Thanks Rebekah, At this time, I feel like we are stranded on one option that used to be very popular with my customers.  Unlike most of the mainland, 95% of our customers want batteries. Right now, we are only going to do ground mounted dc coupled until we have a chance to evaluate the Outback system. The combiner box is large and that doesn't excite some people. Chris

On 7/6/2018 8:23 PM, Rebekah Hren wrote:
Hi Ray and Dan and Chris, etc,

I agree with a lot of what you are saying, don't get me wrong...I have an off-grid house too and I've been worrying about how module level shutdown will be implemented and what it means for reliability and cost, especially dc-coupled battery-based systems that really don't have or need MLPE.

I'm working on article for the Sept/Oct Homepower about rapid shutdown and one the things I've been excited to learn about is the new Sunspec alliance power line communication protocol <https://www.solarpowerworldonline.com/2017/10/communicating-get-job-done-inverters-sunspecs-rapid-shutdown-standard/> for receivers and transmitters for RS. As Ray mentioned Midnite is already selling their SOB <http://www.midnitesolar.com/productPhoto.php?product_ID=671&productCatName=Software&productCat_ID=44&sortOrder=1&act=p> (er, haha). And Tigo just got their cheapest RS MLPE option the TSF-F UL <https://www.tigoenergy.com/library/view/TS4-F+-+Fire+Safety.pdf/> listed. What's cool is the devices are inverter-agnostic, and don't need another conductor for data or power running to them. But as Ray also said, they aren't working with charge controllers, yet.

So I do think there is some good news on the horizon! From the way the 2020 NEC first draft is written, I don't perceive any chance of the 690.12 rules really changing drastically. But something else that may change the products we can use to meet the requirements is a new UL standard that is being worked on- UL 3741 PV Hazard control. I don't know much about it, but here is a list of the people <https://csds.ul.com/Include/ViewRoster.aspx?GroupID=1782&stpNumber=3741> who are on the Standards Technical Panel. I think a few of them are on this listserv so maybe one of them will give us an update!

Best,
Rebekah



On Fri, Jul 6, 2018 at 4:39 PM Ray <[email protected] <mailto:[email protected]>> wrote:




    -------- Forwarded Message --------
    Subject:    Re: [RE-wrenches] Rapid Shutdown and January 1 2019 option?
    Date:       Fri, 6 Jul 2018 16:37:47 -0600
    From:       Ray <[email protected]> <mailto:[email protected]>
    To:         Rebekah Hren <[email protected]>
    <mailto:[email protected]>



    Hi Rebekah;

    I very much appreciated your previous posts on this. Yes, we do
    not need to disconnect the inverter and battery per previous
    interpretations.  However, the RS system can and will trip for a
    variety of reasons, which disconnects the charging system.  It
    might take a couple of days to discharge the batteries, but the
    results are the same: rotten meat in the fridge and a dead
    battery. If no one is home, thousands of dollars of battery could
    be ruined in a matter of weeks, if its Gel or AGM.

    If we get to a point where all the modules have shut down built
    in, and the Controllers also have built in disconnect so their
    capacitors don't back feed, then it won't be so hard to comply
    with 690.12.  In the mean time though, off grid should be given a
    clear exemption based on array size and Voc of the array.  We are
    often only wiring 2 modules in series, so we are already well
    below 100 v.   Rules designed for 600 v arrays should not
    unilaterally apply to everyone, just as 600 VAC rules don't all
    apply to 120 vac residential.  There are numerous exemptions for
    lower voltage AC situations, we are just asking that the same
    thinking be applied to PV.

    Ray Walters
    Remote Solar
    303 505-8760

    On 7/6/18 2:57 PM, Rebekah Hren wrote:
    I believe there was a big improvement for off-grid systems as
    relates to RS in the 2017 NEC - the diagrams in 690.1(b) all show
    the PV system disconnect clearly now.  If you check out the
    diagrams you can see that energy storage/battery circuits,
    including the battery-based inverter whether AC or DC coupled,
    are outside the PV system boundary, thus not PV system circuits,
    thus not subject to RS.

    Also, the NEC 2020 1st draft report has been published
    
<https://downloads.nfpa.org/codes-and-standards/all-codes-and-standards/list-of-codes-and-standards/detail?code=70&tab=nextedition>,
    so get your comments submitted!

    Rebekah Hren
    Member, NEC CMP-4

    On Fri, Jul 6, 2018 at 2:22 PM Dan Fink <[email protected]
    <mailto:[email protected]>> wrote:

        I agree with you, Ray, as a purely off-grid solar installer
        and troubleshooter. I think all that was accomplished in NEC
        2017 on this issue is that non-habitable structures, like the
        common off-grid 'power shed' don't need 690.12 RS anymore.

