Hello, I was called to repair a system.  24 volt 8 strings of Group 31 AGM
batteries.  I had not self-destructed yet.  For the repair, I  insisted on
the strings being on individual breakers of 20 amps on equal length #12
wire to balance the charging.  This is a battery backup system.  I
recommended replacement of the batteries and a complete rebuild and that I
felt the system was unsafe.  That was 8 years ago, no problems yet with the
system I am hoping the next repair happens before disaster.

On Mon, Jul 23, 2018 at 8:56 AM Dave Tedeyan <[email protected]> wrote:

> Since we are on the topic of bad battery practices...
>
> I may be fixing up a system that was both designed and installed very
> poorly.
> They have a 24V Outback VFXR inverter, and ten 12V AGM batteries wired into
> 5 parallel strings. I know that is a bad idea, but since they already have
> the
> equipment, are there any safety issues by re-using this equipment? It is
> for a
> grid tie battery backup system that will remain in float most of the time.
> I assume
> that the batteries will not last particularly long, but is there any harm
> in using them
> and then just getting new batteries once they fail?
>
> Stringing is shown in the attached picture.
> Cheers,
> Dave
>
>
> *--*
>
>
> *Dave Tedeyan*
> *Senior Engineer*
>
> *Taitem Engineering, PC*
> 10 Verizon Lane, Lansing, NY 14882
> Voice: (607) 930-3481 x6
> www.taitem.com
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/[email protected]/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to