I’ve done just that in Pacific Power territory. The first time, they asked for 
an EE’s approval. That cost $500.00. 
> On Aug 27, 2019, at 11:31 AM, Jerry Shafer <[email protected]> wrote:
> 
> Bill
> The meter main is an UL approved product, any alterations may effect that in 
> the eyes of the inspector or PG&E. I have done a breakout panel where l was 
> exceeding the 20% rule but a 128 amp still may be an issue. The break out 
> panel is a connection where there are breakers all around to protect all the 
> connections. You need to confirm that PG&E will require a disco, you might to 
> eliminate a breaker though. The breakout panel is not always approved either. 
> Can you upgrade the panel with dual 200 amp outputs, one goes to a breaker 
> bus and the other just taps out. This would be less of a liability issue l 
> would think also. These panels do what you want and are UL Approved. 
> Jerry
> 
> On Tue, Aug 27, 2019, 10:40 AM frenergy <[email protected] 
> <mailto:[email protected]>> wrote:
> Wrenches,
> 
>              Is the only a way to back feed 128 amps (240v, split PH) 
> onto a 200 amp panel is to tap the conductors between the meter and the 
> main CB, assuming I can pull it off in the "customer section" of the 
> panel.  Of course with the requisite AC disco within 10 feet.  Or, has 
> anybody ever gotten a written approval from a panel manu to thread a 
> 1/4" hole in a bus between the meter and the main CB to install a lug 
> for accepting a backfeed source?
> 
> Bill
> 
> Feather River Solar Electric
> Bill Battagin, Owner
> 4291 Nelson St.
> Taylorsville, CA 95983
> 530.284.7849
> CA Lic 874049
> www.frenergy.net <http://www.frenergy.net/>
> 
> 
> ---
> This email has been checked for viruses by Avast antivirus software.
> https://www.avast.com/antivirus <https://www.avast.com/antivirus>
> 
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: [email protected] 
> <mailto:[email protected]>
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
> 
> List-Archive: 
> http://www.mail-archive.com/[email protected]/maillist.html 
> <http://www.mail-archive.com/[email protected]/maillist.html>
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>
> 
> Check out or update participant bios:
> www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/[email protected]/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 




        Michael Morningstar

        Morningstar Electric
        PO Box 1494
        Mount Shasta, California 96067
        530-921-0560
        CSLB 949635
 
  

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to