>From Schneider 

RESOLUTION:  

                Product Family
                Xantrex Part
Number

                Conext XW, Conext SW, TR, Truecharge2*, XC chargers*, FSW2000*

                808-0232-01

                Trace SW, CR*, DR, RV*, C series
                130-0004-01-01


                Trucharge20+/40+*, Prosine 3.0*
                808-0231

                RS/MS*, RV/GS series*,
FSW3000*, FSW2012*, FSW3012*, Prosine 2.0*
                809-0946

                FDM 458* / FDM
Marine*
                76-0022-00

Dave Angelini Offgrid Solar
"we go where powerlines
don't"
http://members.sti.net/offgridsolar/ [1]
e-mail [email protected]
[2]
text 209 813 0060

On Mon, 6 Aug 2018 14:40:21 +0000, Lones Tuss 
wrote:      

Hello All 

The Trace Battery Temp sensor has a 100 k
negative coefficient. 

The Outback Battery temp sensor has a 10 K negative
coefficient. 

The Outback temp senor will not work with Trace equipment.


FROM: RE-wrenches [mailto:[email protected]] ON
BEHALF OF Chris Schaefer
 SENT: Saturday, August 4, 2018 2:05 PM
 TO:
re-wrenches 
 SUBJECT: [RE-wrenches] battery temp sensors for older
Trace/Xantrex inverters 

Good Day All,  

Running into a lot of missing or
chewed up battery temp sensors for the older Trace inverters. I'm looking
for potential replacements. Anyone had any luck using another vendor or do
you have a direct replacement source for these?   

Thanks,  


Christopher-        

Chris Schaefer's
  [3]
 Tel/Fax 585-229-2083 or
Cell 585-748-1870 
 5115 South Hill Road ~ Canandaigua New York 14424

www.solarandwindfx.com [4] ~ E-mail: [email protected] [5]_ 

__


Thomas Jefferson, the author of our great Constitution, once said,
"democracy" will cease to exist when you take away from those who are
willing to work and give to those who would not."           -- 




Links:
------
[1] http://members.sti.net/offgridsolar/
[2]
mailto:[email protected]
[3] http://www.solarandwindfx.com
[4]
http://www.solarandwindfx.com
[5] mailto:[email protected]
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to