Hi Ray and Dan and Chris, etc,

I agree with a lot of what you are saying, don't get me wrong...I have an
off-grid house too and I've been worrying about how module level shutdown
will be implemented and what it means for reliability and cost, especially
dc-coupled battery-based systems that really don't have or need MLPE.

I'm working on article for the Sept/Oct Homepower about rapid shutdown and
one the things I've been excited to learn about is the new Sunspec
alliance power
line communication protocol
<https://www.solarpowerworldonline.com/2017/10/communicating-get-job-done-inverters-sunspecs-rapid-shutdown-standard/>
for receivers and transmitters for RS. As Ray mentioned Midnite is already
selling their SOB
<http://www.midnitesolar.com/productPhoto.php?product_ID=671&productCatName=Software&productCat_ID=44&sortOrder=1&act=p>
(er, haha). And Tigo just got their cheapest RS MLPE option the TSF-F UL
<https://www.tigoenergy.com/library/view/TS4-F+-+Fire+Safety.pdf/> listed.
What's cool is the devices are inverter-agnostic, and don't need another
conductor for data or power running to them. But as Ray also said, they
aren't working with charge controllers, yet.

So I do think there is some good news on the horizon! From the way the 2020
NEC first draft is written, I don't perceive any chance of the 690.12 rules
really changing drastically. But something else that may change the
products we can use to meet the requirements is a new UL standard that is
being worked on- UL 3741 PV Hazard control. I don't know much about it, but
here is a list of the people
<https://csds.ul.com/Include/ViewRoster.aspx?GroupID=1782&stpNumber=3741> who
are on the Standards Technical Panel. I think a few of them are on this
listserv so maybe one of them will give us an update!

Best,
Rebekah



On Fri, Jul 6, 2018 at 4:39 PM Ray <r...@solarray.com> wrote:

