My first recommendation is to confirm that the static level is OK during 
pumping, the second is; if he has used this scenario in the past and it has 
worked then Id pull the pump and check that the screen on the pump is not 
clogged or silt has not covered the pump + check for leaks in the input side of 
the Pres tank to pump. You can raise the pump higher if it has silted in. I 
have used soft start 3/4 pumps but I have larger 24V BBs
> On Apr 25, 2019, at 12:21 PM, Amos Post <[email protected]> wrote:
> 
> 
> 
> I have an off-grid customer who is having problems with his 10 year+ old 
> 1/2hp well pump.  It is running and running at 900watts constant and hardly 
> building pressure and even caused the 250amp breaker on his single VFX3524 
> inverter to trip.  He is running the pump at 240V off a x240 transformer and 
> thinking he might need to replace the pump and might want to go with a larger 
> 3/4hp pump for better performance and more future capacity.  Does anyone have 
> experience running 3/4hp pumps on this setup?  The pump is approx. 200’ down 
> in the well.
> 
> -- 
> 
>  Amos Post
>  Integrity Energy
>  O: 802.763.7023
>  C: 802.291.2188
>  ienergyVT.com <http://ienergyvt.com/>
>  
>  <http://ienergyvt.com/> 
> <https://www.facebook.com/integrityenergyllp?ref=br_tf>-- 
> 
>  Amos Post
>  Integrity Energy
>  W: 802.763.7023
>  C: 802.291.2188
>  ienergyVT.com <http://ienergyvt.com/>
>  
>  
>  <http://ienergyvt.com/> 
> <https://www.facebook.com/integrityenergyllp?ref=br_tf>_______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/[email protected]/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 

> [email protected] 
> <blocked::mailto:[email protected]%22%20%5Co%20%22blocked::mailto:[email protected]>  
>              www.SWNL.net 
> <blocked::http://www.swnl.net/%22%20%5Co%20%22blocked::http://www.swnl.net/>
>                 Solarwinds Northernlights       
>        Serving Mid Coast Maine & Northern California
>                          207-832-7574   Cl. 610-517-8401                      
>         
>                               Blair "TUMP" May
>                ********  MAINE'S CHARTER ********
>                       NABCEP    "Certified PV Installer" 
>    
>               ********  MAINE'S CHARTER ********
>                   Trace Xantrex "Certified" Dealer / Installer"
> 


_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to