Bill – A couple items:

  1.  The 30000TL-US (along with all the STP TL-US line) has been discontinued, 
and I believe this particular model has been completely sold out.  Some 
Distributors may have stock remaining or you may have already obtained the 
unit.  As Blake noted, if you use this model, it is critical to pay attention 
to service connection requirements.  See technical document: 
https://files.sma.de/dl/7418/STP-US_MV_Trafo-TI-en-13.pdf and particularly the 
table and notes below on page 3.
  2.  Not sure where the array is located on this residential property, but 
single family dwelling roofs are limited to 600V (2014 NEC 690.7(C) or 2017 NEC 
690.7).  If that is where the array is, perhaps the 33kW CORE1-US-41 inverter 
would be an option – it is designed to work with high efficiency down to the 
350VDC level.  The 50kW and 62.5kW units are designed to work best with arrays 
closer to the 1000VDC limit – ok if the array is a large ground mount or 
possibly non-dwelling unit roof. This inverter family requires a 277/480 wye 
service, so a transformer would be required.  Transformer requirements for the 
CORE1 family can also be found in the above linked document.
Best-
Mike

From: RE-wrenches <[email protected]> On Behalf Of 
Blake Gleason
Sent: Thursday, April 18, 2019 5:20 PM
To: RE-wrenches <[email protected]>
Subject: Re: [RE-wrenches] 1000 volt

Bill,

Watch out for the 480 delta with the SMA inverter.  Even though the product 
literature says it works, it doesn't.  If there's ever a ground fault (PV 
system or customer facility wiring) on one of the 480 legs, the other two legs 
will jump to 480V to ground (with much higher spikes along the way) and blow up 
the varistors on the inverter output stage which are not rated for this 
condition.  We learned this the hard way with 10 out of 24 inverters suffering 
complete failures on one project shortly after they were installed.  We're 
talking catastrophic component failure with bits of varistor all over the 
inverter boards and adjacent components scorched.  In the end, we installed a 
750kVA 480 wye to 480 delta isolation transformer to provide a reliable ground 
reference for the inverters.  In the process of solving this problem, we 
learned of several other sites with the same issue...

Best,
Blake
Sun Light & Power

On Thu, Apr 18, 2019 at 3:44 PM frenergy 
<[email protected]<mailto:[email protected]>> wrote:

Wrenches,

            I'm tackling a huge residential system that requires back-feeding 
the grid at 480 volts, delta (no neutral, right?). We're going to GT 30-50 KW.  
The SMA SB30000TL-US-10 is one of the few inverters (apparently) that can do 
this, which I'm planning to use.  The inverter can be fed up to 1,000 vdc,OC. 
1,000 volt array is new to me.  I assume they have to accept the high voltage 
because its a 30K inverter with only 2 MPPT strings.  My question: Other than 
not getting fried during installation, what's different about wiring the array 
or anything else on the DC side?  I don't see anything in our current (2014) 
code cycle on this that's different than 600 volt.  Tips, advice?

            Any links, past webinars, whatever else also helpful would be 
welcome.

Thanks,

Bill
On 4/18/2019 2:32 PM, Starlight Solar Power Systems wrote:
Hi Chris,

SWRC is the remote part name. SW-4024 is the inverter/charge.
I believe all the Trace products from that era use the same BTS with RJ11 plug 
so that should not be a problem.

Larry

[cid:16a32b673f0cc3c664a1]

On Apr 18, 2019, at 10:33 AM, 
[email protected]<mailto:[email protected]> wrote:

Hi Folks:

Does anyone have a line on a remote option and battery temp sensor for a 
SW-RC4024 (in a customer’s motor coach)?  If so, please contact me off list.   
Thanks.

Sincerely,

    Chris Daum
    Oasis Montana Inc.
    406-777-4309
    406-777-4309 fax
    
www.oasismontana.com<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.oasismontana.com%2F&data=02%7C01%7Cmichael.mahon%40sma-america.com%7C45ff938646764e80c74608d6c45486f1%7Ca059b96c28294d1188374cc1ff84735d%7C0%7C0%7C636912264663075189&sdata=lfJ5qBISzhkJU63svMNRzdCtg4ZEcK%2F%2F8XclNM1Yv%2BY%3D&reserved=0>





_______________________________________________

List sponsored by Redwood Alliance



List Address: 
[email protected]<mailto:[email protected]>



Change listserver email address & settings:

http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&data=02%7C01%7Cmichael.mahon%40sma-america.com%7C45ff938646764e80c74608d6c45486f1%7Ca059b96c28294d1188374cc1ff84735d%7C0%7C0%7C636912264663075189&sdata=6du8OEPP%2FXD92GVnY63lI5utxyy%2FY8eppctuhpuMMm8%3D&reserved=0>



List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&data=02%7C01%7Cmichael.mahon%40sma-america.com%7C45ff938646764e80c74608d6c45486f1%7Ca059b96c28294d1188374cc1ff84735d%7C0%7C0%7C636912264663085199&sdata=K6H7kSKzKXoBe8AUT5ABWO6hqQ4b15GzN%2FLZIrd32Tw%3D&reserved=0>



List rules & etiquette:

www.re-wrenches.org/etiquette.htm<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&data=02%7C01%7Cmichael.mahon%40sma-america.com%7C45ff938646764e80c74608d6c45486f1%7Ca059b96c28294d1188374cc1ff84735d%7C0%7C0%7C636912264663095204&sdata=w15%2FXHzOs7dzBbUSBgzTqKyN3TNx4itnniJhehRQ2eg%3D&reserved=0>