        Dan Fink
        Professor of Solar Energy Technology, Ecotech Institute
        IREC Certified Instructor™ for:
        ~ PV Installation Professional
        ~ Small Wind Installer
        Executive Director, Buckville Energy
        NABCEP Registered Continuing Education Providers™
        NABCEP Associate

        970.672.4342


        On Fri, Jul 6, 2018 at 11:32 AM, Ray <[email protected]
        <mailto:[email protected]>> wrote:

            Midnite has some string level and module level 690.12
            disconnects that wire in like an optimizer or micro
            inverter, so those should be able to meet the 2019
            requirements.  However beware:  they as of yet still
            don't have a reasonable disconnect system to disconnect
            the charge controller which has capacitors that back feed
            the PV line for up to 90 seconds. They have a DC GFI
            breaker with remote trip capability but it takes 4
            spaces, so with multiple charge controllers it turns into
            a wiring mess really fast.

            I actually wired in some 60 amp rated diodes on one
            system to get it to pass inspection; what a joke, going
            back to 1980s equipment to pass 2017 code. 690.12 is an
            absolute nightmare for small off grid.  There really
            should be some exemptions for small arrays (under 3 kW)
            and under 100 vdc.  Fire fighters are not going to get
            there till the structure is down anyway,  Response times
            are up to an hour for remote locations with volunteer
            fire departments.  Its not like in town at all;  no one
            is going to go on the roof on an off grid fire.

            On the flip side, there are real dangers created by
            nuisance tripping of 690.12 equipment.  Again, on grid
            it's a mere inconvenience, but off grid it could mean
            spoiled food, frozen water lines, shut down heating
            systems in subzero temperatures, and for the elderly:
            loss of their breathing machines.  I've already had a 74
            year old customer climbing on their roof multiple times
            to reset the Rapid shutdown equipment after nuisance
            trips.  Are we going to wait until we get someone killed
            in the name of "Safety" before we fix this?

            Ray Walters
            Remote Solar
            303 505-8760

            On 7/6/18 9:55 AM, cwarfel wrote:

            I am wondering about the experience installers have with
            a DC coupled multimode system design that will comply
            after January 1 with what I feel is the biggest
            mistake/poorly guided part of NEC 2017 690, and that is
            690.12. We are installing two Outback systems with the
            remote controlled combiner and even that won't comply
            after January 1 unless we parallel more subarrays
            (There's safety for you, lower voltage-higher
            amperage!). Thanks for any insight.

            Chris




--
            Christopher Warfel, PE
                   ENTECH Engineering, Inc.
            PO Box 871, Block Island, RI 02807
            (401)466-8978

            EEI logo <http://entech-engineering.com>


            _______________________________________________
            List sponsored by Redwood Alliance

            List Address:[email protected]
            <mailto:[email protected]>

            Change listserver email address & settings:
            http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

            
List-Archive:http://www.mail-archive.com/[email protected]/maillist.html

            List rules & etiquette:
            www.re-wrenches.org/etiquette.htm
            <http://www.re-wrenches.org/etiquette.htm>

            Check out or update participant bios:
            www.members.re-wrenches.org
            <http://www.members.re-wrenches.org>



            _______________________________________________
            List sponsored by Redwood Alliance

            List Address: [email protected]
            <mailto:[email protected]>

            Change listserver email address & settings:
            http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

            List-Archive:
            
http://www.mail-archive.com/[email protected]/maillist.html

            List rules & etiquette:
            www.re-wrenches.org/etiquette.htm
            <http://www.re-wrenches.org/etiquette.htm>

            Check out or update participant bios:
            www.members.re-wrenches.org
            <http://www.members.re-wrenches.org>



        _______________________________________________
        List sponsored by Redwood Alliance

        List Address: [email protected]
        <mailto:[email protected]>

        Change listserver email address & settings:
        http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

        List-Archive:
        
http://www.mail-archive.com/[email protected]/maillist.html

        List rules & etiquette:
        www.re-wrenches.org/etiquette.htm
        <http://www.re-wrenches.org/etiquette.htm>

        Check out or update participant bios:
        www.members.re-wrenches.org <http://www.members.re-wrenches.org>



-- Tel: 336.266.8800
    NABCEP Certified Solar PV Installation Professional™ 091209-85
    NC Licensed Electrical Contractor


    _______________________________________________
    List sponsored by Redwood Alliance

    List Address:[email protected]
    <mailto:[email protected]>

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    
List-Archive:http://www.mail-archive.com/[email protected]/maillist.html

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm
    <http://www.re-wrenches.org/etiquette.htm>

    Check out or update participant bios:
    www.members.re-wrenches.org <http://www.members.re-wrenches.org>


    _______________________________________________
    List sponsored by Redwood Alliance

    List Address: [email protected]
    <mailto:[email protected]>

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    List-Archive:
    http://www.mail-archive.com/[email protected]/maillist.html

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm
    <http://www.re-wrenches.org/etiquette.htm>

    Check out or update participant bios:
    www.members.re-wrenches.org <http://www.members.re-wrenches.org>



--
Tel: 336.266.8800
NABCEP Certified Solar PV Installation Professional™ 091209-85
NC Licensed Electrical Contractor


_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


--

         Christopher Warfel, PE
       ENTECH Engineering, Inc.
PO Box 871, Block Island, RI 02807
               (401)466-8978

EEI logo <http://entech-engineering.com>
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to