The SPD-600 is evidently the one to use on the SMA TL inverters.

In older grounded PV systems, if the negative or positive is grounded directly to ground, then you could get by without an SPD connected to that grounded conductor because it is, well, already grounded and that line will rise in voltage along with the ground voltage from the strike.  However, if this grounded PV conductor  is connected through one of the r ground fault interrupters that has a 1/2 amp or slightly higher ground bonding connection, (not permanently bonded),  like the Classic or MPPT-60 and some other controllers with internal GFIs then I would think that a separate SPD line be used for positive and negative PV lines on that array. We don't want that ground bond to open on that line and risk internal arcing in the equipment.

As for arc faults, SPDs are a passive type protector and should not make any noise that might be interpreted by the sensor as arcing. Lightning itself may very well be interpreted as an arc.  I think that the Bird-House system which has a switcher supply up-stairs in the Bird-Next might have been an arc fault culprit for some TL inverters.  Sometimes it is hard for a AF detector to tell the
difference.  Hopefully they are better now.

"I have clients who have covered the SPD's in tape to keep the light from attracting small flying insects to the electronics area. "

I hear you there, Dave !  We are working on being able to coordinate the lightning strike with the insects so that the SPD also
works as a bug zapper !    :) :-)
Just kidding...

boB




On 10/9/2018 3:10 PM, Dave Angelini Offgrid Solar wrote:

We have been using Midnite SPD's since they came out. The one suggestion I have is the light is too intense. I have clients who have covered the SPD's in tape to keep the light from attracting small flying insects to the electronics area. Some places just have too many bugs :( The blue seems to bring them. I saw an inverter fan filter that was an 1/8 of an inch thick with gnats.

Fly paper will help but the battery circuit and AC panel SPD's need some help here.

*Dave Angelini Offgrid Solar "we go where powerlines don't" http://members.sti.net/offgridsolar/ e-mail [email protected] <mailto:[email protected]> text 209 813 0060*




" boB,

            To add to Drake's  wonderings, I've had a few SMA TL-40 inverters trip with an AFCI fault.  Significant hassle to get onsite and deal with it. Some with metal roofs some without, may have been lightening in the area.

Bill "




On Tue, 09 Oct 2018 17:02:32 -0400, Drake <[email protected]> wrote:

Hi boB,

I will keep putting an SPD on each string and on the AC line. Sometimes my systems end up with a lot of blue lights hanging from a wiring gutter!

Have you ever heard of any problems using the Midnite SPDs with Sunny Boy TL series inverters? So far, I don't think I've had a problem, although one TL-22, on a large metal roof, had arc fault protector trips.

Thanks,

Drake

Drake Chamberlin
/Athens Electric LLC
OH License 44810
CO License 3773
NABCEP Certified Solar PV
740-448-7328
/http://athens-electric.com/



At 01:39 PM 10/9/2018, you wrote:

    Content-Type: multipart/alternative;
     boundary="------------98C0DCEF93B9ECF248E0580B"
    Content-Language: en-US


    For an inverter with two MPPT inputs, you will need to treat the
    negatives and positive lines separate unless
    the manufacturer says something else.  That means one  SPD per
    array unfortunately.  Negative and positive connect
    to separate leads of the SPD and then ground in the middle. As
    both positive and negative PV lines rise together
    relative to ground, the SPD is supposed to clamp that rise to
    below the equipment's hi-pot voltage that they test
    to at the factory.  (i.e. common mode voltage rise) All wires
    except for ground (chassis) of the equipment are tied
    together and the hi-pot machine (sort of like a Megger ?) applies
    the high voltage between all those wires on one
    side and ground on the other to make sure the insulation doesn't
    break down inside the equipment.
    This hi-pot test goes for AC  utility input/output connections
    and DC from the PV input side.

    The SPD  has to clamp plus and minus and AC inputs to a lower
    voltage than this hipot rating but higher voltage
    than lines will see differentially in voltage.  Remember that in
    a 3-wire SPD, there is two sets of MOVs in series and
    the center is tied to ground.  If one MOV starts conducting at
    say, 500 volts DC then you can apply up to 1000
    volts  between the hot leads.  Each plus and negative line can
    rise up to 500 volts from the lightning before they
    start to clamp.  The  bigger the lightning strikes effect, the
    more current will be applied to the MOVs though and
    the clamp voltage will rise somewhat.  That's why the SPD
    arrestor voltage should be well below the hi-pot voltage,
    whatever that is...  Hi-pot voltages are quite a bit higher than
    the operating voltage.  For example, All Classic CC's
    are tested to 2270 volts DC from hot lines to ground.  It's
    something like double the operating voltage plus 1000V
    and multiply by 1.414 for DC rating.....  I'm going off memory so
    don't quote me on that but something like that.

