William,

I will need system specific information to make any comments on your reported 
communications issues.

As far as the recommendations for 6 foot CAT5, that was done 5 to 7 years ago 
for a specific application, and it is still valid when working with large 
systems, where you are pushing the Xanbus network maximum.

Sandra
[email protected]

From: RE-wrenches [mailto:[email protected]] On Behalf 
Of William Miller
Sent: Friday, February 1, 2019 1:41 PM
To: RE-wrenches <[email protected]>
Subject: Re: [RE-wrenches] No Communication to XW CC


[External email: Use caution with links and attachments]

________________________________


Sandra:

I have frequent communications problems with XW xanbus devices.  At one point I 
was told by Schneider tech support that all Cat5 leads need to be a minimum of 
6 feet in length.  Is this true?

William


From: RE-wrenches 
[mailto:[email protected]<mailto:[email protected]>]
 On Behalf Of Sandra Herrera
Sent: Friday, February 1, 2019 8:44 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] No Communication to XW CC

Hello Drake.
In the Xanbus network, you have devices with power such as inverters, and other 
devices without power.
You can not connect an SCP directly to an MPPT60, because both SCP and MPPT60 
have no power, but if you have an inverter in the network, it should give 
sufficient power for the devices.
There are several reasons why a device that is still fully functional but not 
show up on the network. This ranges from the minor CAT5 cable problem to maybe 
a damage communication card. Some may be solved with a simple factory reset, 
and other cases may require a replacement.
However, without the full context of the conversation, I do not see how 
connecting ComBox or SCP will make any difference. Although, the ComBox as an 
AC power supply it will not power the Xanbus network, it is only to power the 
ComBox.
As far as connecting ComBox directly to your laptop without a router, this is 
possible, but you need to change your network setting on the laptop.
Sandra
[email protected]<mailto:[email protected]>



From: RE-wrenches 
[mailto:[email protected]<mailto:[email protected]>]
 On Behalf Of 
[email protected]<mailto:[email protected]>
Sent: Friday, February 1, 2019 8:28 AM
To: RE-wrenches 
<[email protected]<mailto:[email protected]>>
Subject: [RE-wrenches] No Communication to XW CC


[External email: Use caution with links and attachments]

________________________________


Hello Wrenches,

We have a situation on a repair job (that I didn't install), where the charge 
controllers are not showing up on the SCP. There are 3 charge controllers, two 
600 V and one 150 volt units. There is a ComBox and and SCP.

One Schneider tech recommended that I unplug the SCP and plug a laptop directly 
into the ComBox..The manual shows a router being used.

Can a laptop be plugged directly in to a ComBox? Will this be helpful in 
finding the missing CCs?

Even with new Ethernet cables, the CCs don't show up.

Thanks,

Drake



______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to