Wrenches,

            Is the only a way to back feed 128 amps (240v, split PH) onto a 200 amp panel is to tap the conductors between the meter and the main CB, assuming I can pull it off in the "customer section" of the panel.  Of course with the requisite AC disco within 10 feet.  Or, has anybody ever gotten a written approval from a panel manu to thread a 1/4" hole in a bus between the meter and the main CB to install a lug for accepting a backfeed source?

Bill