Hey Wrenches,

I just did a site visit for a client who's had a few iterations of PV
installed. The main reason for the call was that the battery bank would
never charge to 100%SOC but rather appear to charge to 100%SOC and actually
hover around 70%SOC. At  the end of the day the client would top it off
with the generator for 30-60min. This has been happening since October, I
just got the call the other day.

The site is less than code compliant to say the least and the programming
of the 3 charge controllers were not equal.

Array 1 South Facing 4-Canadian 250w (one string)
Flexmax 80
Absorb 29.3V 6hrs
Float 27.3
End Amps 10A
Rebulk 25V

Array 2 South Facing 6-205w 2-195w (one string)
Flexmax 60
Absorb 29.3V 6hrs
Float 27.3
End Amps 10A
Rebulk 25.6V

Array 3 North Facing 8-295w Renosola (4 strings)
Flexmax 80
Absorb 29.4 1hr
Float 27.3
End Amps 0
Rebulk 24

20-Trojan Reliant L16 12V (5 parallel to a bus) purchased the end of 2017

Apart from the not so great design to say it lightly, the bank is
consistently showing a stepping voltage of about 70%SOC up to 100%SOC from
negative to positive. I changed the charge controllers to an equal
absorption voltage and time (28.8V and 4hrs) to try and slowly bring up the
lagging side of the bank. I was cautious not to raise them all to 29.4 at
4+hrs because I don't know their history and didn't want to cook them
further if they are indeed headed that way. At the time of inspection the
batteries were about 84F and the thermal camera showed no variations or hot
spots.

I asked the owner to report back if it gets better, worse, or the same. He
reported back and said that the total kWh production daily is gradually
going down over these past few days. Any suggestions on how to bring this
bank back to 100%SOC would be appreciated.

Jon Siegenthaler
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to