Yes, microinverters and now I would think other typologies will be included with module level disconnects becoming more common and I guess required. So, as long as you can disconnect each non microinverter individually, and microinverter strings by one disconnect, you should meeting the intent.  Labeling is key too. I still think that this was a big error and the stated intention of making rooftop pv safer has not been achieved.  The wheel fell off of this "safety improvement". Technology is catching up though. Anyone on a roof better assume the array is live until proven otherwise no matter what installation type it is. Chris

On 2/25/2019 5:45 PM, Rebekah Hren wrote:
I should follow up to say that yes Chris is correct - each inverter does require its own equipment disconnects (AC and DC) per 690.15, but those can be connectors, like for Enphase, or any number of other things, as detailed in 690.15. If you try to keep system and equipment disconnect rules separate in your mind, I think it helps - although of course the inverter AC disconnect for a string inverter will often also be serving as the system disconnect, so there is a lot of overlap.


On Mon, Feb 25, 2019 at 5:39 PM Rebekah Hren <[email protected] <mailto:[email protected]>> wrote:

    Hi Chris and William
    There was certainly no intention to mandate that all inverters
    connect to one OCPD/disconnect.But 705.12(B)(1) in 2017 clarifies
    that systems like Enphase could have multiple inverters on one
    breaker, certainly not  that all inverters in a building have to
    be on breaker.

    If an AHJ raises this issue the answer is as follows:

    A single inverter can be called a single PV system  - see the
    diagrams in 690.1(b). A building can have multiple PV systems per
    690.4(D).

    Each PV system can have no more than 6 system disconnect switches
    per 690.13(D). Circuit breakers are allowed as PV system
    disconnects - 690.13(F)(1).

    There is no limit to the number of PV systems allowed on a building.

    Therefore, each inverter can be connected to its own breaker/disco
    for that PV system.


    A few further comments :

    A single PV system can have a single inverter, or multiple
    inverters. It is up to you to define the system and the PV system
    disconnect(s) associated with it.

    OR multiple inverters (power sources) can be connected to a single
    OCPD/disco up to the manufacturer's maximum OCPD limit, per
    705.12(B)(1).

    OR multiple (let's say 10) inverters in a single system can each
    have their own OCPD/disco and ONE master PV system disconnect for
    all 10 inverters to follow the fules of 690.13(D).


    Lots of options, all allowed!


    Best,

    Rebekah

    Principal, CMP-4


    On Mon, Feb 25, 2019 at 5:31 PM Christopher Warfel
    <[email protected]
    <mailto:[email protected]>> wrote:

        Just reading more slowly, each inverter has to be on its on
        separate disconnect means. You cannot put multiple inverters
        on the same disconnecting means unless there are individual
        disconnecting means upstream.

        On 2/25/2019 10:53 AM, William Miller wrote:

        Friends:

        I have an NEC code question on an upcoming project.  It is a
        home that has an existing 8 kW ground-mounted grid-tied
        system.  The owner wants to add another 10 kW of grid-tied
        PV.  My question is about 705.12, point of connection.
        Specifically section (D)(1).  That section states:

        /The source interconnection of one or more inverters
        installed in one system shall be made at a dedicated circuit
        breaker or fusible disconnecting means./

        So if there are going to be two inverters on premise, do the
        outputs have to be aggregated to connect via one circuit
        breaker?  This might be difficult to do as the exiting
        inverter is connected via a different sub-panel than the one
        that is planned to receive the new inverter output.

        This article
        <https://iaeimagazine.org/magazine/2014/01/16/load-side-pv-connections/>
        addresses the question.

        I would be very grateful if any of you can share any
        experience you might have in interpreting this section of the
        code.

        Thanks in advance.

        William


        _______________________________________________
        List sponsored by Redwood Alliance

        List Address:[email protected]  
<mailto:[email protected]>

        Change listserver email address & settings:
        http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

        
List-Archive:http://www.mail-archive.com/[email protected]/maillist.html

        List rules & etiquette:
        www.re-wrenches.org/etiquette.htm  
<http://www.re-wrenches.org/etiquette.htm>

        Check out or update participant bios:
        www.members.re-wrenches.org  <http://www.members.re-wrenches.org>

--                         Christopher Warfel
             ENTECH Engineering, Inc.
        PO Box 871, Block Island, RI 02807
            401-466-8978
        <http://entech-engineering.com>


        _______________________________________________
        List sponsored by Redwood Alliance

        List Address: [email protected]
        <mailto:[email protected]>

        Change listserver email address & settings:
        http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

        List-Archive:
        
http://www.mail-archive.com/[email protected]/maillist.html

        List rules & etiquette:
        www.re-wrenches.org/etiquette.htm
        <http://www.re-wrenches.org/etiquette.htm>

        Check out or update participant bios:
        www.members.re-wrenches.org <http://www.members.re-wrenches.org>



-- Tel: 336.266.8800
    NABCEP Certified Solar PV Installation Professional™ 091209-85
    NC Licensed Electrical Contractor



--
Tel: 336.266.8800
NABCEP Certified Solar PV Installation Professional™ 091209-85
NC Licensed Electrical Contractor

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

--
            Christopher Warfel
                     ENTECH Engineering, Inc.
PO Box 871, Block Island, RI 02807
                                401-466-8978
<http://entech-engineering.com>


_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to