I'm surprised I did not get more of a response on this thread. Is anyone else adding onto M series microinverter systems? I'm starting to get a lot of requests to add more panels to older microinverter systems. Using the IQ combiner seems to make a lot of sense. The existing M series Envoy can just be plugged in nearby. I really like this approach but I don't want to run into a situation where I find out does not allow for this.
On Thu, Jun 6, 2019, 2:34 PM Jason Szumlanski < [email protected]> wrote: > Yes, correct. The M Series Envoy would be plugged in elsewhere, close to > the IQ Combiner. > > The situation is that a customer already has a combo system installed by > some clown with all wrong wire sizes, OCPD, disconnects, and > interconnection on the load side of a whole house generator. It's a mess > and I'm starting over. I literally had to remove ALL of the panels and > mounts for a re-roof because it was done so poorly and the roof is leaking > now. Anyway, the cleanest way to combine all the circuits is to bring all 4 > circuits in one conduit into an IQ Combiner and just use that combine into > one supply-side connection with a fusible disconnect. The M Series neutrals > can just pass through the IQ Combiner (plus one for the IQ Envoy). It would > supply the required OCPD protection. I guess my main concern is whether > this device is listed for use only as an IQ system combiner only or if the > individual components are listed, which would allow this setup for sure I > would imagine. > > Jason > > > > > On Thu, Jun 6, 2019 at 11:54 AM Chad Waits <[email protected]> > wrote: > >> Only thing I see is you will have to have 2 Envoys. The IQ inverters send >> the data on the powered conductors, not on the neutral like the M250’s. >> >> Chad Waits >> President/Owner – Net Zero Solar >> 101 W. 5th St., Tucson, AZ 85705 >> Office: 520-207-4053 >> Cell: 520-270-4873 >> NABCEP Certified PV Installation Professional >> >> >> >> From: RE-wrenches <[email protected]> on behalf >> of Jason Szumlanski <[email protected]> >> Reply-To: RE-wrenches <[email protected]> >> Date: Thursday, June 6, 2019 at 8:42 AM >> To: RE-wrenches <[email protected]> >> Subject: [RE-wrenches] Enphase IQ combiner for M series microinverters >> >> Does anyone see anything wrong with using an Enphase IQ combiner to >> combine two strings of IQ microinverters with two strings of M250 >> microinverters? I would not use the production CT (just use microinverter >> production data). >> >> I can't see any technical reason this can't be done. Do any listing or >> code reasons come to mind? >> >> Jason Szumlanski >> Florida Solar Design Group >> _______________________________________________ List sponsored by Redwood >> Alliance List Address: [email protected] Change >> listserver email address & settings: >> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org >> List-Archive: >> http://www.mail-archive.com/[email protected]/maillist.html >> List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or >> update participant bios: www.members.re-wrenches.org >> _______________________________________________ >> List sponsored by Redwood Alliance >> >> List Address: [email protected] >> >> Change listserver email address & settings: >> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org >> >> List-Archive: >> http://www.mail-archive.com/[email protected]/maillist.html >> >> List rules & etiquette: >> www.re-wrenches.org/etiquette.htm >> >> Check out or update participant bios: >> www.members.re-wrenches.org >> >>
_______________________________________________ List sponsored by Redwood Alliance List Address: [email protected] Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/[email protected]/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org