Check out or update participant bios:

www.members.re-wrenches.org<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.members.re-wrenches.org&data=02%7C01%7Cmichael.mahon%40sma-america.com%7C45ff938646764e80c74608d6c45486f1%7Ca059b96c28294d1188374cc1ff84735d%7C0%7C0%7C636912264663095204&sdata=rBhrWtghaMNK9z9pDmxOhIdK90adbDEUJ64SgKFDC7E%3D&reserved=0>



--

Feather River Solar Electric

Bill Battagin, Owner

4291 Nelson St.

Taylorsville, CA 95983

530.284.7849

CA Lic 874049

www.frenergy.net<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.frenergy.net&data=02%7C01%7Cmichael.mahon%40sma-america.com%7C45ff938646764e80c74608d6c45486f1%7Ca059b96c28294d1188374cc1ff84735d%7C0%7C0%7C636912264663105209&sdata=XCghPQDwnsuqGqf7Re7fnEZKNK%2FjxFwcQgrkHqS4FwI%3D&reserved=0>

[Image removed by 
sender.]<https://eur02.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.avast.com%2Fsig-email%3Futm_medium%3Demail%26utm_source%3Dlink%26utm_campaign%3Dsig-email%26utm_content%3Demailclient%26utm_term%3Dicon&data=02%7C01%7Cmichael.mahon%40sma-america.com%7C45ff938646764e80c74608d6c45486f1%7Ca059b96c28294d1188374cc1ff84735d%7C0%7C0%7C636912264663115219&sdata=BsPLN8CFTsJCKFMv8DjAgCHzaoETJbTt8%2FR6NxqBthQ%3D&reserved=0>

Virus-free. 
www.avast.com<https://eur02.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.avast.com%2Fsig-email%3Futm_medium%3Demail%26utm_source%3Dlink%26utm_campaign%3Dsig-email%26utm_content%3Demailclient%26utm_term%3Dlink&data=02%7C01%7Cmichael.mahon%40sma-america.com%7C45ff938646764e80c74608d6c45486f1%7Ca059b96c28294d1188374cc1ff84735d%7C0%7C0%7C636912264663115219&sdata=SO2zdJCzLA6sAL4wMGSOmVkO2FeEAyfXo19f7nsk3p8%3D&reserved=0>

_______________________________________________
List sponsored by Redwood Alliance

List Address: 
[email protected]<mailto:[email protected]>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&data=02%7C01%7Cmichael.mahon%40sma-america.com%7C45ff938646764e80c74608d6c45486f1%7Ca059b96c28294d1188374cc1ff84735d%7C0%7C0%7C636912264663125224&sdata=6MJa7xrEU2gN9VxIkJzuasYeD6ra0RV6R47NEVpVlzs%3D&reserved=0>

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&data=02%7C01%7Cmichael.mahon%40sma-america.com%7C45ff938646764e80c74608d6c45486f1%7Ca059b96c28294d1188374cc1ff84735d%7C0%7C0%7C636912264663135233&sdata=OoTFhVQQq1Vx7dGYUKw2XZy1J%2FUq42KXg2K7S%2FrsGDw%3D&reserved=0>

List rules & etiquette:
www.re-wrenches.org/etiquette.htm<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&data=02%7C01%7Cmichael.mahon%40sma-america.com%7C45ff938646764e80c74608d6c45486f1%7Ca059b96c28294d1188374cc1ff84735d%7C0%7C0%7C636912264663135233&sdata=R%2BDJUQynNNDkopweymggA6eNHZrohj1I89vxomGTA5M%3D&reserved=0>

Check out or update participant bios:
www.members.re-wrenches.org<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.members.re-wrenches.org&data=02%7C01%7Cmichael.mahon%40sma-america.com%7C45ff938646764e80c74608d6c45486f1%7Ca059b96c28294d1188374cc1ff84735d%7C0%7C0%7C636912264663145238&sdata=Uad3QNQvhHelWiywZoPHnjO7Ow5qs9kr8S382cODnW0%3D&reserved=0>


--


[Image removed by sender.]

Blake Gleason, PE | Employee-Owner |

Director of Innovation & Technical Excellence

510.845.2997 x128

Follow us on 
Facebook<https://eur02.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.facebook.com%2Fpages%2FSun-Light-Power%2F119675658118322%3Fref%3Dhl&data=02%7C01%7Cmichael.mahon%40sma-america.com%7C45ff938646764e80c74608d6c45486f1%7Ca059b96c28294d1188374cc1ff84735d%7C0%7C0%7C636912264663155248&sdata=cpO7MRf16dXBcbnPLXE32iyRTImk8GOQs0ULwztGOz4%3D&reserved=0>,
 
LinkedIn<https://eur02.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fcompany%2Fsun-light-and-power&data=02%7C01%7Cmichael.mahon%40sma-america.com%7C45ff938646764e80c74608d6c45486f1%7Ca059b96c28294d1188374cc1ff84735d%7C0%7C0%7C636912264663155248&sdata=Uvyzd55UAqAUUl21GWMn3H4NhjAKoV42W%2BHK%2FRFObrM%3D&reserved=0>
 or our 
website<https://eur02.safelinks.protection.outlook.com/?url=https%3A%2F%2Fsunlightandpower.com%2F&data=02%7C01%7Cmichael.mahon%40sma-america.com%7C45ff938646764e80c74608d6c45486f1%7Ca059b96c28294d1188374cc1ff84735d%7C0%7C0%7C636912264663165249&sdata=VzqG%2BfrtP4pdq4ocfbRIkFdY2NFKT2gtKJwP18y%2BC%2Bc%3D&reserved=0>.



_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to