Wrenches,

            I'm tackling a huge residential system that requires back-feeding the grid at 480 volts, delta (no neutral, right?). We're going to GT 30-50 KW.  The SMA SB30000TL-US-10 is one of the few inverters (apparently) that can do this, which I'm planning to use.  The inverter can be fed up to 1,000 vdc,OC. 1,000 volt array is new to me.  I assume they have to accept the high voltage because its a 30K inverter with only 2 MPPT strings.  My question: Other than not getting fried during installation, what's different about wiring the array or anything else on the DC side?  I don't see anything in our current (2014) code cycle on this that's different than 600 volt. Tips, advice?

            Any links, past webinars, whatever else also helpful would be welcome.

Thanks,

Bill

Feather River Solar Electric
Bill Battagin, Owner
4291 Nelson St.
Taylorsville, CA 95983
530.284.7849
CA Lic 874049
www.frenergy.net



---