Hi Darryl,

 

I have been looking into the Tigo TS4-F rapid shutdown option, including 
attending a webinar on their products.

As far as I have been told, they DO use a powerline carrier communications 
method to trigger the MLPE units.

A trigger device has to be wired to AC to detect loss of grid, and one 
conductor of every PV string must go through their attached CT donut which 
imposes this communications onto the PV wiring, and communicating with the 
module level components.

>From their documentation:

TS4-F units automatically enter rapid shutdown mode when the RSS Transmitter is 
switched off and resume energy production when power is restored to the RSS 
Transmitter. This solution complies with NEC 2014 & 2017 690.12 specifications 
utilizing power-line communication (PLC).

 

Please tell me what system you have that is wireless?

 

Thanks,

Glenn 

 

From: RE-wrenches <[email protected]> On Behalf Of 
Darryl Thayer
Sent: Thursday, May 30, 2019 12:16 AM
To: RE-wrenches <[email protected]>
Subject: Re: [RE-wrenches] rapid shutdown units for obscure inverter

 

Try Tigo, they have a MLPE shutdown wireless and does not use PLC (Power Line  
Communication).  With an unknown inverter, the inverter switching noise may 
trigger the Tigo's PLC to keep on or shut off.   Shutting off the inverter 
stoping module array current, and the AC supply to the "Gateways" loss of the 
heartbeat signal causes the shutdown of the modules.   I have used such an 
arrangement and it is passing every test.  This was maybe 1 or two years ago. 
Tigo may have made changes since then.  hope this helps.

 

On Wed, May 29, 2019 at 6:07 PM Rick Brown <[email protected] 
<mailto:[email protected]> > wrote:

Jerry,

 

Check out Midnight Solar’s Rapid Shutdown Shut Off Box (SOB). 

 

http://www.midnightsolar.com/

rick brown
SolShine Energy Alternatives, LLC
Electrical & Solar Contracting Services
www.SolShineEnergyAlternatives.com <http://www.SolShineEnergyAlternatives.com> 
Check, Virginia 24072
540.808.9502 <tel:540.808.9502> 

VA Class A Contractor Lic# 2705147660
VA Master Electrician Lic# 2710062762
VA Alternative Energy Systems Installer  
NABCEP Certified PV Installation Professional 110112-21


On May 29, 2019, at 5:44 PM, Jerry Caldwell <[email protected] 
<mailto:[email protected]> > wrote:

Dear Wrenches,

 

We are installing a system for a project we did not design. The plans specify 5 
Ginlong Solis inverters. Ginlong does not make their own rapid shutdown device, 
so units by Innovative Solar Products have been specified. The Innovative Solar 
rapid shutdowns are made to order and will take 4 weeks (not good for us).

 

Does anyone know another mfr that makes rapid shutdown devices that are 
compatible with other mfrs inverters?

 

Thanks,

 

Jerry Caldwell
Redwood Sun

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected] 
<mailto:[email protected]> 

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm> 

Check out or update participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org> 

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected] 
<mailto:[email protected]> 

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm> 

Check out or update participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org> 

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to