HI Mac,

I wondering if you know which SMA  GT inverters communication with the SI?

thx

jay



> On Jan 8, 2019, at 1:02 PM, Mac Lewis <[email protected]> wrote:
> 
> Hi August,
> 
> The limitation with the Sunny Island, (if you don't go 3 phase), is a quad 
> stack of 6048s in a 120/240 system last I checked. I think you can double 
> that with your islanded Sunny Boys. The 6048 had a ridiculously high surge 
> rating so it can cover pretty high loads.
> 
> If you go 3 phase with the multicluster box its above 100 kW.
> 
> We have done a 64 kWh Blue Ion and it seems to work extremely well. The Sunny 
> Island SOC algorithm and Blue Ion SOC don't track perfectly but both are 
> useful.
> 
> I think you can stack 10 x 8048 Radians but AC coupling then becomes a 
> problem.
> 
> Good luck with this.
> 
> On Tue, Jan 8, 2019, 3:49 PM August Goers <[email protected] 
> <mailto:[email protected]> wrote:
> Hi Wrenches,
> 
> We have a new potential client who wants a 60 kW PV system and a battery 
> backup system with 200 kWh of storage. The system will be grid tied and the 
> client insists on some sort of lithium battery technology and doesn't want 
> Tesla. For such a ridiculously large system, what kind of equipment would you 
> recommend? I'm thinking maybe Sunny Islands with Blue Ion LiFePO4 batteries?
> 
> Best, August
> August Goers
> 
> Luminalt Energy Corporation
> 
> 
> 
>  
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: [email protected] 
> <mailto:[email protected]>
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
> 
> List-Archive: 
> http://www.mail-archive.com/[email protected]/maillist.html 
> <http://www.mail-archive.com/[email protected]/maillist.html>
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>
> 
> Check out or update participant bios:
> www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/[email protected]/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to