Hi Jerry

I’m not sure I understand. 
Are you saying that the white paper overrules ( if that’s the correct way to 
say it) the UL and OEM guidelines?

Jay


> On Sep 5, 2019, at 8:25 AM, Jerry Shafer <[email protected]> wrote:
> 
> Brian
> Missing the point, yes they are compatible but as we have seen in the real 
> world there are issues. This can give module and micro inverter manufacturers 
> an out regarding failures and responsibility 
> Jerry
> 
>> On Thu, Sep 5, 2019, 1:41 AM Brian Mehalic <[email protected]> wrote:
>> I don’t think “some white paper” is sufficient based on Code requirements, 
>> UL standards (6703), and verified field failures. Also see 2020 NEC® 
>> 690.33(C) - now requiring intermatability. 
>> 
>> Brian
>> 
>>> On Sep 4, 2019, at 2:06 PM, Jerry Shafer <[email protected]> wrote:
>>> 
>>> Wrenches
>>> Per some white papers connectors are interchangeable, this being said l 
>>> have had arc issues as a result. FYI there are knock-offs out there to.
>>> Jerry
>>> 
>>>> On Wed, Sep 4, 2019, 1:42 PM Brian Mehalic <[email protected]> wrote:
>>>> Are you saying each module has, for example, a positive factory H4 lead 
>>>> and a negative factory MC4 lead?
>>>> 
>>>> I definitely know of H4 problems, both mated with H4s and mismatched.  
>>>> 
>>>> Brian Mehalic 
>>>> NABCEP Certified Solar PV Installation Professional™ R031508-59
>>>> National Electrical Code® CMP-4 Member
>>>> (520) 204-6639
>>>> 
>>>> Solar Energy International
>>>> http://www.solarenergy.org
>>>> 
>>>> SEI Professional Services
>>>> http://www.seisolarpros.com
>>>> 
>>>> 
>>>> 
>>>>> On Wed, Sep 4, 2019 at 1:22 PM Kent Osterberg <[email protected]> wrote:
>>>>> I've recently been looking for the cause of random power drop offs to 
>>>>> zero in an Enphase M215 system with LG260 PV module that was installed 
>>>>> in 2013. Just one inverter in a system of fourteen has been doing this. 
>>>>> Enphase suggested moving the inverter to a different PV module and sure 
>>>>> enough doing that proved the problem wasn't with the inverter.  
>>>>> Intermittent zero output was being caused by the PV module.  In making 
>>>>> the inverter/module change I found that all the LG 260 modules in this 
>>>>> system have one MC4 connector and one H4 connector. At present I'm 
>>>>> convinced the mismatched connector is the actual cause of the problem. 
>>>>> Anyone else ever notice find PV modules with mixed MC4 and H4 connectors?
>>>>> 
>>>>> Kent Osterberg
>>>>> Blue Mountain Solar
>>>>> _______________________________________________
>>>>> List sponsored by Redwood Alliance
> 
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to