What brand of CC please? Sorry if I missed it...--Dave 
Dave Angelini
Offgrid Solar
"we go where powerlines
don't"
http://members.sti.net/offgridsolar/ [1]
e-mail offgridso...@sti.net
[2]
text 209 813 0060

On Tue, 14 Jan 2020 19:51:18 -0700, Ray  wrote:   


If there is any current flow between DC negative and ground anywhere in
the system, it will trip. I would check the dryer for a ground fault, and I
would check the system to make sure Neutral is not bonded to ground in more
than one place (very common). Most importantly, I would make sure that
negative is not bonded anywhere except at the DC GFI in the controller. 


My guess is that DC is bonded at the negative shunt as is normal with
many DC load centers, and that the dryer is a big enough load that pulls
enough DC amps, so that some of DC negative is flowing back through the
ground. Probably doesn't trip normally, because at lower loads, less than
an amp is flowing on the ground. 

Just guessing, 
Ray Walters
Remote
Solar
303 505-8760
 On 1/14/20 7:03 PM, Mac Lewis wrote:  Hi wrenches,  
I've got an off grid customer that has an external PV GFI breaker in his
charge controller that trips when the dryer is on. He snuck in an electric
dryer uggh   However, I am curious what the mechanism might be to cause the
trip. Will a ground fault on the AC side of an inverter trip a PV GFI on a
charge controller?   I haven't dug too deep into this yet but maybe someone
else has seen this.     Thanks in advance for your help. 


_______________________________________________
List sponsored by Redwood
Alliance

List Address: RE-wrenches@lists.re-wrenches.org [3]

Change
listserver email address &
settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
[4]

List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
[5]

List rules & etiquette:
www.re-wrenches.org/etiquette.htm [6]

Check
out or update participant bios:
www.members.re-wrenches.org [7]

   -- 




Links:
------
[1] http://members.sti.net/offgridsolar/
[2]
mailto:offgridso...@sti.net
[3]
mailto:RE-wrenches@lists.re-wrenches.org
[4]
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
[5]
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
[6]
http://www.re-wrenches.org/etiquette.htm
[7]
http://www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to