    I think that Ray has the right idea about short connections like
    from the local generator.  Battery also.
    Just apply SPDs to anything that goes outside like an antenna.

    boB


    On 10/9/2018 8:26 AM, cwarfel wrote:


        I think something on the order of 90+% lightning strikes come
        from the utility feed, not the dc side. That has to be
        ignored if in a high strike area or grid isolated.

        On 10/8/2018 10:37 PM, Ray wrote:


            I believe you can use the SPD 300 AC on 2 strings, if PV
            neg is grounded.  You would connect the green to ground
            (or PV neg) and then connect the red to one string pos,
            and connect the black to the other string pos.  This
            would be limited to 300 v also.  I haven't tried that
            exact configuration, but I have used the 300 AC to
            protect both the AC in and AC out on 120 vac inverters. 
            I also believe you can use a 600 DC version, and wire as
            I mentioned, but the LEDs won't light. If you are using
            ungrounded inverters, then I think you would need an SPD
            for each string in order to protect both the pos and neg
            of each string, like you've been doing.

            Maybe someone from Midnite can clarify this.

            As far as it being worth it, I haven't had lightning
            related damage since I started using the Midnite SPDs,
            and I used to have system damage every year.  If you are
            not in lightning country, or the install is in a low spot
            with less likelihood of taking a hit, you might be able
            to skimp.  But for some of these off grid ridge top
            installs, I consider it a must. Some times I don't
            install one on the gen circuit, if its really close.



            Ray Walters
            Remote Solar
            303 505-8760

            On 10/8/18 4:03 PM, Drake wrote:

                Hello Wrenches,

                Do you use surge arrestors with multi MPPT input
                string inverters? Do you put a separate arrestor on
                each MPPT input? I find it sort of pricey using a
                Midnite Solar arrestor on each string, but have been
                doing that. Is there a less expensive approach that
                is effective?

                I believe the Midnite units are the best. Are they
                worth the expense?

                Thank you,

                Drake


                Drake Chamberlin
                /Athens Electric LLC
                OH License 44810
                CO License 3773
                NABCEP Certified Solar PV
                740-448-7328
                /http://athens-electric.com/




                _______________________________________________
                List sponsored by Redwood Alliance

                List Address:
                [email protected]
                <mailto:[email protected]>

                Change listserver email address & settings:
                
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

                List-Archive:
                
http://www.mail-archive.com/[email protected]/maillist.html

                List rules & etiquette:
                www.re-wrenches.org/etiquette.htm
                <http://www.re-wrenches.org/etiquette.htm>

                Check out or update participant bios:
                www.members.re-wrenches.org
                <http://www.members.re-wrenches.org>





            _______________________________________________
            List sponsored by Redwood Alliance

            List Address:
            [email protected]
            <mailto:[email protected]>

            Change listserver email address & settings:
            http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

            List-Archive:
            
http://www.mail-archive.com/[email protected]/maillist.html

            List rules & etiquette:
            www.re-wrenches.org/etiquette.htm
            <http://www.re-wrenches.org/etiquette.htm>

            Check out or update participant bios:
            www.members.re-wrenches.org
            <http://www.members.re-wrenches.org>


--
                 Christopher Warfel, PE
               ENTECH Engineering, Inc.
        PO Box 871, Block Island, RI 02807
                       (401)466-8978

        EEI logo <http://entech-engineering.com>



        _______________________________________________
        List sponsored by Redwood Alliance

        List Address:
        [email protected]
        <mailto:[email protected]>

        Change listserver email address & settings:
        http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

        List-Archive:
        
http://www.mail-archive.com/[email protected]/maillist.html

        List rules & etiquette:
        www.re-wrenches.org/etiquette.htm
        <http://www.re-wrenches.org/etiquette.htm>

        Check out or update participant bios:
        www.members.re-wrenches.org <http://www.members.re-wrenches.org>




    _______________________________________________
    List sponsored by Redwood Alliance

    List Address: [email protected]

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
    <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>


    List-Archive:
    http://www.mail-archive.com/[email protected]/maillist.html


    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm
    <http://www.re-wrenches.org/etiquette.htm>

    Check out or update participant bios:
    www.members.re-wrenches.org <http://www.members.re-wrenches.org/>

--

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to