>
>
>
> -------- Forwarded Message --------
> Subject: Re: [RE-wrenches] Rapid Shutdown and January 1 2019 option?
> Date: Fri, 6 Jul 2018 16:37:47 -0600
> From: Ray <r...@solarray.com> <r...@solarray.com>
> To: Rebekah Hren <rebekah.h...@gmail.com> <rebekah.h...@gmail.com>
>
> Hi Rebekah;
>
> I very much appreciated your previous posts on this. Yes, we do not need
> to disconnect the inverter and battery per previous interpretations.
> However, the RS system can and will trip for a variety of reasons, which
> disconnects the charging system.  It might take a couple of days to
> discharge the batteries, but the results are the same: rotten meat in the
> fridge and a dead battery.  If no one is home, thousands of dollars of
> battery could be ruined in a matter of weeks, if its Gel or AGM.
>
> If we get to a point where all the modules have shut down built in, and
> the Controllers also have built in disconnect so their capacitors don't
> back feed, then it won't be so hard to comply with 690.12.  In the mean
> time though, off grid should be given a clear exemption based on array size
> and Voc of the array.  We are often only wiring 2 modules in series, so we
> are already well below 100 v.   Rules designed for 600 v arrays should not
> unilaterally apply to everyone, just as 600 VAC rules don't all apply to
> 120 vac residential.  There are numerous exemptions for lower voltage AC
> situations, we are just asking that the same thinking be applied to PV.
>
> Ray Walters
> Remote Solar
> 303 505-8760
>
> On 7/6/18 2:57 PM, Rebekah Hren wrote:
>
> I believe there was a big improvement for off-grid systems as relates to
> RS in the 2017 NEC - the diagrams in 690.1(b) all show the PV system
> disconnect clearly now.  If you check out the diagrams you can see that
> energy storage/battery circuits, including the battery-based inverter
> whether AC or DC coupled, are outside the PV system boundary, thus not PV
> system circuits, thus not subject to RS.
>
> Also, the NEC 2020 1st draft report has been published
> <https://downloads.nfpa.org/codes-and-standards/all-codes-and-standards/list-of-codes-and-standards/detail?code=70&tab=nextedition>,
> so get your comments submitted!
>
> Rebekah Hren
> Member, NEC CMP-4
>
> On Fri, Jul 6, 2018 at 2:22 PM Dan Fink <danbo...@gmail.com> wrote:
>
>> I agree with you, Ray, as a purely off-grid solar installer and
>> troubleshooter. I think all that was accomplished in NEC 2017 on this issue
>> is that non-habitable structures, like the common off-grid 'power shed'
>> don't need 690.12 RS anymore.
>>
>> Dan Fink
>> Professor of Solar Energy Technology, Ecotech Institute
>> IREC Certified Instructor™ for:
>> ~ PV Installation Professional
>> ~ Small Wind Installer
>> Executive Director, Buckville Energy
>> NABCEP Registered Continuing Education Providers™
>> NABCEP Associate
>>
>> 970.672.4342
>>
>>
>>
>> On Fri, Jul 6, 2018 at 11:32 AM, Ray <r...@solarray.com> wrote:
>>
>>> Midnite has some string level and module level 690.12 disconnects that
>>> wire in like an optimizer or micro inverter, so those should be able to
>>> meet the 2019 requirements.  However beware:  they as of yet still don't
>>> have a reasonable disconnect system to disconnect the charge controller
>>> which has capacitors that back feed the PV line for up to 90 seconds.  They
>>> have a DC GFI breaker with remote trip capability but it takes 4 spaces, so
>>> with multiple charge controllers it turns into a wiring mess really fast.
>>>
>>> I actually wired in some 60 amp rated diodes on one system to get it to
>>> pass inspection; what a joke, going back to 1980s equipment to pass 2017
>>> code.    690.12 is an absolute nightmare for small off grid.  There really
>>> should be some exemptions for small arrays (under 3 kW) and under 100 vdc.
>>> Fire fighters are not going to get there till the structure is down
>>> anyway,  Response times are up to an hour for remote locations with
>>> volunteer fire departments.  Its not like in town at all;  no one is going
>>> to go on the roof on an off grid fire.
>>>
>>> On the flip side, there are real dangers created by nuisance tripping of
>>> 690.12 equipment.  Again, on grid it's a mere inconvenience, but off grid
>>> it could mean spoiled food, frozen water lines, shut down heating systems
>>> in subzero temperatures, and for the elderly: loss of their breathing
>>> machines.  I've already had a 74 year old customer climbing on their roof
>>> multiple times to reset the Rapid shutdown equipment after nuisance trips.
>>> Are we going to wait until we get someone killed in the name of "Safety"
>>> before we fix this?
>>>
>>> Ray Walters
>>> Remote Solar
>>> 303 505-8760
>>>
>>> On 7/6/18 9:55 AM, cwarfel wrote:
>>>
>>> I am wondering about the experience installers have with a DC coupled
>>> multimode system design that will comply after January 1 with what I
>>> feel is the biggest mistake/poorly guided part of NEC 2017 690, and that
>>> is 690.12.  We are installing two Outback systems with the remote c
>>> ontrolled combiner and even that won't comply after January 1 unless we 
>>> parallel
>>> more subarrays (There's safety for you, lower voltage-higher amperage!).
>>> Thanks for any insight.
>>>
>>> Chris
>>>
>>>
>>>
>>>
>>> --
>>>
>>>          Christopher Warfel, PE
>>>        ENTECH Engineering, Inc.
>>> PO Box 871, Block Island, RI 02807
>>>                (401)466-8978
>>>
>>> [image: EEI logo] <http://entech-engineering.com>
>>>
>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> List Address: RE-wrenches@lists.re-wrenches.org
>>>
>>> Change listserver email address & 
>>> settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> List-Archive: 
>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>
>>> List rules & etiquette:www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:www.members.re-wrenches.org
>>>
>>>
>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> List Address: RE-wrenches@lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> List-Archive:
>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>>>
>>>
>>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>>
>
> --
> Tel: 336.266.8800
> NABCEP Certified Solar PV Installation Professional™ 091209-85
> NC Licensed Electrical Contractor
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & 
> settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:www.members.re-wrenches.org
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>

-- 
Tel: 336.266.8800
NABCEP Certified Solar PV Installation Professional™ 091209-85
NC Licensed Electrical Contractor
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to