Thanks Brad,

I think I am finally getting it.

When on-grid, the grid is providing wave form and transistors in BB are available to provide voltage regulation.

When off-grid, the transistors in the BB are required to provided wave form and not available to provide regulation.


On 11/4/2019 6:10 AM, Bradley Bassett wrote:
Mark,

The difference is that when AC coupled the power is coming backwards into the AC out. When it's charging from the grid or generator it is charging from the AC inputs. The inverter can control the charge from the inputs but not what is coming in reverse into the output.

Brad

On Sun, Nov 3, 2019 at 6:10 PM Mark Frye <ma...@berkeleysolar.com <mailto:ma...@berkeleysolar.com>> wrote:

    OK Jay that makes sense.

    This must mean that there is a significant difference in the
    function of
    the BB inverter when it is in off-grid mode vs when it is in grid
    connected mode.

    On 11/3/2019 5:45 PM, jay wrote:
    > No, older non frequency shift BB inverters don’t communicate
    that way.
    >
    > They have no communication with a Rule 21 GT inverter.
    >
    > The BB, it will just keep charging and charging with any extra
    energy coming from the GT inverter.  The BB  has no regulation,
    there is no absorb or float, just charge.
    >
    > jay
    >
    > peltz power
    >
    >> On Nov 3, 2019, at 4:31 PM, Mark Frye <ma...@berkeleysolar.com
    <mailto:ma...@berkeleysolar.com>> wrote:
    >>
    >> OK, I am hearing this over and over and I just want to confirm
    that is true even if the BB is older and does not have "NEW
    Frequency Shifting AC Coupling".
    >>
    >> On 11/3/2019 4:26 PM, Dave Angelini Offgrid Solar wrote:
    >>> The BB inverter will drive the grid inverter off frequency
    because it is
    >>> full/floating and the grid tie will stop producing power. This
    is how AC
    >>> coupling works but if something goes wrong, like programming
    gets corrupted
    >>> by surges or the battery hits an LBCO or HBCO AC power will
    stop. Or if
    >>> this is being controlled by Soc and it gets wrong data or
    there is a
    >>> network issue, or all of the other things that can happen that
    I have not
    >>> thought of.
    >>>
    >>> Why do you not want to build a normal DC couples system? I forget
    >>> fast....Happy Hour!
    >>>
    >>> Dave Angelini Offgrid Solar
    >>> "we go where powerlines don't"
    >>> http://members.sti.net/offgridsolar/
    >>> e-mail offgridso...@sti.net <mailto:offgridso...@sti.net>
    >>> text 209 813 0060
    >>>
    >>> On Sun, 3 Nov 2019 16:17:39 -0800, Mark Frye
    <ma...@berkeleysolar.com <mailto:ma...@berkeleysolar.com>>
    >>> wrote:
    >>>> Folks,
    >>>>
    >>>> Please allow me to ask another question:
    >>>>
    >>>> Suppose I have a bi-direction inverter/charge with no
    connection to the
    >>>> grid.
    >>>>
    >>>> I have GT inverter ac coupled and producing 2000w. The
    battery is in
    >>>> float, and I have 2000w of load connected. All is well.
    >>>>
    >>>> Now suppose I remove the loads without disconnecting the GT
    inverters.
    >>>>
    >>>> The word is that something bad happens now. I would like to
    understand
    >>>> what that bad thing is.
    >>>>
    >>>> I have one explanation that I think says that the GTs will
    continue to
    >>>> produce the 2000w, and that energy will go into the batteries
    in an
    >>>> unregulated fashion. When does this end, when the batteries
    blow up? Is
    >>>> that the consequence of not disconnecting the GT?
    >>>>
    >>>> With many thanks in advance for your help in understanding.
    >>>>
    >>>> Mark
    >>>>
    >>>> _______________________________________________
    >>>> List sponsored by Redwood Alliance
    >>>>
    >>>> List Address: RE-wrenches@lists.re-wrenches.org
    <mailto:RE-wrenches@lists.re-wrenches.org>
    >>>>
    >>>> Change listserver email address & settings:
    >>>>
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
    >>>>
    >>>> List-Archive:
    >>>>
    >>>
    http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
    >>>> List rules & etiquette:
    >>>> www.re-wrenches.org/etiquette.htm
    <http://www.re-wrenches.org/etiquette.htm>
    >>>>
    >>>> Check out or update participant bios:
    >>>> www.members.re-wrenches.org <http://www.members.re-wrenches.org>
    >> _______________________________________________
    >> List sponsored by Redwood Alliance
    >>
    >> List Address: RE-wrenches@lists.re-wrenches.org
    <mailto:RE-wrenches@lists.re-wrenches.org>
    >>
    >> Change listserver email address & settings:
    >>
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
    >>
    >> List-Archive:
    http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
    >>
    >> List rules & etiquette:
    >> www.re-wrenches.org/etiquette.htm
    <http://www.re-wrenches.org/etiquette.htm>
    >>
    >> Check out or update participant bios:
    >> www.members.re-wrenches.org <http://www.members.re-wrenches.org>
    >>
    > _______________________________________________
    > List sponsored by Redwood Alliance
    >
    > List Address: RE-wrenches@lists.re-wrenches.org
    <mailto:RE-wrenches@lists.re-wrenches.org>
    >
    > Change listserver email address & settings:
    > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
    >
    > List-Archive:
    http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
    >
    > List rules & etiquette:
    > www.re-wrenches.org/etiquette.htm
    <http://www.re-wrenches.org/etiquette.htm>
    >
    > Check out or update participant bios:
    > www.members.re-wrenches.org <http://www.members.re-wrenches.org>
    >
    _______________________________________________
    List sponsored by Redwood Alliance

    List Address: RE-wrenches@lists.re-wrenches.org
    <mailto:RE-wrenches@lists.re-wrenches.org>

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    List-Archive:
    http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm
    <http://www.re-wrenches.org/etiquette.htm>

    Check out or update participant bios:
    www.members.re-wrenches.org <http://www.members.re-wrenches.org>


_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to