Hi August, The limitation with the Sunny Island, (if you don't go 3 phase), is a quad stack of 6048s in a 120/240 system last I checked. I think you can double that with your islanded Sunny Boys. The 6048 had a ridiculously high surge rating so it can cover pretty high loads.
If you go 3 phase with the multicluster box its above 100 kW. We have done a 64 kWh Blue Ion and it seems to work extremely well. The Sunny Island SOC algorithm and Blue Ion SOC don't track perfectly but both are useful. I think you can stack 10 x 8048 Radians but AC coupling then becomes a problem. Good luck with this. On Tue, Jan 8, 2019, 3:49 PM August Goers <[email protected] wrote: > Hi Wrenches, > > We have a new potential client who wants a 60 kW PV system and a battery > backup system with 200 kWh of storage. The system will be grid tied and the > client insists on some sort of lithium battery technology and doesn't want > Tesla. For such a ridiculously large system, what kind of equipment would > you recommend? I'm thinking maybe Sunny Islands with Blue Ion LiFePO4 > batteries? > > Best, August > > *August Goers* > > Luminalt Energy Corporation > > > > _______________________________________________ > List sponsored by Redwood Alliance > > List Address: [email protected] > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > List-Archive: > http://www.mail-archive.com/[email protected]/maillist.html > > List rules & etiquette: > www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > www.members.re-wrenches.org > >
_______________________________________________ List sponsored by Redwood Alliance List Address: [email protected] Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/[email protected]/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org