Solar*

*Date: Sun, Jun 17, 2018 12:29 PM*

*To: RE-wrenches;*

*Cc: *

*Subject:[RE-wrenches] grounding on metal roofs*



*wrenchers,*

*what methods are you all using for grounding on metal roofs? thanks*

*adam*




*Adam KatzmanAutonomous EnergiesPO Box 1245*



*Kingston, NY 12402www.autonomousenergies.com
<http://www.autonomousenergies.com>(518) 567-1468 <(518)%20567-1468>*


*------------------------------*















*_______________________________________________List sponsored by Redwood
AllianceList Address: RE-wrenches@lists.re-wrenches.org
<RE-wrenches@lists.re-wrenches.org>Change listserver email address &
settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
<http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
<http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html>List
rules & etiquette:www.re-wrenches.org/etiquette.htm
<http://www.re-wrenches.org/etiquette.htm>Check out or update participant
bios:www.members.re-wrenches.org <http://www.members.re-wrenches.org>*
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings: